Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heating theory doesn’t match reality
Hi folks,
im new to the world of ashp and just bought a house with one. It’s a NIEB and it heats underfloor plus hot water. It’s got an SMO 05 controller.
in theory I believe that there is an internal temp probe somewhere in the house but I can’t find it and the internal temp reads as - - but in some menus there are temp settings where there wouldn’t be if it wasn’t attached.
I’ve read a lot about weather compensation and zoning and so I have made some adjustments
1. All room stats fully open to help increase volume and allow a lower flow temp
2. Weather compensation curve lowered by one value every 48hrs for the last week. I’ve gone from 9 to 4 now and about to go to 3
3. Additional heat turned fully off.
4. Set temperature reduced from 20 to 18
i was hoping that I’d see a reduction in house temp, a decrease in flow temps, but longer fan run times and obviously lower bills. Instead what I’m seeing is that the house temperature hasn’t changed at all it’s still 20 to 22 degrees. The calculated flow temp is down to 25c and I never see the device saying that it’s heating, only ever heating the hot water, never the underfloor. At the same time flow temp is up at 45
Am I being thick? Is the unit faulty? Or is something going on where the unit turns on to heat the water and enough heat is created to heat the underfloor?
im completely lost
@drdp – have you considered turning off your compensation and setting a manual flow temperature point.
Remember that your heat pump is aiming to deliver a target temperature for your house (usually 21C) so your weather compensation will adjust your heat pump but not your internal temperature.
Depending on your insulation, maybe start with a flow temperature of 35C. That shouldn't blast heat and it'll keep your heat pump running efficiently. You should see a decrease in room temperature with outside temperatures below 7C.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor hey Mars, thanks for the reply.
im not sure it’s possible to do this with the SMO 05.
I think my problem is slightly different. I’ve been watching the compressor starts and can say with more confidence that the system is only heating hot water and overnight it only turns on twice for total of 2 hours for example.
the compressor is only active when the system valve is set to hw. The line temp goes up to 45 and heats the water. After this the compressor stops, the system goes back to the ch valve setting but the flow temp stays at 45 and then slowly drops down over a few hours.
is it possible that when heating the hot water the system has enough residual heat to then heat the underfloor? I don’t understand how this would work as I thought they were separate systems and separate buffer tanks
@drdp Hi, Difficult to determine what is wrong, can you PM me a system drawing listing all components and wiring if possible. It does not seam to be working like it should, there may be a problem with the diverting valve.
@heacol thanks for the offer but unfortunately I’m not an engineer and have no idea how this is wired up 🙁
im new to the property and any wiring diagrams they had are long gone. I could send photos of the system but I imagine that’s little help.
oh and I can’t do yet as I’m still brand new to this forum and need a few more posts.
thanks for being so helpful! This forum is ace
There is slightly more to the story now. I’ve managed to time it right and get to the system when the compressor is on. Again this is only happening in hw mode. I held on to the blue underfloor pipes where they are exposed and a couple of them were really warm.
It seems that rather than just residual ch heat going in to the underfloor, the system is actually heating some of the underfloor the whole time it’s heating the hw. I assume it’s also putting this very hot water through my underfloor.
I think it’s time I called an engineer
Posted by: @drdpThere is slightly more to the story now. I’ve managed to time it right and get to the system when the compressor is on. Again this is only happening in hw mode. I held on to the blue underfloor pipes where they are exposed and a couple of them were really warm.
It seems that rather than just residual ch heat going in to the underfloor, the system is actually heating some of the underfloor the whole time it’s heating the hw. I assume it’s also putting this very hot water through my underfloor.
I think it’s time I called an engineer
Before calling an Engineer, trace back along the warm pipework until you find the motorised 3-way diverter valve, or do you have two 2-way valves?
There should be a small lever on the side of the motor unit, try moving it back and forth to see if the valve is stuck. Watch the operation of the valve(s) with the system in both CH mode and DHW mode, they should divert the water flow one way and then the other.
@derek-m I think I have a 2-way diverter. It’s got 3 pipes going in to it and two positions (one input pipe and 2 output?).
I’ve been watching this valve and when the system is heating hw it’s in the right orientation and stays there, but at the same time the underfloor pipes are still getting hot.
Do these systems have a heat “overflow”? I.e. if the hot water comes on, but it reaches temp quickly, would it divert some to the underfloor?
I know is sounds like I’m looking at things wrong, but I’m really really sure the physical valve and the SMO unit both say that are heating hw only, when in fact they are also sending heating to the floor
Posted by: @drdp@derek-m I think I have a 2-way diverter. It’s got 3 pipes going in to it and two positions (one input pipe and 2 output?).
I’ve been watching this valve and when the system is heating hw it’s in the right orientation and stays there, but at the same time the underfloor pipes are still getting hot.
Do these systems have a heat “overflow”? I.e. if the hot water comes on, but it reaches temp quickly, would it divert some to the underfloor?
I know is sounds like I’m looking at things wrong, but I’m really really sure the physical valve and the SMO unit both say that are heating hw only, when in fact they are also sending heating to the floor
I suppose it should really be called a 3-port valve rather than a 3-way valve, but it would appear that is what is fitted. When operating correctly, it should divert the flow from the input port, to one or other of the outlet ports, but not to both at the same time. There could be some debris on the sealing face within the valve that is preventing it from shutting fully, or it may be sticking. Try selecting CH then DHW, to operate the valve, whilst gently tapping the valve body with a rubber mallet or suitable piece of wood.
@derek-m I think you've found the issue. I'll report back in a day or so to confirm but I'm pretty sure this is the issue.
The valve is a Honeywell UC4013 and it allows me to press on the valve directly. The value should be fully depressed to send water to the CH and it feels fine for 90% of the stroke and then sticky for the last 10%. It would make sense that when the unit thinks it's heating the hot water it's sending 10% of the heat to the floor.
This would explain why the house is roasting, why the bills are not ideal and why I never see the call for heat to the underfloor (it's already hot).
I'll have to read more and see if I can free up the valve without taking the system apart, otherwise it's still a call to the engineer.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 288 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago