Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Moving growatt axe batteries
I was researching how to keep my loft area cool during summer months since I have two growatt 5kw axe stackable batteries. During this hot spell although I have a large door I can open into the dormer, and fans it’s been a challenge to keep the temp as low as I would prefer. Sitting at 37.5 as I detail.
given the latest regs I’m thinking it’s time to move them to the lower floor and into the utility room or kitchen. Can anybody give me the heads up on how difficult this would be. Should I make new battery leads, can I purchase leads to extend and can I purchase a new communication lead. The distance is minimum since they sit above the kitchen. Plan B would be to simply lift them out of the loft into the bedroom. The easiest option to be honest. A mission impossible to cool the loft and it keeps the insurance happy.
Battery leads are high current low voltage so they really want to be as short as humanly possible. The usual thing to do would be to move the inverter as well. If it's 37.5 your inverter is also probably aging far faster than it should.
If it's short enough and you don't mind a small hit then you can get/make new leads and extend/replace the communcation lead. You can also eliminate some of the additional losses by using thicker and alas pricier cables.
@etchedpixels just been informed that you can’t have batteries in a bedroom and mine are too big to fit in the utility room or kitchen. The batteries are unsuitable for outside and garage too far. So I guess it’s try and cool the loft better.
Currently viewing this topic 3 guests.
Recently viewed by users: Majordennisbloodnok 47 minutes ago.
- 26 Forums
- 2,689 Topics
- 63.1 K Posts
- 363 Online
- 7,099 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
You guys have it easy It's engineering: calories in...
By bobflux , 45 minutes ago
-
RE: Moving growatt axe batteries
@etchedpixels just been informed that you can’t have ba...
By David999 , 2 hours ago
-
RE: Anyone have experience with Daikin Multi+ for air to air & hot water?
Maybe, just maybe, if you are prepared to leave the doo...
By JamesPa , 2 hours ago
-
RE: How to heat a bathroom when using an air to air heat pump?
You can air/air a bathroom with a suitable ceiling or o...
By EtchedPixels , 2 hours ago
-
RE: Plug and play solar. Thoughts?
They've been extensively tested by folks like the Germa...
By EtchedPixels , 2 hours ago
-
RE: How do I set up Tesla Powerwall export for saving sessions since AI Takeover?
@papahuhu The decision as I say, was influenced very he...
By Toodles , 6 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
A summary of this history and discussion for those sear...
By Tim441 , 11 hours ago
-
RE: Electricity price predictions
@majordennisbloodnok Similar, although no heat pump h...
By IanMK13 , 13 hours ago
-
RE: vaillant arotherm plus - Failure - DHW
As expected it failed to run late yesterday with the sa...
By trebor12345 , 15 hours ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
Personally, I don't always rate the "payback on install...
By HeatNoob , 1 day ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thanks. Will be sure to keep a record of s...
By bontwoody , 1 day ago
-
@jamespa Well, something along the lines of "three buse...
By ian33a , 1 day ago