Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @sarahI have also (last night) changed the comp curve to 45 (from 40) - it's not too warm outside today - so I will see if that makes a difference. I've never been able to get this right in the 8 years I've had it - it either uses so much electricity when running that we are at the stage where we have to decide if we can afford to run it or when I make changes it doesn't heat up the area. I really want to like the ASHP but I never have.
I'm assuming that you are not too technical, is that correct?
Could you please post photo's of all the equipment within your system so that we can get some idea about how it has been installed.
When you mention '3 boxes', are these thermostats?
@sarah Hi, the highlighted "-30" your compensation curve is fine. The two highlighted parameters on the graph are just indicating the curve at the marker point, which is the black spot at the bottom left hand corner. You can move this point along the axis using arrow keys, and the highlighted readings will update accordingly. Hope this helps.
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh Hanchu ESS LFP battery storage
PHEV; Zappi charger
1997 stone detached house with updated insulation. 140sqm, maintained at 20-22degC 24/7
When our Ecodan system was first commissioned we had a low flow rate, very similar to this. The engineer simply cleaned the in-line strainer, and since then our flow rate has been over 20l/min. The strainer gets checked on each annual service and it's remained clean.Posted by: @sarah@gary picture of flow rate
-- Attachment is not available --
I just thought it worth mentioning in case you have something similar going on, especially if your strainer hasn't been checked for some time.
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh Hanchu ESS LFP battery storage
PHEV; Zappi charger
1997 stone detached house with updated insulation. 140sqm, maintained at 20-22degC 24/7
@derek-m yes not too technical - at least for heating systems!!! I'm having to learn about it though. Yes three thermostats in each room (they are all on same level) - the "slab" (about 70/80 sqmetres) is one level separated with three manifolds for each space (living area/bedroom and bathroom) - there are doors separating the room but they are not always closed.
In the Eng menu there is a pump speed setting from 1 to 5. What is yours set to. If you increase it and go back to the running info what does the flow rate number change to.
How are you running the system hest pumps needs to be on for hours all day especially with ufh if yours is deep in the concrete you will never get the concrete up to temp if you don’t run it for long periods
@sarah With the pump set to 5 the flow rate you are achieving is too low for the heat pump to be working correctly, it won't be transferring enough heat to the UFH circuit.
When the heat pump is running if you go back to eng menu and into thermistor readings this will show us what the flow and return temps of the heat pump are and the outside temp at the time that will help clarify, but at the moment it looks like the heat pump flow rate is too low.
Yes you are correct but room temp is the temp of the location where that controller is.
Is it currently heating hot water as flow and return aren’t in line with your WC curve.
If so check again when it’s doing heating
THW5 is your HW tank temp and TH7 is the outside temp by the heat pump
- 27 Forums
- 2,745 Topics
- 64.5 K Posts
- 332 Online
- 7,149 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@toodles I invested on Miele a pair of frodge frozor wh...
By AgentGeorge , 40 minutes ago
-
RE: Flushing system, cleaning and inhibitor
Flush and fill all complete. Octopus kindly gave us a...
By Old_Scientist , 50 minutes ago
-
RE: Wood burner with ASHP - direct air?
For what it's worth I installed a wood burner in this o...
By BlizzardGreen , 2 hours ago
-
@editor Thanks for your response and recommendations. ...
By DavidB , 9 hours ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
I think I saw a diagram for an exhaust air dhw tank wit...
By JamesPa , 22 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks, however that's an answer to a subtly different ...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Such elegant symmetry. look at my lumpy bag of...
By Papahuhu , 4 days ago
-
RE: PV and battery long payback - sense check query
Quite probably not, but you can get a 32A relay and a S...
By JamesPa , 4 days ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s Look forward to making contact soon! Regards, To...
By Toodles , 4 days ago
-
I don't notice mine defrosting, and most of the time Im...
By JamesPa , 5 days ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
Kind of you, @calumm, but it was @f1p who did the heavy...
By Majordennisbloodnok , 5 days ago
-
RE: Electricity price predictions
2. As EV ownershp increases it'll certainly increase de...
By EtchedPixels , 6 days ago