Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide

172 Posts
9 Users
16 Reactions
18.9 K Views
(@alfapat)
Estimable Member Member
Joined: 3 years ago
Posts: 187
 

@jamespa 

I read a post on here about converting  a four port Buffer to by-passing and making a volumizer . What is the advantage of including a volumizer as opposed  to by passing and linking ch return through the buffer via the same level and returning the flow to the HP pump as to entering at the top of the tank and back to HP at the bottom.

I remember your drawing and just realised reading similar that I should know more .
I have contacted a local plumber who is yet to visit , to discuss my alterations .



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4864
 

The volumiser provides extra system volume which may reduce cycling or may be necessary for defrost if your system doesn't otherwise have sufficient water in it to meet the specifications for your heat pump.

It may be totally unnecessary, but it does no harm.  So it's the safe option if you have a buffer.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@alfapat)
Estimable Member Member
Joined: 3 years ago
Posts: 187
 

Posted by: @jamespa

The volumiser provides extra system volume which may reduce cycling or may be necessary for defrost if your system doesn't otherwise have sufficient water in it to meet the specifications for your heat pump.

It may be totally unnecessary, but it does no harm.  So it's the safe option if you have a buffer.

That’s good, so what’s the difference between the lower sketch and upper onfeaturing bypass. 
Scan_0014.pdf

 



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4864
 

Posted by: @alfapat

Posted by: @jamespa

The volumiser provides extra system volume which may reduce cycling or may be necessary for defrost if your system doesn't otherwise have sufficient water in it to meet the specifications for your heat pump.

It may be totally unnecessary, but it does no harm.  So it's the safe option if you have a buffer.

That’s good, so what’s the difference between the lower sketch and upper onfeaturing bypass. 
Scan_0014.pdf

 

The second one avoids the possibility that all the hot water collects at the top and is bypassed by the returning flow.

Not a lot really, but perhaps worth doing. I can't quantify it.

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@alfapat)
Estimable Member Member
Joined: 3 years ago
Posts: 187
 

Posted by: @jamespa

Posted by: @alfapat

Posted by: @jamespa

The volumiser provides extra system volume which may reduce cycling or may be necessary for defrost if your system doesn't otherwise have sufficient water in it to meet the specifications for your heat pump.

It may be totally unnecessary, but it does no harm.  So it's the safe option if you have a buffer.

That’s good, so what’s the difference between the lower sketch and upper onfeaturing bypass. 
Scan_0014.pdf

 

The second one avoids the possibility that all the hot water collects at the top and is bypassed by the returning flow.

Not a lot really, but perhaps worth doing. I can't quantify it.

 

h OK James interesting , might include that in the plan.

 



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4864
 

Posted by: @alfapat

Posted by: @jamespa

Posted by: @alfapat

Posted by: @jamespa

The volumiser provides extra system volume which may reduce cycling or may be necessary for defrost if your system doesn't otherwise have sufficient water in it to meet the specifications for your heat pump.

It may be totally unnecessary, but it does no harm.  So it's the safe option if you have a buffer.

That’s good, so what’s the difference between the lower sketch and upper onfeaturing bypass. 
Scan_0014.pdf

 

The second one avoids the possibility that all the hot water collects at the top and is bypassed by the returning flow.

Not a lot really, but perhaps worth doing. I can't quantify it.

 

h OK James interesting , might include that in the plan.

 

It occurs to me that the other way up might be even better, feed water in from rads at bottom, take water out to hp at top.  In reality probably little difference between the two but I would definitely have one at the top and the other at the bottom.

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@alfapat)
Estimable Member Member
Joined: 3 years ago
Posts: 187
 

Ok Guys James,

I cannot get anyone to respond to a request locally to come and have a look at converting a buffer tank to a Volumizer therefore eliminating the constant mixing in this . 

Is it the time of year or lack of committment at this time of year . Due to colder temps and time of year?

The reason being costs normally should have gone down daily given the OAT at this time of the year. So trying to get a plumber to submit his time and have a look at my system seems impossible . 

Shoud I revert to my older system in involving opening lockshields and shuttin down TRV's to suit rooms . Certainly cheaper than exposing the flaw with the present set up or try and get a company to look at the proposed set up meantime .



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4864
 

Before answering that, what do you feel is the problem which you would solve by reverting.  Earlier on you seemed to have made some progress albeit that we both recognise its still not optimal.  Why not leave it at the point of maximum progress, what do you think will improve if you change it back?


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@alfapat)
Estimable Member Member
Joined: 3 years ago
Posts: 187
 

The old problem we had certainly was not right , but while it was using TRV's and open lockshieldsand the buffer, the costs were more controlled but still expensive as they were shutting down the system and then the HP had to make it up. I know from my Bills that they are higher than before but only because I am in this in between stage that now the temperatures in the house are more consistant the the whole idea of bypassing the the tank and or making it a volumiser has to be completed in order that the system is optimised , but I cant get someone to do it . I am committed to completing it , and then savings will be even more , Im sure of it , I am down the a flow temp of 40c now , previously 42 for two weeks,  meanwhile the daytime temperatures are helping things a little now.



   
ReplyQuote
(@heacol)
Prominent Member Contributor
Joined: 5 years ago
Posts: 415
 

@alfapat PM me and I can help, you will just neeed to find a standard plumber, not a specilaised one.



   
👍
2
ReplyQuote
(@alfapat)
Estimable Member Member
Joined: 3 years ago
Posts: 187
 

I have messaged you . 

Thank you in anticipation of your help .



   
ReplyQuote
(@alfapat)
Estimable Member Member
Joined: 3 years ago
Posts: 187
 

Posted by: @heacol

@alfapat PM me and I can help, you will just neeed to find a standard plumber, not a specilaised one.

 



   
ReplyQuote