@cathoderay in fact I think most of our current radiators are oversized for 70C flow. Most of the house was actually acceptable last winter at 50C flow, it was just the living room where on cold days we could "only" get to 22C temps.
So I'm hopeful that by adding a decent amount of insulation where there was none, that may already be enough and the increase in sized would give us headroom we need.
Posted by: @toodles@jamespa i.e ‘We know it is flawed, but we are covering our @rses’. Regards, Toodles.
Precisely that. The method is based on BS something or other, I forget which, so even MCS can say it's someone else's.
BS something or other is designed for new build where you know what the construction is, not retrofit where you don't, but hey-ho.
In summary MCS covers it's backside by reference to bs something or other, and the installers cover theirs by reference to MCS. The only loser is the customer. That of course is perfectly satisfactory from the pov of an industry funded body.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @scalextrixSo I'm hopeful that by adding a decent amount of insulation where there was none, that may already be enough and the increase in sized would give us headroom we need.
If you do this take pictures and get receipts, you may need to get to convince installers it's been done unless the insulation remains visible.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@scalextrix And the chances are you might not have been running your heating ‘24/7’ as you might an ASHP? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@jamespa I have a feeling that there is a play based on groups all basing their requirements on someone else’s requirements - who in turn, based theirs on someone else’s….. Regards, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @scalextrixHome most days, set system to heat 6AM - 11PM, main thermostat
But that isn't the best way to run a heat pump. Weather compensation run 24/7 and if you need a very small nighttime setback of a couple of degrees only
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @scalextrixI think most of our current radiators are oversized for 70C flow. Most of the house was actually acceptable last winter at 50C flow, it was just the living room where on cold days we could "only" get to 22C temps.
That sounds promising. Do you still have the heat loss/rad sizing calculations used to select your current rads? If you do, they may add some more info. If not, using your per room current heat loss calculations, you could check a few of the rads to see how they match up. The down-rating for use at lower flow temps (strictly speaking, lower delta t between the mean rad temp and room temp) is pretty straightforward, by applying a 'correction factor' such as those found on this page for Stelrad rads. For example, at a delta t of 30 (eg highish heat pump setting with LWT 52.5, RWT 47.5, mean rad temp 50, room temp 20 degrees), the output of a rad is half (51.3%) what is with a delta t of 50 (rads 70, room 20 degrees), which is the number behind my earlier statement that by and large correctly sized fossil fuel rads will nee to be roughly doubled in size/output to work with a typical heat pump (not high temp heat pumps, which are I believed intended to allow reuse of existing rads, but I strongly suspect you then end up paying more in ongoing bills).
Thus if the correct rad on a fossil fuel system is 1000W, then you will need one rated at 2000W (at delta t 50) for your typical heat pump, which will then put out 1000W (2000 x correction factor of 0.531 = 1062W) at heat pump flow temperatures. If you run you heat pump lower flow temps, you will need even larger rads...
I emphasise all this because I suspect it (not matching the rads to the heat pump) is a common reason for under-performing systems. It's all very well getting the heat pump sizing right (and of course that is not a back of the envelope job either), but if the rads (heat sprinklers) are too small, they won't be able to deliver enough heat, a bit like a garden hose with plenty of water available behind it, but the nozzle on you sprinkler is too small, and it takes forever and a day to get the watering done.
There might be another analogy based on the waterworks of men of a certain age, but I won't go into that one.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Having had cancer of the prostate a few years back, I appreciate what you are inferring! Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @jamespaWhere are you located? With this info maybe someone here can provide.a recommendation
I'm in Milton Keynes.
I have performed my own quite thorough heat loss analysis. taking into account my detailed knowledge of the construction of my unconventional home. I also paid a modest sum for a remote, desk-based report as a 'sanity check'. When calculating my heat loss through windows, I contemplated replacing my old (35 year old) DG units with new argon-filled ones but this didn't give a sufficiently marked improvement to the heat loss. By far the biggest unknown was the loss due to air change. I don't consider my home to be draughty, but short of commissioning a pressure test, my estimation of the heat loss is no better than a finger in the air.
During last November to January, I set my boiler to its lowest setting of 12kW (I didn't notice any modulation of the fan while the burner was on) with no overnight setback and recorded daily gas use, flow and return temperatures, IAT and OAT. I have a lot of data if I can find a proper ASHP heating engineer who will make use of it. I also have a detailed plan of my existing plumbing which includes pipe gauges but I need to add lengths.
Posted by: @jamespaIn summary MCS covers it's backside by reference to bs something or other, and the installers cover theirs by reference to MCS. The only loser is the customer. That of course is perfectly satisfactory from the pov of an industry funded body.
Exactly the same situation with solar and battery installation. MCS refer to IET regulations for warning labels, among other things. The IET documents are expensive to procure so installers don't buy them or understand the details, but buy sets of warning labels 'in accordance with IET document something or other' and apply them to the equipment. I assume that this would explain why I now have various warnings relating to lead-acid batteries on my LiFePO4 battery pack.
@johnmo understand, but I don't have a heat pump yet or weather compensation, all I can do is hard set flow rate to 50C.
If there is a better way to simulate with the things I have please let me know.
Posted by: @cathoderayDo you still have the heat loss/rad sizing calculations used to select your current rads?
It was installed 18 years ago, plumber just used his thumb-ruler, not calculations. Though back then the house had draughts under doors, poor windows/insulation and all these have been upgraded in the last two decades. Back then we spent £100 per month in gas in winter, for the house to still be cold.
So rads were probably over sized at 70C so the plumber didn't get a call back.
According to the new heat loss survey the hall radiator (almost all internal walls) is 80% oversized (large type 22).
I'm thinking the secret to heat pumps is to try and have all the rad sizes matched to the rooms heat loss and then not use TRVs as much. Oh and emitter balancing is key as well, our living room is last on the circuit and I think the heat isn't always getting there without the boiler cycling. Just need some colder weather to rebalance it all.
-
Installing your own ASHP - DIY
2 weeks ago
-
ASHP install contract and BUS grant money
2 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
2 months ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 months ago
-
Heat Pump starting current
3 months ago
- 22 Forums
- 2,056 Topics
- 44.9 K Posts
- 42 Online
- 3,293 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 16 minutes ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
In fairness to heat pump manufacturers the output inevi...
By JamesPa , 18 minutes ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 3 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Here are the reported most common causes for both. Co...
By abbote , 3 hours ago
-
RE: Is your heat pump insured?
@johnmo sorry it comes across like that. The post is au...
By KevinPotts , 3 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo Perhaps a little detail might explain my reason...
By Toodles , 3 hours ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 16 hours ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 16 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 20 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 21 hours ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 1 day ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 2 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 2 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 2 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 2 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Took a while to find on the OFGEN site: ”The FIT sche...
By AgentGeorge , 2 days ago
-
RE: why solar diverters for HW instead of the heat pump?
For me there are few factors why you may want to heat w...
By Johnmo , 2 days ago
-
RE: Hydronic plinth heaters and ASHPs
@editor yes I think so. It will be a while until I get ...
By benson , 2 days ago