What crazy nonsense are inverter limits and why are they imposed?
Posted by: @transparentMy apologies @batpred I overlooked that you'd already I identified your DNO as being UKPN.
So you are more likely to be in an area where 5kW export could be permitted.
Continuing this here as it is related to dno approvals. Anyone needing the background, it is at the fogstar/solis adventure. The eventual grounding of my dreams for HA optimisation may also fit elsewhere.
When you said I am in an area that allows 5kw single phase, does it mean the DNO have some ability to even it across phases?
As it does not make much sense unless the phase would extend to a very large number of households. I am thinking the # households is restricted by distance on a low density housing setting like mine.
I would be exporting when the agile rate in my region justifies it, not when whoever is on the same phase at local level needs it.
Or is this 5kw capable area going to do something clever to balance power across phases?
Is there a lookup facility to see your limit, or is it just on the original approval document, and can you apply for a limit increase, if for example you expand your system import/export, 16kW battery or even additional batteries, expansion in additional solar panels lets say 8 x 500W panels so 3kW to 4kW extra, 12kW+ heat pump, all electric cooker/hob, EV etc?
This is mine:
Posted by: @dreiIs there a lookup facility to see your limit
With my dno, there's a portal with accounts etc and some "applications" like the ev charger are just a few clicks.
Others you send docs like for export g99, etc and my dno updates it in the portal.
But essentially consumption is not really limited. I get 100amp, so 24kw service.
The way each dno handles requests for export depends on their infra covering your area and overall capacity. The power side of the system works in three phases (4 wires) and it is not common for domestic to take all of that in, specially on urban settings.
Essentially I take one phase and neutral wires. When I start exporting, it will just go via those wires. Only large renewable capacity need to be on dedicated three phase connections.
So what happens with the grid is that, when power is exported to one phase, it should be consumed in that phase, otherwise it may be lost. I do not work for the grid, there are competent people developing strategies for and also managing that stuff..
Posted by: @batpredThe power side of the system works in three phases (4 wires)
That's true for the LV (Low Voltage) level of the grid, which operates at 440v (3ph) and 240v between phase and neutral.
It's not true for all the rest of the grid because there's no neutral.
The national grid is a 3-wire system.
Posted by: @batpredEssentially I take one phase and neutral wires. When I start exporting, it will just go via those wires.
That's not how a 3-phase feed works.
If the load across all three phases is the same, then there will be zero current in the neutral wire.
The problem for local substations supplying (single-phase) housing is that the demand will be different on each house.
When the number of houses connected to a Feed cable is small, there is likely be a greater difference in demand between the phase.
That's called phase-imbalance, and is a serious problem.
In the following diagram, imagine the current being taken by each house is represented as the length of a spring:
The demand from the three houses above is the same.
There is no current traveling on the black neutral wire in the centre.
Lets add four more houses further along the road:
There's increased load from houses 5a and 5b which results in that blue spring being stretched.
But the greater effect is from the EV being charged at No.6.
This greatly increases the current being drawn along the phase coloured yellow.
Notice how the Neutral is also now being pulled off-centre.
It will be carrying current back to the centre-tap of the substation transformer.
Posted by: @batpredwhen power is exported to one phase, it should be consumed in that phase, otherwise it may be lost.
Energy is neither created nor destroyed.
Electricity you've exported from a house can't be 'lost'.
Either other houses on the same phase will use the electricity you've exported,
or else the phase-imbalance will generate heat in the substation transformer.
Losses due to phase imbalance in Britain are currently running at 10%, which is a massive waste.
When I view timelines from local substations, I can 'see' phase imbalance occurring by looking at current in the neutral.
The two concepts are directly linked.
In the above plot you can see households 'waking up'.
Demand increases significantly just before 8am.
There's light cloud in the area until 10:30.
At that point sunlight hits solar panels on rooftops.
But houses on the phase coloured turquoise (L1) have more solar export.
They make less demand on the grid, which is why the L1 current falls more.
The result is a rapid increase of current flowing in the neutral (grey).
Once you understand the concepts above, it becomes possible to appreciate why there are particular limits on the permissible export from properties.
Earlier this year I wouldn't have bothered correcting your statements.
But we now have an AI bot picking up information from this forum.
Wattson then offers that information to other people.
We can no longer allow inadequate explanations to remain unchallenged.
