Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Viessmann heating issues
Hi all,
new to the forum and looking for some help please as I’m a bit at loss with my heating system.
In short, I run a 35KW Viessmann boiler that’s operates by a Vitotronic 200-H. The system has a LLH and 3 heating circuit pumps with mixer valves (one for underfloor heating, one for downstairs rads and one for upstairs rads), plus another pump for the hot water tank. Everything is weather compensated.
My issue is essentially that not enough heat is being drawn from the low loss header. The hot water tank takes around 2-3hrs (!!) to get to it’s desired 50c temp, and on the heating circuits, the flow temp never really gets above 40, even if the boiler is producing 75c+.
As an experiment we removed the LLH, which seemed to improve things, however the boiler was then constantly running at 75c (rather than running at reduced temps of ~50-60 due it’s weather compensation), whilst the radiators were still only getting up to ~40.
We’ve since re-installed the LLH which makes the boiler operate like it should (running at Lower temps), but now the mixer valves seem to be stuck on cold (it’s 8c outside) and having a flow temp. of no more than ~25. I’ve tried increasing the heating slope and curve and whilst this makes the boiler temps increase, the mixers refuse to move and flow temps are low. The LLH is boiling hot but no heat seems to be leaving this.
Any ideas? Could the LLH have failed (there was a lot of rust in it when we cleaned it out)? Could there be sludge/build up in the system causing this?
Any ideas/suggestions would be very welcome!
thanks in advance!
It rather sounds as though you have a build up of sludge from what you say about the LLH. Has the system ever been power flushed? Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles we had it done last year (the magnet one, rather than a power flush) but there does seem to be sludge around as there is still lots of bits and fillings in the small magnaclean filter.
At the moment, we have a huge loss of heat between the LLH and the DHW and virtually a 100% loss between the LLH and the heating circuits. When the LLH was removed, it was better (got ~40c into the heating circuits) but the boiler wasn’t modulating then.
@hubb84 The Magnaclean filter is for everyday removal of particles of any ferrous material circulating in your pipework; I doubt that even if you cleaned out the filter daily, you would ever be likely to achieve a fraction of the muck removal that a power flush would. I’m not trying to suggest that this is your ONLY problem but the fact that you found a lot of sludge in the LLH and the Magnaclean also picked up some particles seems to suggest their is muck in your system and it isn’t Yorkshire Brass!
Your pump would appear to be able to deliver the heat you want but as it is not flowing into the radiators properly (or the DHW tank) it rather suggests a very restricted flow. This may be muck, it may be valves that aren’t opening fully - both aspects are worth checking I think. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles ok thank you. I’ve booked a power flush for next week and see where it goes from there. I agree that there seems to be some sort of restriction, so it’s just trying to find what and where.
will update next week!
ok so update from today: they tried to hook up a Magnaclean (the big one) on the return but we weren’t getting any, or very little, flow. This would explain why things take so long to warm up, or don’t get warm at all.
We checked all pumps and one (on the downstairs radiator circuit) has failed. Whilst this makes sense for not having any flow on that circuit, I don’t understand why we had the same issue when turning this off and running the other circuits separately.
Took two radiators off and both were quite full of stuff, but when we tried to flush the system just with the mains pressure, it was clear.
They’re hesitant to do a power flush as we have a lot of plastic piping too…anyone have experience with this?
At a bit of a loss now as to what to try/do next.
@hubb84 No experience here I’m afraid, but I think your work has confirmed that you have sediment build up. If plastic piping isn’t up to a power flush, might there be a chemical approach? I have in mind using a solvent or sludge softening agent of some sort (if there is such a thing???) I would imagine the likes of Fernox would be the people to ask about such a solution.
Perhaps the pump that failed died of congestion? Are there any power flushing schemes that use suction rather than pressure? Sorry no solution but lots of questions from someone with very little knowledge of such a problem. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@hubb84 Try looking at powerflushassociation.com. They may have a solution to your need to flush out plastic pipes. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 960 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 10 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 10 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 14 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 14 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 15 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 16 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 19 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 19 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago