Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
GSHP COP with and without backup boiler
Good morning,
I have recently had a GSHP installed (Vaillant Flexotherm) including separate electric meters for the GSHP and GSHP Backup boiler. I also have a Sontex heat meter installed.
I have been monitoring the COP of the system daily to try and improve efficiency. The problem is that the efficiency increase greatly on the days the backup boiler is turned on once per week (for legionella) which I'm struggling to understand?? As far as I'm aware the backup boiler roughly produces 1kw of heat per 1kw electric input.
I'm calculating COP as follows. Heat Kw/ (GSHP Electric + Backup boiler Electic)
For example on the days the backup boiler is not on I'm averaging ~3.8 COP
The days the backup boiler is on I'm averaging ~4.2 COP
Any ideas will be greatly appreciated.
Happy to provide more info if needed?
That does sound surprising!
I expect that you're right - the backup heater is likely to be an inline immersion somewhere.
How do you measure the electrical energy? How well are the Sontex temperature probes attached (perhaps a photo?).
Which Flexotherm unit is it - I think they come in 5/8/11kW. So far as I can see, the units are simple on/off gshp ones with impressive COP, not inverter units(correct me if I'm wrong!).
If you run the unit continuously for (eg) an hour (make sure your thermostat is high) without backup heater, what heat energy do you get, and what Electrical does it take?
Ditto, but now with the heater on - what heat and electrical energy?
Thanks for the reply.
The electrical energy is measured via separate electrical meters, one for renewable (i.e. GSHP) and one for non renewable (i.e. backup boiler). I have attached a photo of this and the heat meters. Also the photo of where the sensors are connected.
It is a Flexotherm 11kw. It is sold as having a COP of 4.73 @ 35c flow temp. I'm unsure about whether it has an inverter.
I've run the pump with and without the backup boiler on.
26/01 - Backup boiler off - Electric 44.38kw; Heat 170kw; COP 3.83
30/01 - Backup boiler on - Electric 46.1kw (of which 5.24kw backup boiler); Heat 219kw; COP 4.75
One thought I had was that the DHW when being run by the GSHP was killing the efficiency/COP somehow? Maybe flow temps too high??
I don't think it's an inverter model - this says not:
https://www.toptenuk.org/consumer/product/view/VaillantGmbHflexoTHERMexclusiveVWF874
Perhaps you're right, and it's a "marginal COP" thing due to the DHW temperature. It seems very surprising. How hot does it run to for DHW?
Can you separate out hot water and heating? I assume that you have a hot water tank - does it have it's own immersion heater that you could use for a while, and stop the GSHP trying to heat it. Then run the experiment again - measure Heat and Elec both with and without the backup heater ?
Yes we have a hot water tank so I will try your suggestion of using the immersion to isolate the Heating and DHW.
The flow temps get up to 60c when the DHW is on. Looking at the 'Marginal COP idea' that could make sense if the flow temps are so high its actually less efficient.
I'll let you know how I get on.
- 27 Forums
- 2,746 Topics
- 64.5 K Posts
- 375 Online
- 7,149 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Have you considered keeping your FF boiler and suppleme...
By Old_Scientist , 54 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@toodles I invested on Miele a pair of frodge frozor wh...
By AgentGeorge , 2 hours ago
-
RE: Flushing system, cleaning and inhibitor
Flush and fill all complete. Octopus kindly gave us a...
By Old_Scientist , 3 hours ago
-
RE: Wood burner with ASHP - direct air?
For what it's worth I installed a wood burner in this o...
By BlizzardGreen , 4 hours ago
-
@editor Thanks for your response and recommendations. ...
By DavidB , 11 hours ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
I think I saw a diagram for an exhaust air dhw tank wit...
By JamesPa , 1 day ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks, however that's an answer to a subtly different ...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Such elegant symmetry. look at my lumpy bag of...
By Papahuhu , 4 days ago
-
RE: PV and battery long payback - sense check query
Quite probably not, but you can get a 32A relay and a S...
By JamesPa , 4 days ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s Look forward to making contact soon! Regards, To...
By Toodles , 4 days ago
-
I don't notice mine defrosting, and most of the time Im...
By JamesPa , 5 days ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
Kind of you, @calumm, but it was @f1p who did the heavy...
By Majordennisbloodnok , 6 days ago