Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
One room is colder than the rest of the house
Posted by: @old_scientistIs that because it's putting out more heat than the property requires at this time of year? ASHPs can only modulate their output so low (typically to around a third to a quarter of full output) and achieving continuous running is not always possible this time of year as even at minimum output the heat pump may still be cycling or turning on/off by the thermostat (depending how it's been set up).
Honestly, I don't know. I can see that it is ramping up to 1.75kWh of power but on other occasions it might be around 0.7kWh.
Posted by: @jamespaYes. There is nothing sacrosanct about DT5 even on aggregate, and certainly not for any individual radiator. Furthermore if all the rads have been balanced for DT5 then its possible that all have LSVs turned down, whereas at least one, preferably several, should be fully open.
Installers, if they balance at all, will usually balance for equal deltaT on the basis that this is how the system was designed, it can be done relatively quickly, and if all the calculations are correct this should result in the design room temperatures. But design loss and actual loss are two different things so in practice a basic balance for deltaT may need to be tweaked to get the desired room temps. Turning down one LSV is unlikely to have a major effect on others and yes its generally a better approach than turning down the TRV if only because it ensures that the volume of the radiator is always in circuit to help with cycling and defrost.
If all your upstairs rooms are reaching 24-25 then turning down all the LSVs may not be the thing to do (but neither is having them all switching on and off on TRVs). More likely you could turn up some of the LSVs downstairs (reducing deltaT and thus raising output), perhaps turn them down a bit upstairs, and reduce the WC curve a tad.
@toodles has written an article on balancing for equal room temp/desired temp differences (as opposed to balancing for DeltaT); its worth a read.
That said one doesn't have to get obsessive about eliminating TRVs. I have one out of ~14 rads on a TRV, its in the 'visitor' bedroom and I do it as a courtesy to visitors. I started off with all the upstairs on TRVs and all the downstairs open loop, but gradually adjusted the LSVs until the TRVs became unnecessary. Some installers will say TRVs upstairs, open downstairs. That's not optimum but not completely silly, however it does risk roughly halving the system volume if they all shut down simultaneously, which will half cycle time (bad) at any given set of conditions and reduces the water available for defrost.
@jamespa thanks for all the advice. Just so you know, I'm not ignoring it but pulling it together to try and work out a plan of action. I'm currently measuring what the rooms are heating to so I have an idea at least of what might need doing. So far, the Lounge, which contains the Primary Pod is ranging between 21.8c and 22.5c; the kitchen is between 21.6c and 21.9c; the dining area follows the lounge quite closely (perhaps 0.2c warmer); the hallway is running at around 0.5c warmer than the lounge. Upstairs the rooms I've measured are running at around 23c to 25c.
Anyway, as I say I'm pulling together all the advice to act on. I also have a call out with Octopus to try and speak to someone in more detail about how the Cosy works.
- 26 Forums
- 2,721 Topics
- 63.7 K Posts
- 1,182 Online
- 7,124 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Air to air bus grant installer anywhere
society and politics require things to be made more com...
By Batpred , 1 hour ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
I would also look at an air/air install if you've got t...
By EtchedPixels , 3 hours ago
-
That's more or less what octopus posted about on Facebo...
By JamesPa , 3 hours ago
-
RE: Existing Solar Panel installation - structural roof calculation check
What will also happen is that they see that there is so...
By EtchedPixels , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
@indevolt-tech can you please assist @blizzardgreen.
By Mars , 5 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
It's a great looking piece of kit and the 5kw is very q...
By avenir , 2 days ago
-
RE: Vaillant Arotherm Pro vs new Plus
So with the dedicated Hager CU, flipping the big red bu...
By Batpred , 3 days ago
-
Well I usually do it by feel, which is a slight problem...
By Transparent , 3 days ago
-
@jeff I am well aware of the riskiness of such investme...
By Toodles , 3 days ago
-
Fully understood and entirely reasonable! On the home ...
By JamesPa , 4 days ago
-
RE: Electricity price predictions
So I am really having difficulty trying to work out wha...
By bontwoody , 4 days ago
-
Ok Well almost certainly it could be used instead of ...
By JamesPa , 4 days ago
-
RE: Samsung heat pump - data cable issue
Samsung reference it as "RS485 - COMM" in my manual. ...
By Old_Scientist , 4 days ago
-
RE: SolarEdge SE5000H Inverter Failure
Update. My SolarEdge inverter was replaced yesterday wi...
By L8Again , 4 days ago