Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Seplos Mason DIY Kit - Ancillaries - Advice
Posted by: @makia2023I'm told 48v as the cut off is the best options as that is approx 10% soc. Is this your view and can you provide any advised values for me to confirm what I've read (or not).
Also, I'm assuming Pylontech setting for the inverter should work with the seplos BMS?
Let's deal with the BMS settings first.
Very few people seem to question what is meant by an assertion that a BMS or inverter is somehow compatible with a product from a different manufacturer.
It might be referring to the voltage settings which are required for the connected devices...
... or it might be that data is being transferred across a CANbus or Modbus communications link.
That would enable measurements made by the BMS get reported/recorded by the App issued for the Inverter, or vice versa.
It may have nothing to do with protecting your precious batteries.
So beware!
There are also many views across the internet as to the 'best' parameters which you should apply to your LiFePO4 cells.
Will Prowse, who has been publishing hundreds of You Tube tutorials on inverters, solar panels and batteries over the years, currently suggests:
48V LiFePO4 Battery w/ BMS
- Absorption: 58V
- Float: 54.4V
- Inverter Cut-off: 42.8V-48V
Individual 3.2V LiFePO4 Raw Cell (for individual cell capacity testing)
- Absorption: 3.625V
- Float: 3.4V
- Low voltage disconnect for capacity testing: 2.5V
Whoever you choose to believe, the basic principle remains the same.
The Inverter/Charger parameters are those which you set to define the voltage envelope within which your batteries are charged and discharged.
The BMS parameters are set outside of those.
The BMS acts rather like a fuse. If there's a fault, or an error in configuring the inverter, then it will step in and disconnect the battery before any damage is done.
Putting it the other way around; The inverter parameters are inset from those of the BMS.
Here are the absolute maximum and minimum voltages you should consider using: with a LifePO4 cell.
The inner pair of voltages are those which are set in the inverter (or charger) per cell.
A cell should not fall below 2.6v, nor be charged higher than 3.55v
which equates to a range of 41.4v to 56.8v for a 16S battery (sixteen cells in series).
The outer pair of voltages are applied to the BMS.
If the charge/discharge system fails, then the BMS prevents any cell falling below 2.35v or rising above 3.65v
You might suppose that equates to a maximum voltage of 16 x 3.65v (58.4v) for a 16S battery.
But that's not so.
Remember, the BMS has sense wires across each individual cell.
It will cut off the charge-current as soon as the first cell in that battery rises to 3.65v.
In practice I wouldn't configure my inverters and battery BMS units to these absolute minimum and maximum values.
But everyone will have their own opinion on how much they wish to inset from those extremes.
Save energy... recycle electrons!
@robl when i assembled mine last year around June time i think it was, i used a piece of 18mm melamine (kitchen cupboard shelf) in the bottom, i used EVE 280AH cells and ignored the plastic strips but used the foam between the cells. Using 18mm melamine meant that i could then hold the cells in compression.
some others have 3d printed a mesh type support that fits neatly in the bottom of the case. i have also recently heard that Seplos have now sorted the issue ....?
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 293 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 15 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 15 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 18 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago