Posted by: @transparent

Posted by: @batpred

In my case, my voltage reads are now 240V. They should be 230V, so should I consume less? 

...

The 'Declared Voltage' for LV is currently stated as 230v RMS

..

Since inverters have been pre-certified to G98/G99, they are more likely to decouple themselves from the grid due to low-volts detection.

Ok, my Solis can work to a huge variety of global grid standards. At the moment, it is working on G99, it is something that the engineers asked me early on to confirm before it connected to anything beyond the battery. Is the name for this new standard cenelec something or has bsi come up with a different prefix? I believe this type of info on grid standards is deployed to inverters via firmware updates. 

A small setup like mine (where I do not think I will ever have more than 4kw solar with current panels) will just be expected to have an inverter that backs off if the local grid has a problem, or am I missing anything? To enable normal recovery of the grid, after which my Inverter would connect back to the grid? 

It would be nice to be able to confirm that the standard that will replace g99 is in a future Solis update.. 

 


16kWh Seplos Fogstar battery; 8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
(@batpred)
Honorable Member Member
Joined: 12 months ago
Posts: 335
Topic starter  

Given the underspent for the budget of the Solis inverter and battery 😀 😉, we are considering  the next step: adding PV panels. 

 

Just wanted to share our schedule of works and get views:  

"We are taking care of the G99 approval with UK Power Networks. We expect to get SEG 8kw export via smart meter in a few weeks..

What we are looking for:
 
An estimate for a PV install, to have >4 kWp on the 23 m² flat felt/bitumen roof (the loft has been converted), tying into the existing Solis S6-EH1P8K-L-Plus hybrid inverter + 16 kWh battery.

We assume you would use flat-roof ballasted frames (without penetrations) and a one-storey rear scaffold mounted in the back extension only. The roof has no shading except a small chimney. 

Essentially this may be the PV system that we need: Array size: ~10–12 panels @ 420–440 W on 10–15° tilt frames without parapet ⇒ 4.2–5.3 kWp. 
 
We are interested in supply & fit: 
A. Panels & mounting (flat-roof ballasted trays/frames, rails, clamps, ballast). Mounting on felt/bitumen. Would you install it as 2 strings into the existing hybrid inverter? 
B. Balance of system & works (cables, isolators, DC combiner if used, roof protection mats, labelling, testing & commissioning into existing Solis) 
C. Scaffolding (one-storey rear access, small run, 1 week hire?) 
D. Bird spikes along top edge (say 6–12 m) 
"

16kWh Seplos Fogstar battery; 8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
(@batpred)
Honorable Member Member
Joined: 12 months ago
Posts: 335
Topic starter  

So I submitted the SEG application to Octopus. Fingers crossed, perhaps it will not be tripped by any silly building regs "checking the checkers" process.

I did not manage to confirm if the G99 standard for low voltage is 230V. And is it replacing G59? 

My DNO (UK PN) seems to supplying 240V in my area... Should my inverter be set to work at G59 in the meantime?

Or would there be another name for UK's 230V?

From what I see, the G99 Type A from ENA is a relevant document.. 


16kWh Seplos Fogstar battery; 8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2799
 

G59 has already been replaced by G98 five years ago.
It's the type certification against which manufacturers of inverters are required to have their products tested.

G99 applies to installations which have more than one G98-certified device,
or where the electricity to be exported exceeds 16A per phase.

 

The voltage level of the mains supply isn't defined within the EREC G-standards.
The 'Declared Voltage' is already referenced to 230v, and not 240v AC

Thus the interpretation of the Electricity Specifications [...] Act

GridVoltsLaw

is that LV must be between 216.2v and 254v AC, single phase.

 

UKPN, in common with all other DNOs, would normally keep the LV supply at 240v.

That allows greater voltage-drop to occur before G98-certified equipment would remove itself from the grid.

 

The Electrical Networks Association (ENA) is discussing the possibility of reducing the notional grid voltage to actually be 230v.
That wouldn't require any additional legislation of course.

However, for appliances which adjust their electricity-demand based on watts, such as EV chargers, PCs, televisions and heat-pumps,
the grid current would increase to compensate for the lower voltage.

That creates problems on the 11kV level of the distribution grid...
... which might be reflected in more outages due to thermal overload.

There is no easy answer within the scope of DNOs.


This post was modified 2 weeks ago 2 times by Transparent

Save energy... recycle electrons!


   
ReplyQuote
(@batpred)
Honorable Member Member
Joined: 12 months ago
Posts: 335
Topic starter  

A quick check shows the Solis inverter includes G59/3, G98 and G99 settings.

Based on the fact that the DNO approved 8kW export (so over 32Amp), I understand that I should keep it set to G99. 


16kWh Seplos Fogstar battery; 8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2799
 

If the Solis inverter has a configuration setting labelled G99, then by all means leave it set for that.

But it's a misinterpretation of the regulations by Solis.
Their inverter can't 'know' what other in-house devices are counting towards the export levels approved by a DNO.

This is the sort of detail I feed back to manufacturers.
In this case it would perfectly satisfactory to have configuration 'G98' because that's what they were required to test the inverter for.

Provided that setting still allows you to configure export levels above 16A/phase, then there is no reason why there should be an option to define 'G99' in that field.


Save energy... recycle electrons!


   
ReplyQuote



(@batpred)
Honorable Member Member
Joined: 12 months ago
Posts: 335
Topic starter  

Posted by: @transparent

If the Solis inverter has a configuration setting labelled G99, then by all means leave it set for that.

But it's a misinterpretation of the regulations by Solis.
Their inverter can't 'know' what other in-house devices are counting towards the export levels approved by a DNO.

This Solis inverter being rated 8kw and (I expect, as I did not test) also allowing export of max 8kw, it should be operating to g99 when connecting to the grid.

The solis does allow the voltage on the backup port to be independently set. But that is only effective when the grid port does not sense power and the port is fed from dc sources  (perhaps also if the grid power is outside the expected parameters). In normal circumstances, the backup port power mirrors the grid input. 

 