Good morning,
I have recently had a GSHP installed (Vaillant Flexotherm) including separate electric meters for the GSHP and GSHP Backup boiler. I also have a Sontex heat meter installed.
I have been monitoring the COP of the system daily to try and improve efficiency. The problem is that the efficiency increase greatly on the days the backup boiler is turned on once per week (for legionella) which I'm struggling to understand?? As far as I'm aware the backup boiler roughly produces 1kw of heat per 1kw electric input.
I'm calculating COP as follows. Heat Kw/ (GSHP Electric + Backup boiler Electic)
For example on the days the backup boiler is not on I'm averaging ~3.8 COP
The days the backup boiler is on I'm averaging ~4.2 COP
Any ideas will be greatly appreciated.
Happy to provide more info if needed?
That does sound surprising!
I expect that you're right - the backup heater is likely to be an inline immersion somewhere.
How do you measure the electrical energy? How well are the Sontex temperature probes attached (perhaps a photo?).
Which Flexotherm unit is it - I think they come in 5/8/11kW. So far as I can see, the units are simple on/off gshp ones with impressive COP, not inverter units(correct me if I'm wrong!).
If you run the unit continuously for (eg) an hour (make sure your thermostat is high) without backup heater, what heat energy do you get, and what Electrical does it take?
Ditto, but now with the heater on - what heat and electrical energy?
Thanks for the reply.
The electrical energy is measured via separate electrical meters, one for renewable (i.e. GSHP) and one for non renewable (i.e. backup boiler). I have attached a photo of this and the heat meters. Also the photo of where the sensors are connected.
It is a Flexotherm 11kw. It is sold as having a COP of 4.73 @ 35c flow temp. I'm unsure about whether it has an inverter.
I've run the pump with and without the backup boiler on.
26/01 - Backup boiler off - Electric 44.38kw; Heat 170kw; COP 3.83
30/01 - Backup boiler on - Electric 46.1kw (of which 5.24kw backup boiler); Heat 219kw; COP 4.75
One thought I had was that the DHW when being run by the GSHP was killing the efficiency/COP somehow? Maybe flow temps too high??
I don't think it's an inverter model - this says not:
https://www.toptenuk.org/consumer/product/view/VaillantGmbHflexoTHERMexclusiveVWF874
Perhaps you're right, and it's a "marginal COP" thing due to the DHW temperature. It seems very surprising. How hot does it run to for DHW?
Can you separate out hot water and heating? I assume that you have a hot water tank - does it have it's own immersion heater that you could use for a while, and stop the GSHP trying to heat it. Then run the experiment again - measure Heat and Elec both with and without the backup heater ?
Yes we have a hot water tank so I will try your suggestion of using the immersion to isolate the Heating and DHW.
The flow temps get up to 60c when the DHW is on. Looking at the 'Marginal COP idea' that could make sense if the flow temps are so high its actually less efficient.
I'll let you know how I get on.
- 26 Forums
- 2,338 Topics
- 52.8 K Posts
- 408 Online
- 5,994 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Has anyone tried using the Smart Tariff Control on the ...
By ChandyKris , 3 hours ago
-
RE: What a Bad Heat Pump Installation Looks Like
I was sent this by an installer and honestly, it’s peak...
By Mars , 4 hours ago
-
RE: Grant Aerona Short Cycling
@toodles Billy the big bahco spanner lovingly applied (...
By Grantmethestrength , 5 hours ago
-
RE: Experience with Mitsu Par 50/60 Wireless Controller
The 27°C request doesn't boost the weather compensation...
By Sheriff Fatman , 7 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Oh and it was installed by Stevie Wonder!
By Grantmethestrength , 9 hours ago
-
There seems to be plenty of evidence to support this. ...
By JamesPa , 16 hours ago
-
RE: One Year Review: Grant 13kW ASHP - A Catalogue of Errors
@solenoid it sounds like you are making progress. No n...
By JamesPa , 17 hours ago
-
RE: LiFePO4 lithium battery fires and explosions
@iaack — thanks, a useful video. They do make it clear...
By cathodeRay , 17 hours ago
-
RE: How good is the app support for your heat pump?
I think you are right about the ebus stick. It's cert...
By JamesPa , 1 day ago
-
RE: My DIY Heat Pump installation
@majordennisbloodnok Element-ary my Dear Major.
By Toodles , 1 day ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
Yes, you can work out a lot from a plot of FT. Interes...
By JamesPa , 2 days ago
-
Welcome to the forums @isaac. What you’re describing is...
By Mars , 2 days ago
-
Win an Eve Smart Home Bundle worth over £350!
Win an Eve Smart Home Bundle worth over £350! ...
By Mars , 2 days ago
-
RE: Is your heat pump insured?
I chose Tesco in the end. Unambiguously cover HP, PV an...
By Davesoa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk You can get an idea of if your flow and return...
By SimonF , 2 days ago
-
This Solis inverter being rated 8kw and (I expect, as I...
By Batpred , 2 days ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I have one fancoil in an otherwise all radiator system....
By JamesPa , 2 days ago
-
RE: Electricity price predictions
That's understandable...but I was referring to our 'oth...
By Transparent , 2 days ago