Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Arotherm Settings for New Installation
Im just helping my brother in law with his new 7kW Arotherm installation. I looked at a few youtube videos and found my way around the controller but Im unsure about a couple of things and the COP of the unit for heating is currently poor at about 3 (DHW is OK at 2.5).
Firstly the current room temperature on the controller seems to bear no resemblance to the actual room temperature. (see pic). Is this an issue or just annoying?
Next the unit is set up for pure weather compensation, but i can see the option for using room temperature modulation as well, has anyone any experience of this?
The current curve is 0.85, am I right in assuming that the upper and lower limits of the WC can be set separately to the curve?
Any other tips welcome 🙂
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Just to say, that we have managed to set up the unit now. 22C target indoor temperature and a heat curve of 0.6. High internal temp but the wife is a freezer and room temperature is a constant cause of marital strife.
Currently running on pure weather compensation so I would still be interested to hear from anyone who uses the room temperature compensation feature.
Heating COP appears low still, but Im not sure how much the Vaillant reporting system can be trusted after reading a few online reports.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Hi there,
Would need a few more details of your BIL's install. Radiators, UFH, number of emitters, how many zones, size of property, size of water tank, number of pumps in the system, LLH etc.
- How are you calculating the COP? Vaillant use a different formula from everyone else.
- The Vaillant reporting seems pretty accurate in my experience, well for us anyway.
- We only use pure weather compensation, we even go as far as using the adaptive heat curve, letting the Vaillant software decide the best heat curve for the property.
- Regarding the temp reading, ours is always bob on. Were you sat with the sensocomfort unit in your hands or on your lap for a while, they are quite sensitive units. We've had first hand experience of this.
- As for adjusting the heat curve end points, this is not possible with Vaillant as far as I am aware.
Hope this helps.
Drew
Hi Drew. Thanks for the reply. I’ll post his installation details asap.
The work is neatly done and all the radiators were changed as per the installers spec.
There is no LLH or buffer but they did insist on a volumiser and are using glycol instead of water and anti freeze valves.
Im getting the COP from the app but am aware of the quirk with the way Vaillant describes their energy figures and hence the odd COP calculation.
I haven’t seen the adaptive curve feature but have found a formula for calculating the correct curve for the desired room temperature. I can see how this all works now, very different from the Samsung setup.
I wondered about handling the controller and the temperature reading but that didn’t seem to be the issue. In fact it seems to have stabilised now.
If the displayed COP is correct then that is a worry and needs some investigation.
thanks Mark
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
sounds like you are slowly getting there. From the checks I have done, the COP in the app seems to be fairly accurate, others have confirmed this to. We used to have to do the calc using the figures in the controller. Once you have the system info it will be good to get a look at it for you. Are the radiator valves all fully open?
Drew
@drew-pa Ive attached the performance estimate Drew, that is all I have. There is no UFH.
Also attached are some images of the installation. Other than the things I've already mentioned, the only other thing I wouldnt have done was run the external pipework as far as they did. BTW its white because his wife insisted on them covering it with tape 🙂
There doesnt seem to be anything obvious as to why his COP is so low, despite the settings, the flow temperature over the last couple of days was under 40C so I would have thought he should have a COP of about 4 judging by the arotherm specs.
My sceptism about the reported COP was based around discussions on Protons for breakfast, Energy Stats Uk and a discussion on the openenergymonitor forum. If its accurate, then its a worry.
Not all the radiator valves are fully open but several are as I was trying to balance the system a bit better and warm up some cold radiators. Annoyingly the installers dont seem to have bothered.
Mark
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Can you open all valves, and reduce flow temp further? Various units have run at low 30s or upper 20s in the past days.
CEO and co-founder at HavenWise
Ive opened all but the bedroom radiator valves, which they want to be cooler. Im running my Samsung at about 42C flow at the moment and still getting a COP of 3.8-4.0 so the Vaillant should really be doing a lot better than it is even at a FT of 38C.
Ive attached the COP as reported by the app and the Arotherm COP figures.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Comparing different units in different homes is not very straightforward...
Is the Vaillant cycling a lot?
CEO and co-founder at HavenWise
Apologies for the delay.
How is the unit set up to operate? Are they running it a few times a day, or running it manually? We found ours works at its most efficient if it is running in manual mode(water and heating). Just set the temp we want and leave it. Might be worth a try, also try lowering the heat curve a little.
Drew
@hcas Hi , I appreciate the problems with comparing different systems, but this installation is relatively simple with no buffer/LLH. The estimated SCOP from the installers is 3.65 for heating so you would expect to beat that in the shoulder heating season.
I have no way of monitoring if it is cycling, but the heat pump isnt oversized for the property so I would be very surprised it it was. Apart from a couple of issues I wouldnt have done (eg gycol), it looks like a good install so Im very surprised to see such a low COP.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 1,017 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 6 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 10 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 11 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 11 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 14 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 20 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 20 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 1 day ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago