[Solved] Sudden drop in COP
I've had a sudden drop in COP, from around 3.8-4.4 a few weeks ago, to 2.4-3.0 recently. Any thoughts as to why?
I have a Samsung 8kw ASHP that for the last month or two I've only been using for DHW. I don't have any advanced monitoring, just the energy use and generation output by the unit itself. Over the last week the COP has been way down and I'm not sure why.
I heat up the DHW once a day between 2pm and 3:30pm, 200L water tank with 3m square heating coil. The unit switches into quiet mode when DWH is active. It's not a heavy use set up, one shower a day and maybe some washing up.
I don't have the heating on this time of year and don't want to turn it on to see what that is running at.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
My guess would be that the unit is measuring combined COP for heating and hot water. Therefore because now you are only heating water at a lower COP than heating your average drops.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I don't have any advanced monitoring, just the energy use and generation output by the unit itself.
How do the energy use and generation output differ between the good COP and bad COP weeks? Is it that the energy used has increased or the energy generated has decreased to give you the lower COP?
My Samsung Gen6 8kw had a bit of brain fade earlier in the year when the recorded energy generation figures became ridiculously high - 1,398kWh for one week in February. The energy consumption was recorded as a (more believable) 90kWh, so a fantastic COP of over 15 🤗 . I knew something was really wrong when I saw that the recorded weekly operation time for that week was 524 hours - around 75hrs a day. Samsung Technical Support talked me through a reset of the Wired Remote Controller and that appeared to sort the issue.
@bontwoody The thing is I have been using it for only DHW for a month or two, i was getting higher cop just on the hot water, so it can’t be that I’ve turned off the heating.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@sjn Okay so it was a software issue. It appears my energy use is going up, but my energy generation is staying about the same according to the numbers.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker Yes, it must have been a software bug disrupting my historic energy numbers. I haven't looked at them recently so I should check to see if they are still ok.
Your generation staying about the same makes sense for a consistent use of DHW so it is the increased usage that is unexpected.
One thing I have noticed is that there is some rounding going on with the displayed energy numbers - the sum of the energy figures for each day does not add up to the displayed total for the week. I wonder if with DHW only the usage and generation will be quite low so the rounding errors may have a bigger significance to your COP calculations, possibly amplifying any week to week changes due to different outside air temperature 🤔 .
@sjn I've seen this on other brands as well. Rounding for small consumption (for instance only hot water) really messes up the accuracy.
Another thing we've seen is that some manufacturers just add on a flat energy use per hour (during periods when the heat pump is not running). Maybe Samsung did a software update recently and started doing this as well?
CEO and co-founder at HavenWise
@hcas Thing is I've not updated the software, that's actually quite hard to do with Samsung as its not directly connected to the internet.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
SOLVED
So it turns out the problem is, I am a massive Idiot.
A few weeks ago, I had used most of my hot water, and needed a quick shower as I was in a rush and had to go out. So I put on forced mode for DWH and turned on the immersion heater, which I normally have turned off, to turn on after 15 mins. When I had enough hot water I turned off forced mode but forget to turn off the immersion in the field settings.
So my sudden drop in COP has been down to my immersion firing up and helping heat my hot water for the last few weeks 😭
Turned it off and I got 4.1 cop for DHW today
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
-
Nibe F2040 periodic warm water increase fails
2 months ago
-
Samsung E911 intermittent issue
6 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
8 months ago
-
Heat Pump, DHW, UFH and Radiator Install
8 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,113 Topics
- 46.4 K Posts
- 67 Online
- 3,410 Members
Latest Posts
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 8 hours ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 9 hours ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 21 hours ago
-
RE: Wood burner with ASHP - direct air?
I love the new fully Viking look... best personal avata...
By Mars , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 2 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 3 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 3 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 3 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 5 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 5 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 6 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 6 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 6 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 6 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 6 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 1 week ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago