Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
The Seven Deadly Sins of bad ASHP install
So, putting this out there for comment and debate. OK, it is based in part on my experience, but do chip in with yours. Poor install & commissioning of retrofit ASHP systems seems too prevalent within a relatively new ASHP retrofit market, what's the common issues?:
1. "You're existing radiators will be fine with an ASHP" - No, no and no. Do the calcs based on an efficient maximum design flow temperature, say 45degC, and upgrade the radiators. Whatever is spent on bigger radiators is recovered several times in lower running costs over the system life.
2. "We'll fit a Hive, Tado or Nest 'smart' thermostat and you'll control the ASHP from that" - So, you'll fit some so-called smart on/off wireless switch to my ASHP and kill any chance of it ever reaching stable control and you'll cycle the compressor on/off much more often than it needs to. And that's smart is it?
3. "We'll fit the next size up ASHP" - because you can't be bothered to do that calcs properly, or you don't have the competence, or both. Just like when you were banging 30kW gas boilers into 2 bed terraced houses, you'll adopt the same 'bigger is better' mentality with ASHPs. Right size it, don't oversize it.
4. "We'll leave the heating supply temperature set point high and the weather compensation disabled so you don't call us to complain the radiators are not hot" No matter that the homeowner/occupier will be paying nearly double in ASHP running costs from the day you drive off, but who cares as long as the phone doesn't ring. This has to stop, and it seems to be rather common.
5. "We'll put a 'touch this at your peril' sticker over the ASHP controller cover and hide the controller away in the garage or airing cupboard". After install, the person best placed to fine-tune and maximise the efficiency of the ASHP control is the homeowner/occupier. Only they will be able to correctly set the weather compensation based on experience of living in the property. Stop putting scare stickers on controls because you, the installer, cannot be bothered to invest the time to learn the basics and commission it properly, spend time with the homeowner/occupier and communicate that knowledge, or make a call-back visit to tweak the system.
6. "We'll not bother with any cable trunking or pipe insulation on this one, we've only got a day for the job and it's a social housing install anyway". This has has to stop, minimum standards need to apply across the board, and action taken against installers whose workmanship falls short of the mark. The companies doing this sort of thing need to be called out & held to account.
7. "It's a replacement boiler" - no, it's not. Repeat, no it's not. An ASHP needs to control and operate differently, and the ASHP is just one part of a replacement heating system. It's the heat source, but that's where the similarity to a boiler ends.
@alleyfish - excellent list, I would add, only it takes the list to eight and so loses the alliteration of seven deadly sins, "Of course your heat pump is more than big enough, its 14kW for an 12kW loss property, what could possibly go wrong" Well, it isn't a 14kW heat pump when it matters, when it's cold, it's more like 11kW, so quite a lot can go wrong when you need your heating the most. I think this may even be more common a problem than number 3 in your list, ie more people end up with undersized rather than oversized heat pumps.
Midea 14kW (for now...) ASHP heating both building and DHW
The one issue I've had with my install is checking that the we have the correct level of flow around the heating system before the install is performed. So this may be related to pipe sizing or some other issue but surely this is the first thing to check before doing the install on a retrofit install
When say flow I mean litres per minute flowing through the system to the heat pump as different size heat pumps have different requirements. I don't mean flow temperatures just to be clear about my last comment
Posted by: @soniksSo this may be related to pipe sizing or some other issue but surely this is the first thing to check before doing the install on a retrofit install
And are there any unseen leaks, if it is an old system, and used to be open system with a feed tank in the loft, ie a pressure test. I accidentally had one, when my installer's plumber accidentally put full mains pressure on the secondary rad circuit, perhaps around 5 bar as the mains pressure is quite high here. It blew the 3 bar pressure release valve on the circuit, which made quite a bang, but after the 'pressure test' the circuit still maintains standard operating pressure, about 1 bar, for months at a time, so no leaks.
The same can't be said about the primary circuit, that does lose pressure over time. I suspect a small invisible leak somewhere...
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay That's a difficult one to answer as I can't see any obvious signs of leeks but I do have to top up CH circuit more regularly than I think I should have too - maybe every 2 months and when I look at the pressure guage it does tend to vary through the day. I did hear once when I was in the loft an air vent hissing and appears to be covered in some brown residue. Is there any other reason air could fill in the system the circulating pumps may be?
4. "We'll leave the heating supply temperature set point high and the weather compensation disabled so you don't call us to complain the radiators are not hot" No matter that the homeowner/occupier will be paying nearly double in ASHP running costs from the day you drive off, but who cares as long as the phone doesn't ring. This has to stop, and it seems to be rather common.Posted by: @allyfish5. "We'll put a 'touch this at your peril' sticker over the ASHP controller cover and hide the controller away in the garage or airing cupboard". After install, the person best placed to fine-tune and maximise the efficiency of the ASHP control is the homeowner/occupier. Only they will be able to correctly set the weather compensation based on experience of living in the property. Stop putting scare stickers on controls because you, the installer, cannot be bothered to invest the time to learn the basics and commission it properly, spend time with the homeowner/occupier and communicate that knowledge, or make a call-back visit to tweak the system.
My parents moved into a new build flat last year which was heated with a heat pump. There was basically no hand-over or instruction from the builders. The documents they were given for how the flat is designed to operate was absolutely laughable - it said that the heat pump was controlled by a powerful AI computer and that nobody should ever touch it. Meanwhile, the flow temperature was set to 60 degrees C!!! Presumably they meant to set the hot water to that (still too high), but couldn't be bothered to work out which was which and just put all the temps to 60. Radiators were lovely and warm though so my parents didn't complain... I've changed it to weather compensation and sensible flow temps that are a bit higher than the norm (they are old, they like it nice and toasty). But now every time I go over there I have to ask them if they're too hot or too cold, which is a difficult task for a "mustn't grumble" generation...
This is another aspect of the whole thing - it's one thing to regulate retrofits or installs where the homeowner actively desires one installed and can be expected to have done some level of research beforehand, but regulating new builds where the homeowner doesn't know anything about them, and the building company doesn't know anything about them - that's going to be a nightmare. And especially when those homeowners are elderly on a fixed pension and really REALLY need their home to be both warm and cost-effective.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
Wow, 60degC flow temperature. There must be artificial intelligence there at work as there's no human intelligence. Great that you were able to fix it for them. You have to wonder how many people are crippled by massive electricity bills through similarly appalling commissioning. There are manufacturers who I'm convinced actually encourage installers to disable WC and set the flow temperature high to avoid the 'my radiators are not very warm' calls to their customer service centre.
The quantity of badly installed and commissioned ASHPs is probably on a par with badly installed and commissioned gas boilers, but no-one seems to notice bad gas boiler installs. As long as they heat the water to 70degC who cares if the condenser part never works or if the gas boiler is more than twice the size it needs to be.
The new build ASHP market is an issue. The information given to the new buyer/tenant is non-existent, they don't know who installed it or who to contact to get help, etc. It will be sold as an efficient green heating system (which it could and should be), but may be commissioned badly or inefficiently if any proper commissioning has been done at all. The whole UK domestic heating industry has to raise its game.
With the current state of play in the installer market - a homeowner has to take some responsibility for the install.
And they need to understand that beforehand.
The undersizing issue is real - I'm concerned my own is too small - 250m2 - Heat Loss Calc = 7.1kW @-1.5Deg = 10kW Grant Aerona (As calculated by grant, on a computer, without a visit)
But the real life scenario is that it doesn't seem to have the grunt when it is <5Deg and defrost cycling kicks in.
Also, manufacturers could make many things easier - the Aerona controller has far too many parameters - read/inst/User - the lists are long - and many will never be viewed or seen - a bluetooth connection, if not a wifi app, would also help to monitor. (All cost, I know)
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 293 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils I saw the announcement last week. I'm going to ...
By Mars , 14 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 15 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago