Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Digest of UK Energy Statistics

25 Posts
8 Users
12 Reactions
9,124 Views
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 5 years ago
Posts: 3503
Your energy: 41 kWh
Topic starter  

Posted by: @ianmk13
↑

I am in Milton Keynes - a new city, so you might think the local infrastructure would have plenty of capacity. However, many of the sub-stations already have limited availability for prospective solar generation, batteries and EV chargers.

Unfortunately MK was designed when the national grid was still viewed as a system to deliver electricity.
Little thought would've been given to 'reverse power' from local generation.

The local situation is a 'mixed bag'.

The following map shows the Bulk Supply Point (BSP) and Primary Substation available capacity to receive local generation.

MK BSPdistrib

Green pins have available headroom for more local generation, red is 'at or over capacity' and blue is 'not enough data to define'.

If I zoom in to a lower level and pick out a typical 500kW local substation (11kV input) in the Titchmarsh area, then I can see

  • 400kW Daytime peak demand
  • 512kW Night peak demand (marginally outside spec)
  • 191kW Total connected generation
  • and there are 5 properties with EV charge points

 

That's fairly typical for SE England.
Consumption per household is particularly high, and the region is dependent on substantial energy supplies from elsewhere in Britain and the overseas Interconnectors.
That can be seen from the orange arrows on the grid-flow maps from National Grid ESO.

image

 

I've picked up this area, not just because it's of interest to Ian, but that it shows deficiencies in the DUKES statistical approach.

The more GB uses electricity generated from distributed renewable sources, the less useful it is to create policy based on national traits.

We need to think much more strategically about how we use the generation sources that are local to us.


Save energy... recycle electrons!


   
Like
3
ReplyQuote
Jeff
 Jeff
(@jeff)
Noble Member Member
Joined: 6 years ago
Posts: 656
Your energy: 0 kWh
 

The Titchmarsh area was one of the first areas to be built in the new town, including housing for people who built the new town. Fishermead in that area is particularly poor quality housing so I am not surprised that area is an issue. I wonder if the in fill of flats around the center and the expansion of retail, snowdome and business sites also exacerbated the challenge in that area. It is very different to the wider new town estates.

I wonder if some of the other red areas are historical and pre date the new town. They look like Wolverton and Newport Pagnell rather than Milton Keynes.

I use to live in next to the old Milton Keynes Village.

 



   
ReplyQuote
(@ianmk13)
Reputable Member Member
Joined: 4 years ago
Posts: 195
Your energy: 0 kWh
 

Posted by: @jeff
↑

The Titchmarsh area was one of the first areas to be built in the new town, including housing for people who built the new town.

Amazing.  I've lived a couple of miles north of Fishermead for over 40 years and never heard of any 'Titchmarsh' area.  I thought he was a gardener on the telly.

@Transparent. I'm on the local substation by Broughton and if I remember correctly (which I may not), this has available capacity for local generation but its my local neighborhood substation that's creaking at the seams.



   
Like
1
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 5 years ago
Posts: 3503
Your energy: 41 kWh
Topic starter  

@ianmk13 - There are two Primary Substations (33kV/11kV) at Broughton:

Kingston 940070; 23MW transformer; 9MW demand headroom, 10MW reverse-power (generation) headroom

Fox Milne 940043; 23MW; 1.5MW demand headroom, 6MW reverse-power headroom

In both cases, the National Grid data suggests that these transformers could be opened up to far more generation assets than the reverse-power headroom figure suggests. There will be technical reasons for this which are not explained by the raw figures.

Just because the local substations (11kV/440v) have generation constraints on them doesn't prevent you from making better use of the available reverse-power headroom.

Instead of thinking at the level of each individual house, consider the issue in a wider context.

A local Community Energy Group should be opening discussions with NGED about adding community-operated solar/wind/anaerobic-digester types of generation. You could connect at the 11kV level within the area already served by those two Primaries.

Alternatively, NGED may be even more attracted by the possibility of community-run battery storage, especially in areas of higher-density social housing.

