Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
I suggest you start by looking at the Sunsync Hybrid Inverters and then compare any others against that.
Sunsync have pioneered a concept of "Home Loads" which can be powered by your solar panels, whilst preventing any export to the grid.
These Home Loads are distinct from those appliances which are supplied from the inverter's Backup Load output.
A Backup Load will be powered from the storage battery in the event of a power outage, whilst the Home Loads will not.
Sunsync's zero-export credentials have been accepted by the Electrical Networks Association within the UK.
Thus you should easily obtain the required G99 approval from your regional DNO.
Note:
Sunsync is a company based in South Africa.
Their installation diagrams contain a mixture of colour codes for wiring Live, Neutral and Earth, which befit that country being referred to as "The Rainbow Nation"! 😉
To compound the problem, Sunsync inverters have three 240v AC mains connections, with their Live and Neutral wires using adjacent terminals.
Take care, and label everything!
Save energy... recycle electrons!
@transparent I've been recommended this setup for my existing hybrid inverters by someone in a group I am a member of. Any thoughts? It involves adding a third CT clamp, spliced onto the existing one to measure load
Sorry @batalto as it stands that diagram doesn't make sense to me.
1: You have PV panels connecting into a consumer unit, via two CTs in series..
Is that a DIN enclosure with DC-rated MCBs in it?
2: I don't understand how you can have two CTs wired in parallel.
The common type of mains CT (measuring current in an AC wire) produces a smaller proportional current.
The photo is a current-clamp which produces 50mA output when 100A (AC) passes through the centre square hole.
Within the instrumentation, that small current (<50mA) is connected across a resistor to produce a voltage.
The voltage is fed to an analogue to digital converter, which can then be read by the micro-controller.
Some CT's have the required resistor within the clamp itself.
They are therefore marked with a maximum voltage which will be produced at the rated max AC current.
Here are the wiring diagrams for each type
If you place two CTs in parallel, connected to the same port of the inverter, then those resistances are in parallel.
The A-to-D converter won't produce the required output.
Save energy... recycle electrons!
@batalto What is your experience of living with the Mason batteries? Have you had to perform any battery resets (e.g. the BMS got into a funny state)? I am considering getting a (vertical) Mason box for my Mother who is not at all technical, so would not be able to perform such maintenance tasks. In addition the location of the battery would be a bit tricky, so accessibility may be rather sub-optimal.
Honestly since I set them up I've not touched them at all - the only times I've turned them off was when I was messing around with the inverter and needed to make sure they were disconnected. I got the bluetooth versions so I could connected if I needed to, but I haven't. I did tweak the settings at the start for voltages/alarms, but it was a 5min job.
@chickenbig I'm not your tagged forum user but my Seplos system has been live since February this year. After the initial assembly, balancing and configuration I've had zero need to interact with it again other than checking the temperature during a cold snap (my battery is in an unheated garage). There have been no alarms/discontinuations in operation, seamlessly charging/discharging with a Solis inverter.
I would caveat this by saying that 3 months is admittedly a rather short period of time vs. the 10+ years that I hope the system to operate for.
I believe the latest Seplos BMS version comes with Bluetooth functionality which would reduce the importance of physical accessibility.
@batalto Thanks for the quick response. It is good to hear that they just work, and (in the other thread) good to see your grid usage is so low.
@korwraith Thank you for another data-point for the reliability of the system. How did the batteries cope with the cold-snap? Did you need to insulate the enclosure, or was there sufficient thermal mass (and heat generated during charge/discharge) to keep the batteries comfortable)?
Yes the bluetooth version would be handy when I visit the house. Remote monitoring would be ideal, although I suppose an internet-enabled inverter (e.g. Solis) would give some part of that.
The battery could be located behind a fridge (not ideal for access, but minimises the works needed to route cables to the inverter) or in the airing cupboard underneath the combi-boiler (not ideal from a water system failure perspective, and may hinder access to the gas meter) or finally in the garage (unheated, plus not sure where the inverter will be put, but it has plenty of room were she to want another battery). I'm not sure which to pick!
Posted by: @chickenbigI am considering getting a (vertical) Mason box for my Mother...
Really?
The Mason box is intended for Lithium cells.
It would be a bit uncomfortable for your Mother, even in vertical orientation. 😋
Save energy... recycle electrons!
Posted by: @transparentIt would be a bit uncomfortable for your Mother, even in vertical orientation. 😋
Unfortunately her balancing has been getting worse, but I think this happens with calendar ageing as well as use.
Posted by: @transparentPosted by: @chickenbigI am considering getting a (vertical) Mason box for my Mother...
Really?
The Mason box is intended for Lithium cells.
It would be a bit uncomfortable for your Mother, even in vertical orientation. 😋
Or is it that he is exchanging his mother for a vertical Mason box. 😋
Posted by: @chickenbig@korwraith Thank you for another data-point for the reliability of the system. How did the batteries cope with the cold-snap? Did you need to insulate the enclosure, or was there sufficient thermal mass (and heat generated during charge/discharge) to keep the batteries comfortable)?
The battery could be located behind a fridge (not ideal for access, but minimises the works needed to route cables to the inverter) or in the airing cupboard underneath the combi-boiler (not ideal from a water system failure perspective, and may hinder access to the gas meter) or finally in the garage (unheated, plus not sure where the inverter will be put, but it has plenty of room were she to want another battery). I'm not sure which to pick!
I added PIR insulation board to 5 of the 6 sides (attached with double-sided tape), that was enough to keep the cells above 10'C but only just. I may well add another board to the front panel of the box next winter; it's a bit more complicated as I'll have to make cut-outs for the screen/terminals but as the heat-generating BMS is directly behind that panel it should have an outsized effect vs. the other 5 sides.
I think the garage is often a good option for batteries; my garage is attached to my house so it doesn't get as cold as a detached garage which may be a consideration in your case.
(pic from a few months ago, I later added some aluminium tape along the joints to cover the gaps)
@korwraith - Could I perhaps suggest a method of insulating the front of the case which doesn't use a board covered with aluminium foil?
Also... when we say that the cells need 'balancing',
we're not expecting a 110Kg box to be left overhanging either side of wooden fulcrum! 🤣
Save energy... recycle electrons!
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 271 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 58 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 1 hour ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 15 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 15 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 18 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago