Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Power surge (?) caused Ecodan damage
So a few weeks back, we woke up to a powercut. We're on 3 phase so didn't immediately notice, but 2 of the 3 phases were off, with 1 still working.
ENWL came out and found a fault in the supply cable in a field nearby, affecting a few properties. I was out at the time, but the power was off for a good 15 hours.
During this time the power came on/off a few times, from what I undestand was part of the repair process / pulling fuses at the transformer/etc.
However, our Ecodan hasn't worked since. We've had the engineer around who's said there's a fault code saying the External Fan Motor is faulty. As we have two in our heat pump (14kW) and both aren't working, Mitsi have said we also need to replace the PCB.
About £1000 + vat to sort.
The heat pump is under warranty by Mitsi have washed their hands of it saying they don't cover if there's a power surge (there's no proof of this, but with both blowing, they've said it's obvious). Our solar monitor doesn't show any voltage surges but I guess they might not register if short, it could just be rapid on/off causing it?
ENWL have also said they have no responsibility to the end user for consequential loss of equipment.
Has anyone else succeeded in getting any of this covered by the DNO or manufacturer? Very annoying when it's completely out of our hands but we have to stump up the bill.
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Posted by: @bensebSo a few weeks back, we woke up to a powercut. We're on 3 phase so didn't immediately notice, but 2 of the 3 phases were off, with 1 still working.
ENWL came out and found a fault in the supply cable in a field nearby, affecting a few properties. I was out at the time, but the power was off for a good 15 hours.
During this time the power came on/off a few times, from what I undestand was part of the repair process / pulling fuses at the transformer/etc.
However, our Ecodan hasn't worked since. We've had the engineer around who's said there's a fault code saying the External Fan Motor is faulty. As we have two in our heat pump (14kW) and both aren't working, Mitsi have said we also need to replace the PCB.
About £1000 + vat to sort.
The heat pump is under warranty by Mitsi have washed their hands of it saying they don't cover if there's a power surge (there's no proof of this, but with both blowing, they've said it's obvious). Our solar monitor doesn't show any voltage surges but I guess they might not register if short, it could just be rapid on/off causing it?
ENWL have also said they have no responsibility to the end user for consequential loss of equipment.
Has anyone else succeeded in getting any of this covered by the DNO or manufacturer? Very annoying when it's completely out of our hands but we have to stump up the bill.
Is it covered under your household insurance?
The alternative could be to get a friendly electrician to test the fan motors and see if there is any output from the PCB.
Could be covered, but by the time we pay excess, increased premium next year, etc I doubt it'll be worth it
Might be a good shout about testing the motors yes, will try that, thanks
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Posted by: @bensebCould be covered, but by the time we pay excess, increased premium next year, etc I doubt it'll be worth it
Might be a good shout about testing the motors yes, will try that, thanks
Are there any fuses or protection devices on the PCB or elsewhere?
Posted by: @bensebWe're on 3 phase so didn't immediately notice, but 2 of the 3 phases were off, with 1 still working.
Do you have a 3-phase heat pump? What's the model number?
Posted by: @bensebAs we have two in our heat pump (14kW) and both aren't working, Mitsi have said we also need to replace the PCB.
It seems like a sub-optimal design if both motors *and* the PCB go up in smoke at the same time.
Posted by: @bensebAs we have two in our heat pump (14kW) and both aren't working, Mitsi have said we also need to replace the PCB.
I presume you have some form of PUZ-ZM140YKA :- https://library.mitsubishielectric.co.uk/pdf/book/PUZ-ZM100-140VYKA_Service_Manual .
The service engineer probably followed the chart on page 60 and found a blown F5 fuse.
F5 being circled in blue on the following diagram
It seems as if the fuse is being used as an overcurrent detection device but does not serve as a protection device. Fan connections are all DC (or pulsed DC?). *sigh*
- 27 Forums
- 2,767 Topics
- 65.2 K Posts
- 1,642 Online
- 7,169 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
Others would have a different interpretation of the BUS...
By JamesPa , 8 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist When I switched back to Cosy (bog standa...
By Toodles , 11 minutes ago
-
RE: Is it the house or the equipment?
@rob-of-york @springswood I did exactly this combina...
By JamesPa , 1 hour ago
-
RE: Missing flow temperature in Heat Geek proposal
I suspect it's a deliberate decisi...
By JamesPa , 1 hour ago
-
RE: Vaillant Arotherm – Using Heating
@l8again Mine is typically using 11w including the i...
By Batpred , 2 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
If you have a flowmeter and two temperature probes, the...
By bobflux , 10 hours ago
-
RE: Siting of the external sensor on a heatpump
@jamespa Absolutely. Even if the same mistake was mad...
By Batpred , 18 hours ago
-
-
RE: Recommendations in Ely (Cambs) area for Full setup checks on Nibe HP setup for House.
In fairness all heating has cost a lot to run in recent...
By JamesPa , 2 days ago
-
RE: Navigating the World of Refrigerants In Heat Pumps: A Guide for Homeowners
Indeed we are invvestigating AC at present and are havi...
By Toodles , 3 days ago
-
No, but the heat pump must be capable of delivering a S...
By JamesPa , 3 days ago
-
RE: Daikin ESPAltherma and Home Assistant installation
It's laziness lol The PV system is very chatty, meter...
By bobflux , 4 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
R (The R Project for Statistical Computing, I use it wi...
By cathodeRay , 4 days ago
-
RE: Vaillant Arotherm Plus 7KW need a service on it
booked it with Vaillant. will use them until i can find...
By AdamK , 4 days ago