Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
GSHP COP with and without backup boiler
Good morning,
I have recently had a GSHP installed (Vaillant Flexotherm) including separate electric meters for the GSHP and GSHP Backup boiler. I also have a Sontex heat meter installed.
I have been monitoring the COP of the system daily to try and improve efficiency. The problem is that the efficiency increase greatly on the days the backup boiler is turned on once per week (for legionella) which I'm struggling to understand?? As far as I'm aware the backup boiler roughly produces 1kw of heat per 1kw electric input.
I'm calculating COP as follows. Heat Kw/ (GSHP Electric + Backup boiler Electic)
For example on the days the backup boiler is not on I'm averaging ~3.8 COP
The days the backup boiler is on I'm averaging ~4.2 COP
Any ideas will be greatly appreciated.
Happy to provide more info if needed?
That does sound surprising!
I expect that you're right - the backup heater is likely to be an inline immersion somewhere.
How do you measure the electrical energy? How well are the Sontex temperature probes attached (perhaps a photo?).
Which Flexotherm unit is it - I think they come in 5/8/11kW. So far as I can see, the units are simple on/off gshp ones with impressive COP, not inverter units(correct me if I'm wrong!).
If you run the unit continuously for (eg) an hour (make sure your thermostat is high) without backup heater, what heat energy do you get, and what Electrical does it take?
Ditto, but now with the heater on - what heat and electrical energy?
Thanks for the reply.
The electrical energy is measured via separate electrical meters, one for renewable (i.e. GSHP) and one for non renewable (i.e. backup boiler). I have attached a photo of this and the heat meters. Also the photo of where the sensors are connected.
It is a Flexotherm 11kw. It is sold as having a COP of 4.73 @ 35c flow temp. I'm unsure about whether it has an inverter.
I've run the pump with and without the backup boiler on.
26/01 - Backup boiler off - Electric 44.38kw; Heat 170kw; COP 3.83
30/01 - Backup boiler on - Electric 46.1kw (of which 5.24kw backup boiler); Heat 219kw; COP 4.75
One thought I had was that the DHW when being run by the GSHP was killing the efficiency/COP somehow? Maybe flow temps too high??
I don't think it's an inverter model - this says not:
https://www.toptenuk.org/consumer/product/view/VaillantGmbHflexoTHERMexclusiveVWF874
Perhaps you're right, and it's a "marginal COP" thing due to the DHW temperature. It seems very surprising. How hot does it run to for DHW?
Can you separate out hot water and heating? I assume that you have a hot water tank - does it have it's own immersion heater that you could use for a while, and stop the GSHP trying to heat it. Then run the experiment again - measure Heat and Elec both with and without the backup heater ?
Yes we have a hot water tank so I will try your suggestion of using the immersion to isolate the Heating and DHW.
The flow temps get up to 60c when the DHW is on. Looking at the 'Marginal COP idea' that could make sense if the flow temps are so high its actually less efficient.
I'll let you know how I get on.
- 27 Forums
- 2,799 Topics
- 66.2 K Posts
- 2,408 Online
- 7,206 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: How will removing the standing charge on gas bills benefit heat pumps?
@toodles GIGO always stands! My Cosy 6, as you can...
By Watcher , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
@editor Mystery solved to some extent. Need to selec...
By dansus , 5 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
Interestingly we had an internet outage about a month a...
By Rob of York , 9 hours ago
-
RE: Double or Triple Glazed Windows?
Posted by: @singlespeed With 9 years repairing windo...
By Rob of York , 9 hours ago
-
@transparent we’re still running a secure version of PH...
By Mars , 13 hours ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
Much longer than that here. The heating isn't even on. ...
By bobflux , 1 day ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Obviously the weather is changeable but there's a defin...
By Singlespeed , 1 day ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@rob-of-york I must admit that when we had a Daikin hea...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
Get the Renewable Heating Hub heads-up on WhatsApp. I...
By Mars , 1 day ago
-
RE: Safety study for plug in batteries out to tender - looks like Q3 2027 at best before legal
@editor I pointed out to the one of the Fuse execs that...
By dansus , 1 day ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews As well as loft insulation, there are othe...
By Rob of York , 1 day ago
-
RE: BT cuts you off, Plusnet blames Openreach... welcome to “seamless” broadband switching
Both of which (in most cases) use Openreach for the las...
By JamesPa , 1 day ago
-
RE: Renewables & Heat Pumps in the News
Yes, this is a swiss and german standard I believe, Vai...
By Batpred , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@editor FWIW my problem was resolved, eventually, after...
By BigFish , 2 days ago