Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New installation not quite right, advice sought
@cathoderay I agree with cathoderay, my Mitsubishi does not use it's thermistor (in it's control panel) when on Weather Comp mode. If WC is set too high, it uses more power, but if it is set too low, it cycles. I do not want it cycling more than occasionally as I believe that risks premature breakdowns as well as reducing the heating efficiency. So I set the WC a little higher and usually mid morning my room thermostat stops calling for heat and the HP should shut down. I may have to turn the room thermostat up in the afternoon to restart the HP as we have UFH in concrete floors which take a while to warm up, especially on sunny Winter days when the living room is very warm but the floors are cold. At night I program my room thermostat to set back by not more than 2C so the floors will warm up enough by the morning. At the moment, the HP mostly draws approx 1 kW, per our smart meter. I could relocate the control panel into the living room and then use Auto Adaptation in the future but first I would really like to know how that would affect cycling.
Posted by: @sliderule@cathoderay I agree with cathoderay, my Mitsubishi does not use it's thermistor (in it's control panel) when on Weather Comp mode. If WC is set too high, it uses more power, but if it is set too low, it cycles. I do not want it cycling more than occasionally as I believe that risks premature breakdowns as well as reducing the heating efficiency. So I set the WC a little higher and usually mid morning my room thermostat stops calling for heat and the HP should shut down. I may have to turn the room thermostat up in the afternoon to restart the HP as we have UFH in concrete floors which take a while to warm up, especially on sunny Winter days when the living room is very warm but the floors are cold. At night I program my room thermostat to set back by not more than 2C so the floors will warm up enough by the morning. At the moment, the HP mostly draws approx 1 kW, per our smart meter. I could relocate the control panel into the living room and then use Auto Adaptation in the future but first I would really like to know how that would affect cycling.
@Sliderule, I wouldn't become too concerned by some cycling. As @cathoderay has explained, it's what ASHPs do. You fridge cycles all the time and never comes to any harm. The sort of cycling that tends to happen at the right hand end of the WC curve, 2-4 times per hour, is OK. The rapid cycling, 6 plus times per hour that happens when something is wrong or you only have one radiator open isn't, but can usually be fixed.
The way you are running your ASHP sounds fine. AA will have a similar result but without manual intervention. In my case, it pretty much eliminates cycling, even at warmer OATs.
As an alternative to relocating your control panel you can connect a remote temp sensor Mitsubishi Electric PAC-SE41TS. These are about £20 off eBay. You can also use the wireless controller but these are expensive and hard to find right now.
What Ecodan do you have?
@kev-m Hi kev-m, We have an 11.2kW R32 model PUZ-WM112VAA, just installed replacing a 13 year old 14kW Ecodan which had a refrigerant loss last year and again this year with a compressor failure, which is why I am paranoid about cycling. In the early years it wasn't until we got a smart meter that I realised it was cycling and put in some programmable thermostats to help reduce the cycling. I know now that it cycled an average of 4 times a running hour over its life, more in the early years and less later. This time I did the heat loss calculation and went down in power. I am still waiting for the installer to fix a few bugs, but it's running well, and cycles less than once per hour, often only once or twice a night.
I don't think much of the fridge comparison, HPs are much more complicated with variable speed compressors working at much higher power levels and with greater lubrication challenges, lots of soldiered joints in the heat exchanger exposed to greater temperature ranges, let alone the electronics, inverter, plate heat exchanger, reversing valve etc.
It's nice to know that AA works well. I'll probably give it a try when I get time, thanks for that.
Posted by: @bontwoody@guthrie Moving the Samsung controller is quite easy, just two wires. This would be suitable to extend it.
https://midsummerwholesale.co.uk/buy/renewable-heat-accessories/cy-2-core-comms-cable
I think I shall leave that alone for now until I understand if it affects any warranty or suchlike. Probably the easiest long term option.
Posted by: @guthrie2) Would it make sense to just run the hot water tank heating once a day, say 3 to 5pm or so?
I have a similar Samsung and have found a hot water mode that works for me. I am on an Agile tarif and so I force the hotwater to heat up at 2pm-3pm and 2am-3am when electricity is cheap.
I had mixed success with this to start with as I had the schedule set to Off for the remaining time and On only in those time windows. The problem was that if the tank temperature didn't drop to the bottom of its hysteresis band at 40 during that On period, it wouldn't charge. That sometimes left me with water at 41 at 3pm, that wouldn't last until 2am. I found that if I changed a DHW mode setting I could force it to ignore the hysteresis band and charge up when it was turned On. This was much better. However I still had the occasional issue when lots of hot water was used that it wasn't heated on-demand. I also didn't want it heating at peak times due to cost.
I ended up with two time windows where it will be On and forced to heat, two peak times it is Off and won't heat. The rest of the time is in economy mode which is 5c cooler, which has the effect of not heating unless the tank cools a lot. This worked an absolute treat in the summer. I might get rid of the 2am charge in the winter, although the COP hasn't been too bad overnight right now.
Regarding the heating, I do wonder how effective set points are, given they require setting the flow temperature/water law higher to be able to recover. I have been dropping my water law down to a point where around 8c is modulated right down and running continously. It was cycling before. I am gauging this by looking at the operating time measurement in the energy consumption on the control panel. Mine is a slighly different case though as I have a third party controller and no solar panels/battery. I hope to get some panels soon though!
Good luck with your adventures with the Samsung unit. I am enjoying mine overall, but the data exposed thought the controller is minimal. e.g. I can't work out COP of hotwater and heating individually.
@olly That makes sense for the water tank. When our smart meter gets sorted out so it actually works (no signal) it would definitely be worth using an agile tariff.
I am also irritated that it isn't really possible to work out the COP without adding more measuring gubbins.
I am looking at the MCS handover checklist and thinking hang on, we don't have all of that.
We have the invoice, MCS certificate, not necessarily insurance backed warranty details but at least the paperwork for the equipment which contains the usual warranty stuff. Also manuals.
But I do't seeheat loss calculations for each room, internal and design temps, and the duty of the heat emitters in each room. I suppose the design max heat emitter flow temp is in the quote, but I don't see any details of maintenance requirements beyond what the manuals say.
Also no sign of comissioning control values...
I take it this is quite normal.
My installer left me the entire package from soup to nuts but from what I read here that does not seem to be the norm. May I enquire what part of central Scotland you are in? I ask because in my corner of eastern Perthshire we are a group of 16 house none of whom get any mobile signal whatsoever and the few brave souls who have attempted smart meters have very dumb meters. I very much doubt that the Arqiva signal from Durris, near Banchory, can get us.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 624 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 37 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 9 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 9 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 13 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 13 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 14 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 15 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 17 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 17 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 23 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago