@cathoderay in fact I think most of our current radiators are oversized for 70C flow. Most of the house was actually acceptable last winter at 50C flow, it was just the living room where on cold days we could "only" get to 22C temps.
So I'm hopeful that by adding a decent amount of insulation where there was none, that may already be enough and the increase in sized would give us headroom we need.
Posted by: @toodles@jamespa i.e ‘We know it is flawed, but we are covering our @rses’. Regards, Toodles.
Precisely that. The method is based on BS something or other, I forget which, so even MCS can say it's someone else's.
BS something or other is designed for new build where you know what the construction is, not retrofit where you don't, but hey-ho.
In summary MCS covers it's backside by reference to bs something or other, and the installers cover theirs by reference to MCS. The only loser is the customer. That of course is perfectly satisfactory from the pov of an industry funded body.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @scalextrixSo I'm hopeful that by adding a decent amount of insulation where there was none, that may already be enough and the increase in sized would give us headroom we need.
If you do this take pictures and get receipts, you may need to get to convince installers it's been done unless the insulation remains visible.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@scalextrix And the chances are you might not have been running your heating ‘24/7’ as you might an ASHP? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@jamespa I have a feeling that there is a play based on groups all basing their requirements on someone else’s requirements - who in turn, based theirs on someone else’s….. Regards, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @scalextrixHome most days, set system to heat 6AM - 11PM, main thermostat
But that isn't the best way to run a heat pump. Weather compensation run 24/7 and if you need a very small nighttime setback of a couple of degrees only
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @scalextrixI think most of our current radiators are oversized for 70C flow. Most of the house was actually acceptable last winter at 50C flow, it was just the living room where on cold days we could "only" get to 22C temps.
That sounds promising. Do you still have the heat loss/rad sizing calculations used to select your current rads? If you do, they may add some more info. If not, using your per room current heat loss calculations, you could check a few of the rads to see how they match up. The down-rating for use at lower flow temps (strictly speaking, lower delta t between the mean rad temp and room temp) is pretty straightforward, by applying a 'correction factor' such as those found on this page for Stelrad rads. For example, at a delta t of 30 (eg highish heat pump setting with LWT 52.5, RWT 47.5, mean rad temp 50, room temp 20 degrees), the output of a rad is half (51.3%) what is with a delta t of 50 (rads 70, room 20 degrees), which is the number behind my earlier statement that by and large correctly sized fossil fuel rads will nee to be roughly doubled in size/output to work with a typical heat pump (not high temp heat pumps, which are I believed intended to allow reuse of existing rads, but I strongly suspect you then end up paying more in ongoing bills).
Thus if the correct rad on a fossil fuel system is 1000W, then you will need one rated at 2000W (at delta t 50) for your typical heat pump, which will then put out 1000W (2000 x correction factor of 0.531 = 1062W) at heat pump flow temperatures. If you run you heat pump lower flow temps, you will need even larger rads...
I emphasise all this because I suspect it (not matching the rads to the heat pump) is a common reason for under-performing systems. It's all very well getting the heat pump sizing right (and of course that is not a back of the envelope job either), but if the rads (heat sprinklers) are too small, they won't be able to deliver enough heat, a bit like a garden hose with plenty of water available behind it, but the nozzle on you sprinkler is too small, and it takes forever and a day to get the watering done.
There might be another analogy based on the waterworks of men of a certain age, but I won't go into that one.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Having had cancer of the prostate a few years back, I appreciate what you are inferring! Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @jamespaWhere are you located? With this info maybe someone here can provide.a recommendation
I'm in Milton Keynes.
I have performed my own quite thorough heat loss analysis. taking into account my detailed knowledge of the construction of my unconventional home. I also paid a modest sum for a remote, desk-based report as a 'sanity check'. When calculating my heat loss through windows, I contemplated replacing my old (35 year old) DG units with new argon-filled ones but this didn't give a sufficiently marked improvement to the heat loss. By far the biggest unknown was the loss due to air change. I don't consider my home to be draughty, but short of commissioning a pressure test, my estimation of the heat loss is no better than a finger in the air.
During last November to January, I set my boiler to its lowest setting of 12kW (I didn't notice any modulation of the fan while the burner was on) with no overnight setback and recorded daily gas use, flow and return temperatures, IAT and OAT. I have a lot of data if I can find a proper ASHP heating engineer who will make use of it. I also have a detailed plan of my existing plumbing which includes pipe gauges but I need to add lengths.
Posted by: @jamespaIn summary MCS covers it's backside by reference to bs something or other, and the installers cover theirs by reference to MCS. The only loser is the customer. That of course is perfectly satisfactory from the pov of an industry funded body.
Exactly the same situation with solar and battery installation. MCS refer to IET regulations for warning labels, among other things. The IET documents are expensive to procure so installers don't buy them or understand the details, but buy sets of warning labels 'in accordance with IET document something or other' and apply them to the equipment. I assume that this would explain why I now have various warnings relating to lead-acid batteries on my LiFePO4 battery pack.
@johnmo understand, but I don't have a heat pump yet or weather compensation, all I can do is hard set flow rate to 50C.
If there is a better way to simulate with the things I have please let me know.
Posted by: @cathoderayDo you still have the heat loss/rad sizing calculations used to select your current rads?
It was installed 18 years ago, plumber just used his thumb-ruler, not calculations. Though back then the house had draughts under doors, poor windows/insulation and all these have been upgraded in the last two decades. Back then we spent £100 per month in gas in winter, for the house to still be cold.
So rads were probably over sized at 70C so the plumber didn't get a call back.
According to the new heat loss survey the hall radiator (almost all internal walls) is 80% oversized (large type 22).
I'm thinking the secret to heat pumps is to try and have all the rad sizes matched to the rooms heat loss and then not use TRVs as much. Oh and emitter balancing is key as well, our living room is last on the circuit and I think the heat isn't always getting there without the boiler cycling. Just need some colder weather to rebalance it all.
-
ASHP install contract and BUS grant money
7 days ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 week ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 weeks ago
-
Heat Pump starting current
1 month ago
-
Running my new Nibe ASHP efficiently
1 month ago
- 21 Forums
- 1,964 Topics
- 42.6 K Posts
- 17 Online
- 2,278 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami yes. 8kw = 8000w I would change the areas in th...
By bontwoody , 1 hour ago
-
RE: Towel rails. An unexpected final hurdle
I had a similar issue but convinced the installer to le...
By Pie_Eater , 2 hours ago
-
Cliff, welcome to the forum. You’re running into one ...
By Mars , 2 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
This whole discussion highlights just how much of a mes...
By Mars , 2 hours ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
@cheshirejohn thanks for the update and for sharing. I’...
By Mars , 3 hours ago
-
RE: Setback savings - fact or fiction?
Here's the same plot, less the R squared values, done q...
By cathodeRay , 5 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 5 hours ago
-
@robs useful thread! Thanks for sharing - Octopus are c...
By big_si , 6 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 8 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 8 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 9 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 13 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 1 day ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 2 days ago
Latest Topics
-
By cliffhanger 2 hours ago
-
Heat Pump Sizing & Installation Costs
By Mars 15 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 16 hours ago
-
SolarPV tables / online calculator
By MichelleC 23 hours ago