Save energy... recycle electrons!
Thank you for a very comprehensive, timeless and rounded explanation, that gets to the core of the title of the thread.
No problem at all, and even if there were corrections. A few lines could only be based on a simplified model.
So by that principle, during the Octopus Free Sessions when I maximise all I can, including pushing the heat pump to draw up to 6kw, battery 6kw, appliances washing and what not, plus one or two electrical radiators, space heaters... my string is pretty damn stretched.
When I produce more solar power than I use, does it go to all the houses around mine that need it, or does it go to the grid then back to those houses? Wouldn't electricity take the shortest path and be drawn by my neighbour? From what I can tell, before I had my panels, I used google maps to check others, and can't see a great number of solar panels. I would say that out of 100 house, maybe 5 have panels.
If you’re interested in finding out which of your neighbours is on the same colour as you, get a mains driven baby monitor and play music on it, then visit your neighbours and plug in the receiver; if you hear the music, you’re on the same phase.
My home assistant plots some simple graphs of the voltage of my grid. It is never the same!
No idea if when we export it goes beyond our nearest neighbours.. a properly incentivised dno should be on top of that..
Posted by: @batpredMy home assistant plots some simple graphs of the voltage of my grid. It is never the same!
The same as what?
Do you mean that it continuously varies according to demand by houses connected to that local substation?
Because that's what you'd expect it to do of course!
And it will also vary according to the loading on the 11kV grid which supplies local substations.
If I plot a timeline of grid voltage taken from three LV monitors which are on different 11kV lines from the same Primary Substation,
I can see some variations which are common to all 3 locations.
That's where the voltage is affected by supply/demand over the wider region, possibly at 33kV or above.
The yellow highlighter box shows a voltage-dip due to a demand surge which affects the location of the Grey Monitor to a greater extent than Brown or Peach.
After a few months of running tests across the area covered by my own Primary Substation, I can now 'see' when cloud-cover has suddenly reduced solar generation
at a couple of villages over 5-miles away!
Posted by: @batpredNo idea if when we export it goes beyond our nearest neighbours.. a properly incentivised dno should be on top of that..
The DNOs Network Planners have in-house software which they use to estimate the likely effect of export to the grid when you make an application.
A similar software tool is used for LCT Applications (EV chargers and heat pumps).
But it's very unlikely that the DNO would know the actual grid voltages on their 11kV and LV levels.
I occasionally tell them what I find!
Amongst the factors which they input to their software calculator are
- distance between your house and the local substation
- total number of properties on that local sub-station
- the number of houses between you and the substation (divided by 3 to estimate the number on your phase)
- the conductor material your LV feed is made from (copper or aluminium)
- cross-sectional area of the conductors
Do you get the idea?
Save energy... recycle electrons!
Posted by: @transparentPosted by: @batpredNo idea if when we export it goes beyond our nearest neighbours.. a properly incentivised dno should be on top of that..
But it's very unlikely that the DNO would know the actual grid voltages on their 11kV and LV levels.
I occasionally tell them what I find!
That's exactly what is expected, that voltage etc will vary. But how can the DNO keep it within specific quality parameters, unless they monitor it?
Posted by: @batpredAmongst the factors which they input to their software calculator are
...
Do you get the idea?
What the folks were asking is if these components are smart enough to balance some aspects in near real time. Or monitor it, so they could take the peaks and troughs into account..
This is probably different in different parts of the DNO grid anyway.
Anyway, I'd better get back to work!
Posted by: @batpredBut how can the DNO keep it within specific quality parameters, unless they monitor it?
Let's first note what those parameters are.
They are defined by Sect.27 of the Electricity Regulations 2002.
Historically DNOs have maintained the voltage bands by simply having greater grid capacity than is required.
The physical grid is 'over-sized' and hence it takes a pretty massive 'event' to pull the grid outside specification.
But us consumers have to fund grid upgrades, and an overly-large capacity would cost Britain more than it can afford as we progress to 2050.
Electrification of domestic heating and transport is a key component of the Net Zero strategy.
We can't afford to monitor the lower levels of the grid.
It's not just the cost of fitting monitoring apparatus, but also creating the data-gathering comms network, with large data servers,
and a wide array of software tools to analyse the data trends and tell engineers what they need to know.
