Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
R32, "optimum" delta T
Hi everyone,
I heard on the podcast recently that Daikin have changed to a 10C delta-T, and that this could reduce the flow rate needed which has intrigued me as I think our house is pipework limited (also heat pump power output limited but that's another story). I then read around a bit and saw that natural refrigerants can operate with a much larger deltaT than synthetic refrigerants like R32, e.g. R290 can operate happily with more than 10C deltaT I believe and CO2 (R744) actually needs a very large deltaT to operate effectively.
This made me wonder, what's the optimum deltaT for an R32 heat pump? I see most default to 5, Daikin just started using 10, and I'd read but without explanation that 8 is the magic number. I'm sure there's a good scientific calculation for this, something to do with PT curves?
Cheers 🙂
There’s no definitive magic deltaT for a heatpump, just pragmatic ‘generally optimum’. If you put more power into the water pump, the deltaT will reduce, and so then does the refrigerant gas-liquid transition temperature, making the heatpump more efficient. This lower deltaT requires a faster water flow though - so the pump needs more power. There’s an overall minimum power - and it’s generally found somewhere around deltaT=5 ish. If your pipes are thin, it’s likely higher.
In our case the pipe run for the heat pump is short and large bore to a heat exchanger, so it's a bit more complicated. Interesting that a smaller deltaT is more efficient, I had thought that a higher deltaT would be more efficient, because it would mean the water was extracting more energy from the refrigerant per m3 of flow. Anyway, for us I think it's irrelevant as I don't think our Midea heat pump allows the deltaT to be changed, it seems to be fixed at 5C.
- 26 Forums
- 2,643 Topics
- 61.7 K Posts
- 128 Online
- 7,043 Members
Join Us!
Latest Posts
-
Mentally you have to separate the ac side and the DC si...
By JamesPa , 5 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 7 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 14 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
Hopefully the ambient temperature sensor drives a weath...
By JamesPa , 1 day ago
-
RE: How many people are happy with their ASHP and do you believe them?
Im looking into these and my figures. The think that I...
By JamesPa , 1 day ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 1 day ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
Yes - we use our Mitsi 14kW unit for cooling. I have j...
By downfield , 1 day ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 1 day ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 2 days ago
-
Hard to tell but I think I have placed the arrow on wha...
By ASHP-BOBBA , 3 days ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Great. My guess is that you will need to re-adjust yo...
By JamesPa , 3 days ago
-
RE: UK warm homes plan - how can it be delivered?
I know it is not as simple as going from a fossil fuel ...
By Batpred , 3 days ago
-
@editor this is great news.
By ASHP-BOBBA , 4 days ago
-
RE: Daikin Altherma 3 with Fan Coils in Puglia (Italy)… Sanity Check on System Operation
AH (Absolute humidity) is grams of moisture per volume ...
By bobflux , 4 days ago