The available Demand Headroom at these two Primaries is defined by the Peak Demand in the early evening.

If a community operated storage network could deploy batteries which remove 10% of the housing from any demand at peak time, then that would alleviate thermal stresses on underground cables and prevent outages. That's highly desirable from NGED's viewpoint.

The problem you're up against is a low level of social enterprise, partly due to the way in which Milton Keynes was designed.

 


Save energy... recycle electrons!


   
ReplyQuote

(@derek-m)
Illustrious Member Member
Joined: 6 years ago
Posts: 4425
Your energy: 0 kWh
 

@transparent

While I agree with your suggestions, and have made similar ones myself on a number of occasions, the point at which I feel it falls down is when you state 'community-run battery storage'.

For such systems to operate in the most efficient and cost effective manner, the battery storage would need to be under the control of NG and/or the DNO's. Afterall, they are the ones controlling the supply of electrical energy to the various consumers, so are in a much better place to know how best to fully utilise such a system.

I realise that at present NG and the DNO's are prohibited from doing so, because it is deemed to be generation, and therefore violates their license to operate. This limitation needs to be changed, such that energy storage is not classified as generation.



   
ReplyQuote
(@ianmk13)
Reputable Member Member
Joined: 4 years ago
Posts: 195
Your energy: 0 kWh
 

@transparent Are you advocating communities collaborating on storage at the 11kV level only, or an alternative of a cluster of homes somehow collaborating at the 440V level (potentially complicated by the 3-phase element) ? As far as I am aware, no suppliers are (yet) offering a ToU Export tariff, but you seem to be suggesting that NGED may welcome the idea.

Incidentally, an error/fault/anomaly occurred on my newly-installed home battery system a week or so ago and neither battery inverter nor solar inverter's G100 system activated. I am restricted to 5kW but I actually exported at 6-8kW for a while with my grid voltage knocking on 253V. Presumably this will have increased the grid voltage of others on the same phase, but I didn't hear any neighbours shouting 😉 .



   
ReplyQuote
(@katler)
New Member Member
Joined: 2 years ago
Posts: 1
Your energy: 0 kWh
 

interesting to read

first time see this information



   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 5 years ago
Posts: 3503
Your energy: 41 kWh
Topic starter  

Feel free to comment @katler

Very few consumers know anything about how our UK energy supplies operate.
Would it help if we understood it better?

I wonder what drew you here to this topic. 🤔 

Are you aware that today is the final day on which National Grid Electricity System Operator (ESO) will be running the supply network?
Tomorrow, 1st October, all British energy supplies will be managed by a new organisation, the National Energy Systems Operator.


Save energy... recycle electrons!


   
ReplyQuote

Jeff
 Jeff
(@jeff)
Noble Member Member
Joined: 6 years ago
Posts: 656
Your energy: 0 kWh
 

Posted by: @transparent
↑

@ianmk13 - There are two Primary Substations (33kV/11kV) at Broughton:

Kingston 940070; 23MW transformer; 9MW demand headroom, 10MW reverse-power (generation) headroom

Fox Milne 940043; 23MW; 1.5MW demand headroom, 6MW reverse-power headroom

In both cases, the National Grid data suggests that these transformers could be opened up to far more generation assets than the reverse-power headroom figure suggests. There will be technical reasons for this which are not explained by the raw figures.

Just because the local substations (11kV/440v) have generation constraints on them doesn't prevent you from making better use of the available reverse-power headroom.

Instead of thinking at the level of each individual house, consider the issue in a wider context.

A local Community Energy Group should be opening discussions with NGED about adding community-operated solar/wind/anaerobic-digester types of generation. You could connect at the 11kV level within the area already served by those two Primaries.

Alternatively, NGED may be even more attracted by the possibility of community-run battery storage, especially in areas of higher-density social housing.

The available Demand Headroom at these two Primaries is defined by the Peak Demand in the early evening.

If a community operated storage network could deploy batteries which remove 10% of the housing from any demand at peak time, then that would alleviate thermal stresses on underground cables and prevent outages. That's highly desirable from NGED's viewpoint.