When I was first allowed access to a single grid monitor in 2018, I was receiving half-hour packages which gave me figures on 146 different measurements.
Some were averages over that 30-mins, whilst others were maxima or minima, according to what was the parameter being measured.
If I'd wanted to, I could've received data packages per minute, which was the granularity being held by the server.
That's a stunningly large quantity of data to handle if DNOs were to be incentivised to collect it!
In GB there are 230,000 ground-mounted local substations (11kV input)
and another 320,000 which are pole-mounted.
Many of the pole-mounted transformers are no less massive than those in ground-level compounds.
Typically you'd find them serving country estates, such as those owned by the National Trust.
It was the early experiments undertaken by the wealthy landowners of those estates which enabled engineers to calculate what was
required in order to light our towns and cities.
A landowner would install a primitive hydro-electric generator on a river in the estate, and run the output to a room-sized consumer unit
in the cellar of his house:
If there are going to be voltage variations on the grid which take it outside of the statutory limits, then it's more likely that they'll
be occurring in the furthest reaches of the network.
A commercial operation to measure and record that data would be monumental in size and cost.
Posted by: @batpredWhat the folks were asking is if these components are smart enough to balance some aspects in near real time.
Or monitor it, so they could take the peaks and troughs into account..
I'm sure the DNOs would love to have such a requirement put onto them.
The work would keep thousands of new engineers in work for a decade or more...
... and allow third-party Energy Agents to license that data in order to directly control our household appliances!
That's what the Smart & Secure Electricity System (SSES) team of civil servants are busy developing within DESNZ.
They intend allowing licensed agents to turn off domestic heat pumps during periods of high (national) demand.
However, domestic appliances are connected to the LV level of the grid, whilst national demand statistics are done at 275kv - 400kV.
You cannot mathematically extrapolate sensible interpretation and derive control algorithms at the two extreme ends of the electricity supply network.
I doubt that DESNZ had ever seen LV monitoring data before embarking on their mission, now dubbed "Consumer Led Flexibility" or CLF.
But I've had years of reading and interpreting such data.
So I bundled up a representative sample, wrote explanatory text, and sent it to them four weeks ago.
I do know how to use sparse data from a monitored grid to benefit demand-loading on the LV grid.
As a consumer, I'm a 'free thinker' and can consider all possibilities,
whereas the energy sector is based on how much profit can be made.
That's unlikely to reach a workable solution.
We discussed these issues extensively on the Heat Battery topic which was started by @wully
Save energy... recycle electrons!
- 26 Forums
- 2,265 Topics
- 50.6 K Posts
- 466 Online
- 5,924 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: My DIY Heat Pump installation
@polar-bear So from your diagram I see that you are usi...
By bontwoody , 22 minutes ago
-
Great idea. TOU includes Agile (mirroring wholesale)...
By Batpred , 25 minutes ago
-
RE: Electricity price predictions
So he must have a good team helping him in this.. ...
By Batpred , 1 hour ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Gone with Fernox Alphi-11, relieves the installers conc...
By Crimson , 3 hours ago
-
RE: Midea ASHP – how to set weather compensation
I can't do it for a Shelley device, but I can for Eastr...
By cathodeRay , 3 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
There is no such thing as a silly question! @toodles ...
By JamesPa , 5 hours ago
-
RE: UFH downstairs and radiators upstairs balancing question
Isn't this a great example of KISS!
By JamesPa , 5 hours ago
-
RE: Who has a V2G EV installation
Would that be a Chint RCD perhaps? Have a look at thi...
By Transparent , 5 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
11.2kW Ecodan Manufacturer: Misubishi Model: PUZ-WM...
By DRB01 , 18 hours ago
-
RE: Homely asking about Solar Panels.
@majordennisbloodnok I will report back with any develo...
By Toodles , 21 hours ago
-
RE: Mediation with RECC, what's your experience?
@editor Thank you, I really appreciate it! I've made ...
By TreeWizard , 23 hours ago
-
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Are you able to post a photo of that 180-litre cylinder...
By Transparent , 1 day ago
-
Agreed. It doesn't take all that much maintenance to ke...
By Majordennisbloodnok , 1 day ago
-
RE: Oil Boiler & Heat Pump Hybrid System
OK. Got it. As a fellow rural West Country resident, ...
By Transparent , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 2 days ago
-
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 2 days ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 2 days ago