Thanks Craig, now lower the LWT setting to 30C and see what happens to how the system operates.
Right, finished timing. Now back to 8 mins on 20 seconds off again.
Flow temp 28.1 set to 30
Indoor 22.1Â
Outdoor 6.5
Room temp 19
Posted by: @craig1980Right, finished timing. Now back to 8 mins on 20 seconds off again.
Flow temp 28.1 set to 30
Indoor 22.1Â
Outdoor 6.5
Room temp 19
Hi Craig,
I'm afraid that I have run out of suggestions.
There appears to be something fundamentally wrong with your heat pump, and/or how the system has been installed. The only thing that I can see that appears to be incorrect is the Teva_out temperature reading of -50C, which could possibly be due to a faulty or disconnected temperature sensor.
I would suggest that you e-mail Samsung Technical Help and ask them why your system may be operating as it is doing.
In the meantime set your system back onto WC mode and adjust for the required indoor temperature.
Â
Okay, many thanks for all of your help. I'll update if I find anything from Samsung. Thanks again. Much appreciated.Â
Interestingly, when I put the settings back to WC I get error E121. Upon looking this up in the manual it saysÂ
"Short-or open- circuit error of the room temperature sensor of the zone 1 indoor unit (detected only when the room thermostat is used) Error source - Hydro unit.Â
Posted by: @hughfPosted by: @mike-hAm I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
It doesn't have a buffer, no...
Which set of instructions say that the samsung needs a buffer?
Â
@hughf Please see the topic about Samsung install and buffer tank
https://renewableheatinghub.co.uk/forums/postid/11342
Freedom Heat Pumps claims a buffer tank is required to be within the Samsung warranty, even though the manual implies otherwise and Joule make a pre-plumbed cylinder without a buffer tank.
Â
@mike-h Ah yes, good old freedom. I’d trust the instructions from midsummer wholesale personally. I know that GH was always getting 911 errors (low flow) on his early installs, so they probably mandated a buffer to deal with that issue, allowing the primary pump to run at full speed to charge the buffer.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 344 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: What determines the SOC of a battery?
@batpred I didn't write the Seplos BMS software, I a...
By Bash , 12 minutes ago
-
RE: Electricity price predictions
Sorry to derail this thread ‘slightly?’ but back to the...
By Toodles , 21 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
Without knowing it, @andrewj, you've laid down the gaun...
By Majordennisbloodnok , 40 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos and @cathoderay thanks. I have some history grap...
By benson , 44 minutes ago
-
I am having my existing heat pump changed to a Vaillant...
By trebor12345 , 1 hour ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 2 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 4 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 4 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 10 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 20 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 22 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago