Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Newbie: utterly confused with my Mitsubishi Zubadan air source heat pump running on 55C set flow temperature
@jamespa Ah, really? Maybe we’re not as well insulated as we thought.
I am definitely going to follow the more logical approach you outlined. Current setup is just me dropping the flow temp after being alarmed at the amount of electricity we’re using.
I tried changing the flow temp to 36 initially and found the thermostats reporting that the temperature was dropping in some rooms so I’ve upped it to 38.
@sandman1600 if your house is 130m2 and you have a 14kw mitshi machine....... I would be staggered if it wasn't oversized. that's 107w/m2. that's a really really poorly insulated house with holes in the windows
Posted by: @davidnolan22Your problem will be the minimum output of the 14kw heat pump might be not far from your heat loss in cold weather,
I'm sorry to sound thick but what does this mean?
As for the rest of your advice, thank you. Definitely makes sense that it may take time to warm up the fabric of the house. I’d kind of considered that the concrete floor would take time to heat but yeah, I’d not really considered the whole property absorbing that heat. Thanks.
@davidnolan22 Oh wow. Starting to sweat that we have been sold an inappropriate heat pump.
Posted by: @sandman1600@davidnolan22 Oh wow. Starting to sweat that we have been sold an inappropriate heat pump.
Based on the numbers I think its likely its oversized. Not a disaster but it means it will probably cycle on and off a lot. If does prove to be oversized (difficult to tell until you have it working without influence from external controls and also some monitoring) and you have a big enough slab you may find you can cost effectively batch heat the slab during cheap rate periods (much like storage heaters). It may take some experimentation but for sure you are going to save money relative to operating at 55C flow temperature!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I’d also listen to James, he gives good advice.
i didn’t mean to concern you, and I’ve seen the 14kw zubadan modulate quite low on heat pump monitor.
but keep patience with it. It’s take me an entire winter to get a grasp of my system. And you’ll likely run out of time soon and it will get too warm outside
Posted by: @gary@davidnolan22 good spot, that should probably be ideally removed not needed for a heat pump.
Needs to be set so it doesn't do anything if possible.
Sorry I totally overlooked the comment about the Blending Valve. There’s one on each manifold and they’re set to a high temperature… 52 degreesish.
The only option I have is to turn them right down or right up to max.
I’m assuming max would be the best option?
I’ve set the weather curve to -3 and 45 initially.
Looking at reports (obsessively at 5am this morning) it’s mostly stayed at a flat 40 degrees approximately but then its wobbled between 2am and 4am and its flat again for the last hour but falling right now.
I’m going to continue adjusting the curve to see how low I can get it but temperature overnight in the various room thermostats seems to have been kept constant at around the levels we’d like so I’m concerned that reducing them will cause the room temperature to drop too much but we’ll see.
csn you post the pictures again, but just have flow temperature and return temperature showing.
this is the important temp in the primary flow snd return. Do you have a buffer tank? Or low loss header?
snd do you have the UFH design with pipe size and spacing?
and yes, set blending valves to max.
the wobbles are the unit defrosting I think, but need return temp to be sure
@davidnolan22 Apologies. I didn’t realise you could select which options were showing on the graph. 🤦🏻♂️
I’ve attached them below.
The UFH uses 12mm pipe on an overlay board with 150mm spacing. I’ve attached a photo of one of the rooms mid progress for reference.
We do have separate buffer tanks for the hot water and UFH
does it have a finishing screed over it?
do you know how to get the flow rate through the machine from the FT6 control panel?
do you happen to have a temp gun or probe and would you be confident measuring the water temp at the manifold of system side of the buffer?
how many pump and runs do you have off the buffer?
Posted by: @davidnolan22does it have a finishing screed over it?
do you know how to get the flow rate through the machine from the FT6 control panel?
do you happen to have a temp gun or probe and would you be confident measuring the water temp at the manifold of system side of the buffer?
how many pump and runs do you have off the buffer?
The pipes and overlay board were tiled on directly as per Polypipe recommendation.
We’ve been given an FTC7 controller. I’ll take another look but when I checked originally all flow temp indication seems to disappear when we turn on weather compensation.
I have a laser temperature gun. If it’s just a case of aiming it at the right pipe, I can do that. When I figure out what the right pipe is.
I’ll take a look at the buffer tanks and see if I can figure out what’s what. We have a white one and a red one and I think the red one was for the UFH.
Sorry for the lack of clarity. There’s a reason why I thought this was best left to the “experts” that installed it. Clearly a mistake
Most installers I think want to do a good job.
im struggling to getting head around a 14kw unit for a smallish bungalow that I can see insulation has been put into. But the flow rate through the machine will give you a good indication on how much power the unit is giving out. You won’t find that in the main screen. ite I’m settings, running information, then code 540. It will display a number.
was the UFH installed initially into a gas system? You happen you know the output per m2 of that UFH system.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 312 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Our Cosy 9 has been in hush mode for three days. So far...
By KevH , 4 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 4 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 16 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 18 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 18 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 21 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago