Posted by: @ashp-bobba@netdonkey Primary pump should run as follows:
Heating demand on
DHW demand on
Defrost demand on
Secondary pump should run as follows:
Heating demand on
Defrost demand on (only of the volume of the buffer is not enough for the min volume for the ASHP to defrost)
Primary pump runs as described above. Secondary pump is constantly on until DHW is activated
@netdonkey so you may find the pump is wired through the 3 port switch so when sitting in heating mode but the demand is off the pump runs all the time but when switched to DHW it switches off as the movement of the 3 port would break the 3 port switch, if so this would be the wrong way to wire, your wire centre with the ASHP should have electrical connections for the primary and secondary pump set, you should also be able to dip switch or programme the ASHP so it knows if you are using a buffer or just 3 port valve, this way the ASHP will know if to just run one or 2 pumps and when. Not all ASHP are exactly the same and I don't know all of them but most are very simular.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobba@netdonkey so you may find the pump is wired through the 3 port switch so when sitting in heating mode but the demand is off the pump runs all the time but when switched to DHW it switches off as the movement of the 3 port would break the 3 port switch, if so this would be the wrong way to wire, your wire centre with the ASHP should have electrical connections for the primary and secondary pump set, you should also be able to dip switch or programme the ASHP so it knows if you are using a buffer or just 3 port valve, this way the ASHP will know if to just run one or 2 pumps and when. Not all ASHP are exactly the same and I don't know all of them but most are very simular.
Just heard back from Samsung and there is a software upgrade that will fix this logic so the secondary pump isnt always running.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @netdonkeythere is a software upgrade that will fix this logic so the secondary pump isnt always running
Is that upgrade applied automatically over-the-air to all Samsung units?
Or does it require the householder or installer to do something?
Save energy... recycle electrons!
Sheesh! Ash him/her how many sites they have to visit to implement the firmware change.
... and why they couldn't devise a system to do this remotely.
Yes, it might need the homeowner to authorise the upgrade within the App,
and it might need to be undertaken within a time-window in order to prevent hackers attempting such a route in future.
But we already have such functionality on the UK Smart Meter system, and that was designed a decade ago.
Save energy... recycle electrons!
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @netdonkey@transparent Samsung service rep coming out on 3/1
Did you have to pay for the visit?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@netdonkey could this be a first for Samsung? 😂 They do have a habit of charging for visits. I’m curious to see whether it’s an actual Samsung engineer or one of their many agents handling the call-out.
But fully agree in you maximising the visit and getting as much as info as you can out them. Looking forward to the update.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
8 months ago
-
Sudden drop in COP
1 year ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
-
Any installer recommendations for Samsung ASHP?
1 year ago
-
Issue with Samsung A2W Heat Pump - Water Outlet Temperature
3 years ago
- 23 Forums
- 2,098 Topics
- 46.2 K Posts
- 233 Online
- 3,385 Members
Join Us!
Latest Posts
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 10 hours ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 10 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 17 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
Hmm Before doing that I would want to be certain that...
By JamesPa , 22 hours ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 22 hours ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 1 day ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 2 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 2 days ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 3 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 4 days ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 5 days ago