@cathoderay in fact I think most of our current radiators are oversized for 70C flow. Most of the house was actually acceptable last winter at 50C flow, it was just the living room where on cold days we could "only" get to 22C temps.
So I'm hopeful that by adding a decent amount of insulation where there was none, that may already be enough and the increase in sized would give us headroom we need.
Posted by: @toodles@jamespa i.e ‘We know it is flawed, but we are covering our @rses’. Regards, Toodles.
Precisely that. The method is based on BS something or other, I forget which, so even MCS can say it's someone else's.
BS something or other is designed for new build where you know what the construction is, not retrofit where you don't, but hey-ho.
In summary MCS covers it's backside by reference to bs something or other, and the installers cover theirs by reference to MCS. The only loser is the customer. That of course is perfectly satisfactory from the pov of an industry funded body.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @scalextrixSo I'm hopeful that by adding a decent amount of insulation where there was none, that may already be enough and the increase in sized would give us headroom we need.
If you do this take pictures and get receipts, you may need to get to convince installers it's been done unless the insulation remains visible.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@scalextrix And the chances are you might not have been running your heating ‘24/7’ as you might an ASHP? Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@jamespa I have a feeling that there is a play based on groups all basing their requirements on someone else’s requirements - who in turn, based theirs on someone else’s….. Regards, Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @scalextrixHome most days, set system to heat 6AM - 11PM, main thermostat
But that isn't the best way to run a heat pump. Weather compensation run 24/7 and if you need a very small nighttime setback of a couple of degrees only
Posted by: @scalextrixI think most of our current radiators are oversized for 70C flow. Most of the house was actually acceptable last winter at 50C flow, it was just the living room where on cold days we could "only" get to 22C temps.
That sounds promising. Do you still have the heat loss/rad sizing calculations used to select your current rads? If you do, they may add some more info. If not, using your per room current heat loss calculations, you could check a few of the rads to see how they match up. The down-rating for use at lower flow temps (strictly speaking, lower delta t between the mean rad temp and room temp) is pretty straightforward, by applying a 'correction factor' such as those found on this page for Stelrad rads. For example, at a delta t of 30 (eg highish heat pump setting with LWT 52.5, RWT 47.5, mean rad temp 50, room temp 20 degrees), the output of a rad is half (51.3%) what is with a delta t of 50 (rads 70, room 20 degrees), which is the number behind my earlier statement that by and large correctly sized fossil fuel rads will nee to be roughly doubled in size/output to work with a typical heat pump (not high temp heat pumps, which are I believed intended to allow reuse of existing rads, but I strongly suspect you then end up paying more in ongoing bills).
Thus if the correct rad on a fossil fuel system is 1000W, then you will need one rated at 2000W (at delta t 50) for your typical heat pump, which will then put out 1000W (2000 x correction factor of 0.531 = 1062W) at heat pump flow temperatures. If you run you heat pump lower flow temps, you will need even larger rads...
I emphasise all this because I suspect it (not matching the rads to the heat pump) is a common reason for under-performing systems. It's all very well getting the heat pump sizing right (and of course that is not a back of the envelope job either), but if the rads (heat sprinklers) are too small, they won't be able to deliver enough heat, a bit like a garden hose with plenty of water available behind it, but the nozzle on you sprinkler is too small, and it takes forever and a day to get the watering done.
There might be another analogy based on the waterworks of men of a certain age, but I won't go into that one.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Having had cancer of the prostate a few years back, I appreciate what you are inferring! Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @jamespaWhere are you located? With this info maybe someone here can provide.a recommendation
I'm in Milton Keynes.
I have performed my own quite thorough heat loss analysis. taking into account my detailed knowledge of the construction of my unconventional home. I also paid a modest sum for a remote, desk-based report as a 'sanity check'. When calculating my heat loss through windows, I contemplated replacing my old (35 year old) DG units with new argon-filled ones but this didn't give a sufficiently marked improvement to the heat loss. By far the biggest unknown was the loss due to air change. I don't consider my home to be draughty, but short of commissioning a pressure test, my estimation of the heat loss is no better than a finger in the air.
During last November to January, I set my boiler to its lowest setting of 12kW (I didn't notice any modulation of the fan while the burner was on) with no overnight setback and recorded daily gas use, flow and return temperatures, IAT and OAT. I have a lot of data if I can find a proper ASHP heating engineer who will make use of it. I also have a detailed plan of my existing plumbing which includes pipe gauges but I need to add lengths.
