Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
GSHP COP with and without backup boiler
Good morning,
I have recently had a GSHP installed (Vaillant Flexotherm) including separate electric meters for the GSHP and GSHP Backup boiler. I also have a Sontex heat meter installed.
I have been monitoring the COP of the system daily to try and improve efficiency. The problem is that the efficiency increase greatly on the days the backup boiler is turned on once per week (for legionella) which I'm struggling to understand?? As far as I'm aware the backup boiler roughly produces 1kw of heat per 1kw electric input.
I'm calculating COP as follows. Heat Kw/ (GSHP Electric + Backup boiler Electic)
For example on the days the backup boiler is not on I'm averaging ~3.8 COP
The days the backup boiler is on I'm averaging ~4.2 COP
Any ideas will be greatly appreciated.
Happy to provide more info if needed?
That does sound surprising!
I expect that you're right - the backup heater is likely to be an inline immersion somewhere.
How do you measure the electrical energy? How well are the Sontex temperature probes attached (perhaps a photo?).
Which Flexotherm unit is it - I think they come in 5/8/11kW. So far as I can see, the units are simple on/off gshp ones with impressive COP, not inverter units(correct me if I'm wrong!).
If you run the unit continuously for (eg) an hour (make sure your thermostat is high) without backup heater, what heat energy do you get, and what Electrical does it take?
Ditto, but now with the heater on - what heat and electrical energy?
Thanks for the reply.
The electrical energy is measured via separate electrical meters, one for renewable (i.e. GSHP) and one for non renewable (i.e. backup boiler). I have attached a photo of this and the heat meters. Also the photo of where the sensors are connected.
It is a Flexotherm 11kw. It is sold as having a COP of 4.73 @ 35c flow temp. I'm unsure about whether it has an inverter.
I've run the pump with and without the backup boiler on.
26/01 - Backup boiler off - Electric 44.38kw; Heat 170kw; COP 3.83
30/01 - Backup boiler on - Electric 46.1kw (of which 5.24kw backup boiler); Heat 219kw; COP 4.75
One thought I had was that the DHW when being run by the GSHP was killing the efficiency/COP somehow? Maybe flow temps too high??
I don't think it's an inverter model - this says not:
https://www.toptenuk.org/consumer/product/view/VaillantGmbHflexoTHERMexclusiveVWF874
Perhaps you're right, and it's a "marginal COP" thing due to the DHW temperature. It seems very surprising. How hot does it run to for DHW?
Can you separate out hot water and heating? I assume that you have a hot water tank - does it have it's own immersion heater that you could use for a while, and stop the GSHP trying to heat it. Then run the experiment again - measure Heat and Elec both with and without the backup heater ?
Yes we have a hot water tank so I will try your suggestion of using the immersion to isolate the Heating and DHW.
The flow temps get up to 60c when the DHW is on. Looking at the 'Marginal COP idea' that could make sense if the flow temps are so high its actually less efficient.
I'll let you know how I get on.
- 26 Forums
- 2,603 Topics
- 60.6 K Posts
- 270 Online
- 6,958 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Anyone concerned about GivEnergy?
Oh for a Crystal Ball and a polishing cloth… Toodles.
By Toodles , 41 minutes ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 59 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
@sonosppp, the Powerflex 2000 is a really interesting p...
By Mars , 1 hour ago
-
RE: Ecoflow UK Support & Info Thread
@sonosppp I've just recorded my review of the Delta 3 M...
By Mars , 1 hour ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Sorry, I don't know what a UFH is. That valve ...
By bazcurtis , 2 hours ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
True. But a minor earth leakage will make no significa...
By JamesPa , 4 hours ago
-
RE: Renewables & Heat Pumps in the News
A bit meh! TBH. No strong opinion and not really bothe...
By JamesPa , 5 hours ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
That's true. Some heat pumps quote capacity including ...
By JamesPa , 8 hours ago
-
RE: Microbore heat pump installs
It's possible you don't need to replace the microbore b...
By JamesPa , 8 hours ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 11 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 22 hours ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 22 hours ago
-
@transparentransparent I guess there is nothing you don...
By David999 , 22 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Alan(alan22) Manufacturer: Valiant Mo...
By Alan , 23 hours ago
-
Having seen that screenshot, I think I know what "Gener...
By Transparent , 23 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
I had an initial estimate for a Grant HP, as we are loo...
By Batpred , 24 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
So we are starting to see the options land where they m...
By Batpred , 1 day ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
After running a search in the god ol' watson, this is w...
By Batpred , 1 day ago
-
RE: GivEnergy 2025 forthcoming batteries and inverters
@drei I wrote an email to Greg Jackson at the end of la...
By Toodles , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
Sorry to resurrect, but did you have any luck tweaking ...
By marcexec , 1 day ago
-
RE: Choosing a time for DHW heating?
@grahamf On the initial question of when to heat the DH...
By DavidAlgarve , 1 day ago
-
RE: ECO4, ECO3, ECO2, ECO1, HUS, BUS, GBIS Dedicated Support and Advice
It has come to my attention that Consumer Energy Soluti...
By Mars , 1 day ago
-
Hello I’ve sent an email to @editor asking if there...
By Little Lights , 2 days ago
-
RE: Replacement parts Samsung Gen5 control panel
Thanks so much for your detailed reply. I will see if I...
By Ian L , 2 days ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Your ‘hand waving’ above isn’t too far off mostly. Our ...
By Judith , 2 days ago