Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Error on Immersun – Error 8 Load Short Circuit
Well the unit has been repaired and returned after what must have been literally a few hours back at Immersun.
I asked for a detailed service report and got this:
"Multiple fairchild transistors and 1x T3 Transformer was found to be non-responsive via extensive repeat testing protocol, they appear to have been overloaded at some point in prior operation"
I have yet to replace and recommision it but hope this is the end of the saga for a long long time.
I will probably change the immersion heating element and stat too as a precaution.
Jules
@julesmp8 fingers crossed.
I have to say our Immersun is quite noisy with loads of weird high pitched sounds and buzzing coming from the various components. By extension our Solar iBoost was completely silent.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@editor Hi, I helped fix a friend's Immersun recently. He had completely removed it and when we provided power it showed an error code. I took out all 4 of the big power transistors and tested them with a multimeter, just measuring resistance between collector and emitter, in either direction. One was open circuit, we found some in the same series but with higher capacity (current). My friend bought 4 of them and I soldered them in which fixed the problem. We went for the transistors because he had read on a forum others had blown. If I didn't know that I would have gone for the electrolytic capacitors first. NB there was no visible sign of the fault (no charring etc). The Immersun was just out of warranty and I think they wanted £160 just to look at it!
@mikeavison that's a great fix. Well done, and £160 - transistors saved.
I don't suppose you took photos of the transistors you replaced as an additional reference to this post?
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@editor Hi, not as clever as you might think! In taking a picture for you I now note that the four we took out were not identical but having reviewed the data sheets of them both I think they were so similar they probably came out of the same storage bin at Immersun and randomly installed. In my defence, I was in need of laser eye surgery at the time to clear some scum which was impeding my vision and the text on these transistors is very faint unless you get the light at just the right angle. Unfortunately I don't have a note of the ones we replaced them with but I have sent a message to my friend (who I was mending the Immersun for, and who ordered the replacements) and I will post again if he can remember the ID.
The data sheets of the 2 types we took out are at:
and https://www.onsemi.com/download/data-sheet/pdf/fgh40t65spdcn-d.pdf
I suspect the ones we put in might have been something like:
https://www.onsemi.com/download/data-sheet/pdf/fgh60t65sqd-f155-d.pdf
Which has similar characteristics except is able to handle 60A instead of 40A
I hope this is of some help.
PS Incidentally, just for interest, these transistors are a sort of hybrid I had never heard of before Insulated Gate Bipolar Transistors (IGBT). The input is like a MOSFET and the output is like a bipolar junction transistor.
Addendum / correction : we have checked the ID of the transistors we used and they were FGH 50T65 UPD. I used 4 of these to replace all 4 of the large transistors in the unit, i.e. the ones in the photograph above. It was about a month ago and still working fine, of course I don't know how long it will carry on for but I expect it will outlast a unit with the original transistors since these have a higher rating (50A compared with 40A). If you have a broken Immersun it might of course not be the transistors that have blown but reading blogs elsewhere it seems to be a common cause of failure. You can check before you buy but it does mean unsoldering, then you only need a multimeter to check them. If it is not them I would replace all the electrolytic capacitors (they are not expensive). There is not easy way to thoroughly check electrolytics, you would have to feed them DC with ripple at or near the specified maximum voltage and then measure the leakage as they got hot, not really worth the effort, just replace them.
- 27 Forums
- 2,787 Topics
- 65.8 K Posts
- 1,643 Online
- 7,192 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent I was replying about the accuracy of "AI" ...
By EtchedPixels , 59 minutes ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
I too found the same thing, so reduced the hysteresis. ...
By trebor12345 , 1 hour ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
@cathoderay The 'constant' has dimensions. Its the ...
By JamesPa , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
SunSynk hybrid inverters also have the capability to as...
By Transparent , 2 hours ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
If you've got a sash window or a door you can remove th...
By EtchedPixels , 3 hours ago
-
RE: Heat Geek Zero Disrupt: Are We Sleepwalking Into Another Race to the Bottom?
Roughly how most air/air is done except that step 3 doe...
By EtchedPixels , 3 hours ago
-
RE: Nook batteries from Octopus
@batpred If your energy use is low enough that just get...
By EtchedPixels , 4 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
I suspect 4 yrs ago, their approach had not got to this...
By Batpred , 4 hours ago
-
RE: battery storage without solar
Also don't forget that in you may not be able to use th...
By JamesPa , 14 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
One practical safeguard is to separate the calibration ...
By EnergyStorageTech , 15 hours ago
-
RE: tepeo ZEB UK Support & Info Thread
There is at least one large scale system in this catego...
By Toodles , 1 day ago
-
RE: Getting closer to a finished Haier system
Apart from sealing the external Primary Pro joints and ...
By Singlespeed , 1 day ago
-
RE: Air-to-Air Heat Pumps & Air Conditioning: UK Heating and Cooling Q&A
Our latest Homeowners’ Q&A episode has just dropped...
By Mars , 2 days ago
-
RE: Vaillant ecoTEC Plus with sensoCOMFORT and weather compensation
Yes, its described in the sensocomfort manual. Its als...
By JamesPa , 2 days ago
-
RE: Heat Geek installations: share your experiences
My summary, highlighting the oddities.
By Batpred , 2 days ago