Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New to world of ASHPs: Ideal Logic Air Monobloc heat pump 8kW questions
Our new tariff with eon cheaper rates at night. Found out our hallway radiator is a buffer radiator
OK.
To minimise costs and maximise efficiency you are going to need to get your 'weather compensation' curve as low as possible so you are running with the flow temperature (the temperature of thee water produced by the heat pump) as low as it can be consistent with heating your house. If you haven't already, I suggest you read this introduction to heat pumps which explains some of the features of heat pumps including this one.
In essence the process to optimise is this:
1. Set your heat pump to operate 24*7
2. Because you have a Halo (at least I think you do) disable the 'room influence' setting. If you dont have a halo then turn any thermostat up to maximum
3. Turn all TRVs to maximum or remove the heads
This will result in a house that is too hot - so now:
4. Slowly adjust the weather compensation down until the house is just below the required temperature, then turn it up one notch. By slowly I mean no more than one step at a time no more than twice a day, reducing to once per day as you get close.
5. If rooms are settling at different temperatures (or more precisely if the temperature differential between rooms is not what you want - eg you may want bedrooms cooler than living rooms), you will need to 'balance' the radiators using the lockshield valves (the valves opposite the TRVs). We can provide separate instructions for this
The process takes a couple of weeks (which is why installers rarely complete it).
Once this is done, you have the system operating at its most efficient point and should provide a high degree of stability throughout the season. If there are a couple of rooms that, for example, suffer from excess solar gain, you can reinstate TRVs in those rooms but by and large the majority of TRVs should be at maximum or the heads removed.
Ultimately its you choice if you wish to do this. It may, depending on how you are currently set up, save in the region of 10-20% running costs and result in a higher level of comfort. However it does require patience and a level of trust in the theory. It also requires that you 'see it through', stopping halfway may make things worse.
If you do wish to do it please say so and I or another can talk ou through in a bit more detail.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I would worry about the heat loss from the cylinder and pipework in the loft. My cylinder and associated pipework have turned what was the coldest room in my house into the warmest room but at least that heat loss is in the house.
Posted by: @johnrI would worry about the heat loss from the cylinder and pipework in the loft. My cylinder and associated pipework have turned what was the coldest room in my house into the warmest room but at least that heat loss is in the house.
In fairness sometimes it's the only viable location. So long as gge pipes and tank are well insulated it may be the best that an be done.
My cylinder is in a small airing cupboard which, unlike with the previous cylinder, now barely gets warm. We actually instructed the plumber to omit the pipe insulation in this cupboard so we would get some heat for airing! If yours has as much effect as you say something is wrong.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa similar for us.
Our ashp cylinder is in the airing cupboard where very few pipes were insulated.
So after I insulated them the other half complained the airing cupboard was cold so I removed all insulation.
Now, at least the heat loss is still going into the house so what does it matter?
Posted by: @westkentNow, at least the heat loss is still going into the house so what does it matter?
Only to the extent that the heat has been produced at a lower COP than your space heating. But as you are probably talking 1-2kWh max per day, who cares?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,781 Topics
- 65.6 K Posts
- 1,371 Online
- 7,187 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Tesla Powerwall (2) Calibration Cycles
In previous firmware versions you could not effectively...
By Old_Scientist , 17 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu @papahuhu A lot of tears and sweat went into ...
By Andris , 22 minutes ago
-
RE: battery storage without solar
I'll illustrate that Bypass Mode like this: ...
By Transparent , 43 minutes ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
The source legislation is here and is definitive The ...
By JamesPa , 3 hours ago
-
RE: Getting closer to a finished Haier system
Very nice! Congratulations. Big MLC looks neat whe...
By bobflux , 5 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We have the same problem, 12 mature trees clip the morn...
By Papahuhu , 21 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I had a battery and inverter installed a while ago, my ...
By Batpred , 1 day ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@ltron2 The EPC on our house is A-92, however that i...
By Rob of York , 1 day ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
One thing a spreadsheet based heat loss calculator can ...
By cathodeRay , 1 day ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
The layout is confusing - much better like this: We b...
By downfield , 2 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
My experience, backed up by opinions from various frien...
By Majordennisbloodnok , 2 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
I had a meeting today with a company based out of Swede...
By Mars , 3 days ago
-
RE: Review your electricity provider
We were with Octopus in our old house and it was fault...
By ian33a , 3 days ago
-
RE: Estimating true heat loss from twelve months of consumption data
I did, indeed, go with the 12 KW Vaillant unit.  ...
By ian33a , 3 days ago