Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

R32, "optimum" delta T

3 Posts
2 Users
1 Reactions
1,158 Views
(@madbilly)
Active Member Member
Joined: 1 year ago
Posts: 17
Topic starter   [#2206]

Hi everyone,

I heard on the podcast recently that Daikin have changed to a 10C delta-T, and that this could reduce the flow rate needed which has intrigued me as I think our house is pipework limited (also heat pump power output limited but that's another story). I then read around a bit and saw that natural refrigerants can operate with a much larger deltaT than synthetic refrigerants like R32, e.g. R290 can operate happily with more than 10C deltaT I believe and CO2 (R744) actually needs a very large deltaT to operate effectively.

This made me wonder, what's the optimum deltaT for an R32 heat pump? I see most default to 5, Daikin just started using 10, and I'd read but without explanation that 8 is the magic number. I'm sure there's a good scientific calculation for this, something to do with PT curves?

Cheers 🙂



   
Quote
 robl
(@robl)
Reputable Member Member
Joined: 4 years ago
Posts: 214
 

There’s no definitive magic deltaT for a heatpump, just pragmatic ‘generally optimum’. If you put more power into the water pump, the deltaT will reduce, and so then does the refrigerant gas-liquid transition temperature, making the heatpump more efficient.  This lower deltaT requires a faster water flow though - so the pump needs more power.  There’s an overall minimum power - and it’s generally found somewhere around deltaT=5 ish.  If your pipes are thin, it’s likely higher.



   
👍
1
ReplyQuote
(@madbilly)
Active Member Member
Joined: 1 year ago
Posts: 17
Topic starter  

In our case the pipe run for the heat pump is short and large bore to a heat exchanger, so it's a bit more complicated. Interesting that a smaller deltaT is more efficient, I had thought that a higher deltaT would be more efficient, because it would mean the water was extracting more energy from the refrigerant per m3 of flow. Anyway, for us I think it's irrelevant as I don't think our Midea heat pump allows the deltaT to be changed, it seems to be fixed at 5C.



   