Posted by: @jamespaIn summary MCS covers it's backside by reference to bs something or other, and the installers cover theirs by reference to MCS. The only loser is the customer. That of course is perfectly satisfactory from the pov of an industry funded body.
Exactly the same situation with solar and battery installation. MCS refer to IET regulations for warning labels, among other things. The IET documents are expensive to procure so installers don't buy them or understand the details, but buy sets of warning labels 'in accordance with IET document something or other' and apply them to the equipment. I assume that this would explain why I now have various warnings relating to lead-acid batteries on my LiFePO4 battery pack.
@johnmo understand, but I don't have a heat pump yet or weather compensation, all I can do is hard set flow rate to 50C.
If there is a better way to simulate with the things I have please let me know.
Posted by: @cathoderayDo you still have the heat loss/rad sizing calculations used to select your current rads?
It was installed 18 years ago, plumber just used his thumb-ruler, not calculations. Though back then the house had draughts under doors, poor windows/insulation and all these have been upgraded in the last two decades. Back then we spent £100 per month in gas in winter, for the house to still be cold.
So rads were probably over sized at 70C so the plumber didn't get a call back.
According to the new heat loss survey the hall radiator (almost all internal walls) is 80% oversized (large type 22).
I'm thinking the secret to heat pumps is to try and have all the rad sizes matched to the rooms heat loss and then not use TRVs as much. Oh and emitter balancing is key as well, our living room is last on the circuit and I think the heat isn't always getting there without the boiler cycling. Just need some colder weather to rebalance it all.
-
Where has Watson gone?
10 hours ago
-
First time wall mounting an ASHP
2 weeks ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
3 weeks ago
-
Rodents! A word of warning for heat pump owners
1 month ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
2 months ago
Currently viewing this topic 3 guests.
- 26 Forums
- 2,306 Topics
- 51.7 K Posts
- 275 Online
- 5,970 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Buffer tank bypass on EDF Ideal heat pump installation
@kevb, many of these companies look for the smallest of...
By Mars , 47 minutes ago
-
RE: Don’t Install a Heat Pump Until You Read This
@briansprankle, good luck. Keep us posted. Glad they’re...
By Mars , 49 minutes ago
-
RE: Commencing on an ASHP Installation Process
Me too, but I think we are in the minority. Most homeo...
By JamesPa , 2 hours ago
-
RE: Electricity price predictions
Simple article with a DENZ graph showing how gas which ...
By Jeff , 3 hours ago
-
RE: 10kw heat pump run in 24*7 data?
Thats really helpful as it clearly says target 49C. So...
By JamesPa , 3 hours ago
-
RE: Heat Pump on Flat Roof Low Frequency Noise from Detached Neighbor
@davidnolan22 Yes have been communicating woth the neig...
By People_Noise , 3 hours ago
-
Power Cut - Heat Pump Evaporator Iced Up
We have just had a power cut and 1 hour later power was...
By trebor12345 , 4 hours ago
-
@sand Yes. The COP is reported and you can split it int...
By bontwoody , 5 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
A few weeks ago, I was having a discussion with someone...
By Majordennisbloodnok , 6 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk Hi I see you posted on openenergymon...
By JamesPa , 8 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Often the default password is in the installation manua...
By JamesPa , 9 hours ago
-
RE: Cashback Incentives That Reward Shorter Heat Pump Warranties
@andrewj Indeed, ’Appalling’ is a rather mild term for ...
By Toodles , 9 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
@editor When do “Mars Heat Pump Installation and Servic...
By Toodles , 9 hours ago
-
@morgan Likewise, I realise that some readers will appr...
By Toodles , 10 hours ago
-
A Smarter Smart Controller from Homely?
I received an email from Homely this morning enquiring ...
By Toodles , 10 hours ago
-
RE: Grant Aerona 3 and Drayton system questions
Yes in general terms (obviously I cant tell if its exac...
By JamesPa , 12 hours ago
-
Yes, the Grundfos pump has a built in timer. However, t...
By DavidAlgarve , 13 hours ago
-
Ecodan - Flow temperature spiking causing shutdown
Hi everyone, looking for some help. I am in a new bu...
By Gl3484 , 1 day ago
-
Solis AI is on the right track to leverage the battery:...
By Batpred , 1 day ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Thanks James, its honestly hard to keep it tog...
By Crimson , 1 day ago