10kw heat pump run in 24*7 data?

66 Posts
5 Users
10 Reactions
1,325 Views
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2488
 

@jeegnesh — that's fine, it is cycling less than once an hour, ie long cycling rather than short cycling, and it has to do it, as it is the only way it can reduce overall output when the outside air temp is warmer and the heat demand is less.


Midea 14kW (for now...) ASHP heating both building and DHW


   
👍
1
ReplyQuote
(@jeegnesh)
Reputable Member Member
Joined: 1 year ago
Posts: 96
Topic starter  

Posted by: @cathoderay

@jeegnesh — that's fine, it is cycling less than once an hour, ie long cycling rather than short cycling, and it has to do it, as it is the only way it can reduce overall output when the outside air temp is warmer and the heat demand is less.

Music to my wallet 

 


13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car


   
ReplyQuote
(@jeegnesh)
Reputable Member Member
Joined: 1 year ago
Posts: 96
Topic starter  

So with the constant mild temps not a great deal to report, i'm on the 24*7 the house and wife are happy, the usage is reasonable - so really its this cold spell i'm waiting on.

So we have been running at 0.3 / 0.35 heat curve and so far all good.  The only 2 things that come to mind while I await this colder weather:--

1 - After hot water run its taking a long time for recovery before heating kicks back in.
2 - Running a curve like .3 or .35 makes me think I did not even need a 10kw heat pump and perhaps a 5,6,7 would have been fine, or is this silly thinking on my part?

Screenshot 2025 12 12 at 11.41.13

13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car


   
ReplyQuote



(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 3716
 

Posted by: @jeegnesh

2 - Running a curve like .3 or .35 makes me think I did not even need a 10kw heat pump and perhaps a 5,6,7 would have been fine, or is this silly thinking on my part?

The curve really depends on the emitters in relation to the loss not the heat pump capacity in relation to the loss.  But its certainly not silly thinking that your heat pump may have greater capacity than is needed, I would say that its perhaps more likely than not given the way heat loss estimates are done by many installers.

 

If you can tell us either:

  • Your annual gas/oil consumption if you previously had gas/oil heating or
  • the floor area, age and construction/insulation standard of the house

Its pretty easy to ballpark what the loss is likely to be!

 

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@jeegnesh)
Reputable Member Member
Joined: 1 year ago
Posts: 96
Topic starter  

So going back, I see octopus always referred to an annual gas estimate of 22,790kw (i'll be honest the house was still cold) - think total space is around 250/270sqm, also attaching the heat loss calculations that were done prior to the heat pump install.

Construction wise brick, slate roof, minor bits of flat roof, was pretty much fully rebuilt in 2014, insulation is very decent too, double glazed - Kitchen area does have a lot of glass doors and windows.


13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 3716
 

Posted by: @jeegnesh

So going back, I see octopus always referred to an annual gas estimate of 22,790kw (i'll be honest the house was still cold) - think total space is around 250/270sqm, also attaching the heat loss calculations that were done prior to the heat pump install.

Construction wise brick, slate roof, minor bits of flat roof, was pretty much fully rebuilt in 2014, insulation is very decent too, double glazed - Kitchen area does have a lot of glass doors and windows.

I would say you most likely do need 10kW.  My gas consumption with the house warm was 18-20MWh/annum and 7kW is pretty much spot on.  If yours was ~23MWh and the house not warm, 7kW which is the next size down from 10 in the Vaillant range is most likely undersized.  Of course your gas boiler might have been very inefficient or run inefficiently but I would say quite plausibly marginal to run on the 7kW machine.

 


This post was modified 5 days ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote