Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Here is my heat pump installation with questionable COP in Italy
Hi everybody, this is my first post here, I've been watching the podcasts for a while and I hope it's ok to write here even if I'm not in the UK but in Italy, hills around Florence to be precise.
So I had my heat pump installed 4 years ago and my installation was a disaster. My installer was very very new to heatpumps and had no idea how they worked or how to configure it properly. Due to the lack of expertise, I turned to the internet and with a lot of struggles I've been using somewhat succefully for the past 2 years but, as you know, I'm alwasy monitoring and ttrying to see if I can Improve efficency. A little summary of my setup. I have a viessman 100-s 8kwh (more on that later), connected to a 40L buffer, from the buffer I have 2 wilo para pumps (regulated to low speed), one goes to the radiator circuit and the other to a fancoil circuit (hydronic split? I'm not sure how they're are called in english).
My house is old, it was built in 1823 and had several upgrade trough the years, it's about 80 square meters but on 3 floors + small attic (less than 10 sqm) with the inside unit of the heatpump (it's a split model), water cylinder 300L. My roof is insulated and all the windows are double glazed but pretty old (18 years). The walls are all stone and brick (mixed) and avergae about 70cm thick , 80cm in some spots. Now I know perfectly that I need to upgrade the windows, unfortunately because of town regulations I could'nt insulate the walls, and I can't install PV on my roof (crazy stupid italian legislation).
I upgraded radiators (apparently not enough) when I renovated 4 years ago and installed the heatpump, and installed the fancoils, 4 total. In the summer I use the fancoils to cool and they work very well, here it gets very very hot in summer. In winter I use both radiators and fancoils to heath the house. The system is setup trough weather compensation, and I have no thermostat but several temp sensor in each room for monitoring.
After years of trial and error and research I understood the logic behind my veissman HP, and I can change almost all parameters. This model unfortunately is oversized for my house, it's a nominal 8kw but it's more like a 12kw, meaning that the minimum heat it can generate it's around 4kwh. regarding the logic, basically the whole heating cycle is based on the buffer temperature. The heatpump heats the water to bring it to the target (set by weather comp) and it can increase that temperature based on a tolerance that I can change, after many tests I set it to 4 degrees up or down. This way I drastically reduced the on/off as you can see from the graphs, unfortunatly this setup I think it's not great for efficency (no buffer would be better) but I can't do it differently because of the dual circuit. So In a situation like the graphs attached, the heatpump is constantly running at it's minimum which is 25hz or 28% capacity, and it can run for hours.
The delta T in this cased is calculated by the heat pump that regulates it's secondary pump to the buffer to mantain 5K spread constantly. The problem I have is that the COP is pretty low, as you can see. My data is based on Thermal energy (from heatpump data), electrical energy (shelly em that measures also the 2 pumps on the buffer). I can also see the heat pump's COP as a datapoint and of course that one is higher. Last night it was around 4-6C and the cop was under 3. Am I just unlucky that my model has low efficency? I know that lowering supply temperature will of course increase COP, but I feel there is more to it. Any idea is appreciated . Sorry for my english as it isn't my first language.
I forgot to mention that the target room temperature is achieved and mantained pretty well, but since I live in a moderate climate (maybe it goes below zero a handful of times a year), I was wondering if I can get better COP
Hi, and welcome to the forum.
I cant quite understand whats going on in the charts because the labels arent obvious.
Cn you clarify which of the lines shows:
Temperature of the water exiting the heat pump flowing to the buffer
Temperature of the water exiting the buffer flowing to the emitters
Temperature of the water returning to the buffer from the emitters
It looks like with an outside temp of ~7 you are running at a flow temp (I cant tell whether measured at the heat pump or at the output of the buffer) of ~40. Is that a correct interpretation? Can you tell me what your weather compensation parameters are please?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Sorry for the late reply, I apologize for the graphs not clear. you are correct, so for example for the past 12hrs or so exterior temperature was between 5 and 7 C, the heatpump maintains a constant delta 5 between what it prduces and the return, and it never stops, it runs at the minimum of 25hz which is 28% of the compressor, and it delivers 4.3 KW of thermal energy (according to the data it spits out), it produces water around 40C and I will say that it can't run any better. I have a shelly that measures the electric consumption of heatpump with all the pumps, including 2 wilo pumps that serve 2 circuits at the same temperature (radiators+fancoils), IF I calculate the COP using this data en the heat generated (data from hetpump), I average a cop of 3.4. The heatpump itself says 4.3 because it doesn't count any pump but only the compressor (that's what veissman says). I'm planning to replace some radiators next year so I can reduce the supply temperature, I'll probably have more on/off but I don't see anything else I can try. my next step is to measure the delta after the buffer to see if I can improve on that side, right now both pumps run at minimum speed. you can see from the new graphs the behaviour. The big "bumps" in the graphs are Hot water preparation, not sure about the small bumps but I don't think it's defrost. to read the charts, blue line in the first graph is power consumption for the whole system (shelly em ), red is supply temperature, yellow return temperature, green buffer temperature, blue in second graph is outside air temperature
Just an update, I was able to impreove a bit the COP with some more monitoring, I realized that the Delta T after the buffer was too low so the additional pumps were sucking colder return water. So I went to each radiator starting from the one closest to the HP and closed off the return valve little by little to obtain around 4-5 C delta in each radiator, after that I reduced the delta between HP and buffer to 4, now it heats the house better with lower supply temperature. I honestly had no idea about balancing and I've never seen it mentioned in Italian groups, but I think it's very important, I just wish the installers did their job to begin with.
@materox345 It would seem that some installers regard the commissioning stage as an ‘optional extra’ and only do that which enables them to ‘sort of comply’ with MCS requirements in the UK (perhaps something similar happens in Italy). Balancing the system does seem to be very optional when it comes to some installers. ☹️ Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Well in Italy there is nothing controlling the quality of the work in any capacity. There are very few competent installers as far as I know, and a lot of costumers with nightmare installations. To give an example I have a friend that recently remodeled his house, it's a single building but pretty small, 2 floors with about 75 sq meters total area with brand new underfloor heating (low thickness) and very good new double glazed windows. few months ago he got 2 different quotes from installers recommended by the construction company. One told him he needed 16kw heatpump. and the other told hime he needed 2, the first of 12kw for heating and another 4kw to do hot water only, both quotes were astronomical in price and comical. Note that neither company did any sort of heatloss calculation in person, nothing at all, but gave him final quotes based on paper plans. In the end I convinced him to go with a reputable installer that put a 5kw panasonic K and he is very happy with it, low consumption, optimal comfort. This is just an example but there are many many horror stories around. Most boiler installers here keep going with the same : it doesn't work when it's cold etc etc and if they install anything is very very oversized like Italy is the new Siberia when last year in my area we went below 0 just 2 nights total
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 136 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 7 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 7 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 7 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 8 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 9 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 10 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 12 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 12 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 14 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 17 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 20 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago