Posted by: @ashp-bobba@netdonkey Primary pump should run as follows:
Heating demand on
DHW demand on
Defrost demand on
Secondary pump should run as follows:
Heating demand on
Defrost demand on (only of the volume of the buffer is not enough for the min volume for the ASHP to defrost)
Primary pump runs as described above. Secondary pump is constantly on until DHW is activated
@netdonkey so you may find the pump is wired through the 3 port switch so when sitting in heating mode but the demand is off the pump runs all the time but when switched to DHW it switches off as the movement of the 3 port would break the 3 port switch, if so this would be the wrong way to wire, your wire centre with the ASHP should have electrical connections for the primary and secondary pump set, you should also be able to dip switch or programme the ASHP so it knows if you are using a buffer or just 3 port valve, this way the ASHP will know if to just run one or 2 pumps and when. Not all ASHP are exactly the same and I don't know all of them but most are very simular.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobba@netdonkey so you may find the pump is wired through the 3 port switch so when sitting in heating mode but the demand is off the pump runs all the time but when switched to DHW it switches off as the movement of the 3 port would break the 3 port switch, if so this would be the wrong way to wire, your wire centre with the ASHP should have electrical connections for the primary and secondary pump set, you should also be able to dip switch or programme the ASHP so it knows if you are using a buffer or just 3 port valve, this way the ASHP will know if to just run one or 2 pumps and when. Not all ASHP are exactly the same and I don't know all of them but most are very simular.
Just heard back from Samsung and there is a software upgrade that will fix this logic so the secondary pump isnt always running.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @netdonkeythere is a software upgrade that will fix this logic so the secondary pump isnt always running
Is that upgrade applied automatically over-the-air to all Samsung units?
Or does it require the householder or installer to do something?
Save energy... recycle electrons!
Sheesh! Ash him/her how many sites they have to visit to implement the firmware change.
... and why they couldn't devise a system to do this remotely.
Yes, it might need the homeowner to authorise the upgrade within the App,
and it might need to be undertaken within a time-window in order to prevent hackers attempting such a route in future.
But we already have such functionality on the UK Smart Meter system, and that was designed a decade ago.
Save energy... recycle electrons!
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @netdonkey@transparent Samsung service rep coming out on 3/1
Did you have to pay for the visit?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@netdonkey could this be a first for Samsung? 😂 They do have a habit of charging for visits. I’m curious to see whether it’s an actual Samsung engineer or one of their many agents handling the call-out.
But fully agree in you maximising the visit and getting as much as info as you can out them. Looking forward to the update.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
Samsung problems
2 weeks ago
-
Sudden drop in COP
1 month ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
10 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
-
Any installer recommendations for Samsung ASHP?
2 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 70 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
Hi I'm back after running the ASHP for 7 months now w...
By cliffhanger , 2 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay, @old_scientist I think @old_scientist is o...
By JamesPa , 4 minutes ago
-
-
Crazy large and unexplained so far as I know, I had hea...
By JamesPa , 52 minutes ago
-
RE: Big Changes Coming to Our Heat Pump System
Day one is done. The system’s been fully flushed and ...
By Mars , 15 hours ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 16 hours ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 16 hours ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 17 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 20 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 2 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 2 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 4 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 5 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 5 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 5 days ago