The problem you're up against is a low level of social enterprise, partly due to the way in which Milton Keynes was designed.

 

May also be the new build houses going up near there, many of those may have solar etc.

The Milton Keynes city "boundary" has been dramatically expanded over the years, both for housing and business. Last time I drove in I barely recognised the outskirts and there is still a lot of building work going on from what I saw

 



   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 5 years ago
Posts: 3503
Your energy: 41 kWh
Topic starter  

The DUKES report for 2025 has just been published here.
Note that DESNZ always refer to this by the year of publication rather than the year for which the statistics cover. So this is DUKES 2026.

Electricity is addressed in Chapter-5.

Domestic consumption remains steady. It's been between 29% - 30% for the last 5 years.

There's a marginal increase in generation of just 2.6% during the year.

image

There is no data for potential generation which is actually rejected/curtailed due to over-supply,
nor for that switched off for technical reasons, such as the solar sites in the West Country.
See Topic Solar Energy - No thanks.

Collecting data on generation which doesn't get exported to the grid is incredibly difficult for obvious reasons.

 

Data centres are starting to become significant:

image

Ofgem is wrestling with the regulations needed to govern Connection Applications for data centres.

They have just published their report on the initial consultation, and are now requesting further feedback.

I feel the problem is that they wish to control access to the grid by asking for a financial commitment up front.
But the 'big boys' in the fields of online commerce and AI can throw any amount of money on the table.

Ofgem have already shot us in the foot by their TM04+ Guidance. That means connection applications may not be refused on either of these grounds

  • the location of the site. Is it in an area without sufficient capacity?
  • the need for that technology. Ie is it beneficial to the UK?

 


Save energy... recycle electrons!


   
Like
Interesting
3
ReplyQuote
Jeff
 Jeff
(@jeff)
Noble Member Member
Joined: 6 years ago
Posts: 656
Your energy: 0 kWh
 

Posted by: @transparent
↑

The DUKES report for 2025 has just been published here.
Note that DESNZ always refer to this by the year of publication rather than the year for which the statistics cover. So this is DUKES 2026.

Electricity is addressed in Chapter-5.

Domestic consumption remains steady. It's been between 29% - 30% for the last 5 years.

There's a marginal increase in generation of just 2.6% during the year.

image

There is no data for potential generation which is actually rejected/curtailed due to over-supply,
nor for that switched off for technical reasons, such as the solar sites in the West Country.
See Topic Solar Energy - No thanks.

Collecting data on generation which doesn't get exported to the grid is incredibly difficult for obvious reasons.

 

Data centres are starting to become significant:

image

Ofgem is wrestling with the regulations needed to govern Connection Applications for data centres.

They have just published their report on the initial consultation, and are now requesting further feedback.

I feel the problem is that they wish to control access to the grid by asking for a financial commitment up front.
But the 'big boys' in the fields of online commerce and AI can throw any amount of money on the table.

Ofgem have already shot us in the foot by their TM04+ Guidance. That means connection applications may not be refused on either of these grounds

  • the location of the site. Is it in an area without sufficient capacity?
  • the need for that technology. Ie is it beneficial to the UK?

 

What happens to curtailment is interesting if you look at other areas of the world. 

There are already parts of Australia where home owners are charged if they export solar energy from their homes when there is too much electricity generation overall. 

This could easily be necessary in the future in the UK if the government isn't careful. 

 



   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 5 years ago
Posts: 3503
Your energy: 41 kWh
Topic starter  

Posted by: @jeff
↑

There are already parts of Australia where home owners are charged

That sounds painful.

It would be much better to charge a battery. 😎 

 

There would be side benefits if such a system were implemented in the UK.
Solar export from domestic properties also increases losses at the local substation because homes are usually single-phase.

But if such a system of export charging were introduced here, then we'd need nodal tariffs to be offered first.
We don't want to be levying a charge on a householder exporting in Durham just because Exeter to London is bathed in sunshine!