Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New installation not quite right, advice sought
@cathoderay I agree with cathoderay, my Mitsubishi does not use it's thermistor (in it's control panel) when on Weather Comp mode. If WC is set too high, it uses more power, but if it is set too low, it cycles. I do not want it cycling more than occasionally as I believe that risks premature breakdowns as well as reducing the heating efficiency. So I set the WC a little higher and usually mid morning my room thermostat stops calling for heat and the HP should shut down. I may have to turn the room thermostat up in the afternoon to restart the HP as we have UFH in concrete floors which take a while to warm up, especially on sunny Winter days when the living room is very warm but the floors are cold. At night I program my room thermostat to set back by not more than 2C so the floors will warm up enough by the morning. At the moment, the HP mostly draws approx 1 kW, per our smart meter. I could relocate the control panel into the living room and then use Auto Adaptation in the future but first I would really like to know how that would affect cycling.
Posted by: @sliderule@cathoderay I agree with cathoderay, my Mitsubishi does not use it's thermistor (in it's control panel) when on Weather Comp mode. If WC is set too high, it uses more power, but if it is set too low, it cycles. I do not want it cycling more than occasionally as I believe that risks premature breakdowns as well as reducing the heating efficiency. So I set the WC a little higher and usually mid morning my room thermostat stops calling for heat and the HP should shut down. I may have to turn the room thermostat up in the afternoon to restart the HP as we have UFH in concrete floors which take a while to warm up, especially on sunny Winter days when the living room is very warm but the floors are cold. At night I program my room thermostat to set back by not more than 2C so the floors will warm up enough by the morning. At the moment, the HP mostly draws approx 1 kW, per our smart meter. I could relocate the control panel into the living room and then use Auto Adaptation in the future but first I would really like to know how that would affect cycling.
@Sliderule, I wouldn't become too concerned by some cycling. As @cathoderay has explained, it's what ASHPs do. You fridge cycles all the time and never comes to any harm. The sort of cycling that tends to happen at the right hand end of the WC curve, 2-4 times per hour, is OK. The rapid cycling, 6 plus times per hour that happens when something is wrong or you only have one radiator open isn't, but can usually be fixed.
The way you are running your ASHP sounds fine. AA will have a similar result but without manual intervention. In my case, it pretty much eliminates cycling, even at warmer OATs.
As an alternative to relocating your control panel you can connect a remote temp sensor Mitsubishi Electric PAC-SE41TS. These are about £20 off eBay. You can also use the wireless controller but these are expensive and hard to find right now.
What Ecodan do you have?
@kev-m Hi kev-m, We have an 11.2kW R32 model PUZ-WM112VAA, just installed replacing a 13 year old 14kW Ecodan which had a refrigerant loss last year and again this year with a compressor failure, which is why I am paranoid about cycling. In the early years it wasn't until we got a smart meter that I realised it was cycling and put in some programmable thermostats to help reduce the cycling. I know now that it cycled an average of 4 times a running hour over its life, more in the early years and less later. This time I did the heat loss calculation and went down in power. I am still waiting for the installer to fix a few bugs, but it's running well, and cycles less than once per hour, often only once or twice a night.
I don't think much of the fridge comparison, HPs are much more complicated with variable speed compressors working at much higher power levels and with greater lubrication challenges, lots of soldiered joints in the heat exchanger exposed to greater temperature ranges, let alone the electronics, inverter, plate heat exchanger, reversing valve etc.
It's nice to know that AA works well. I'll probably give it a try when I get time, thanks for that.
Posted by: @bontwoody@guthrie Moving the Samsung controller is quite easy, just two wires. This would be suitable to extend it.
https://midsummerwholesale.co.uk/buy/renewable-heat-accessories/cy-2-core-comms-cable
I think I shall leave that alone for now until I understand if it affects any warranty or suchlike. Probably the easiest long term option.
Posted by: @guthrie2) Would it make sense to just run the hot water tank heating once a day, say 3 to 5pm or so?
I have a similar Samsung and have found a hot water mode that works for me. I am on an Agile tarif and so I force the hotwater to heat up at 2pm-3pm and 2am-3am when electricity is cheap.
I had mixed success with this to start with as I had the schedule set to Off for the remaining time and On only in those time windows. The problem was that if the tank temperature didn't drop to the bottom of its hysteresis band at 40 during that On period, it wouldn't charge. That sometimes left me with water at 41 at 3pm, that wouldn't last until 2am. I found that if I changed a DHW mode setting I could force it to ignore the hysteresis band and charge up when it was turned On. This was much better. However I still had the occasional issue when lots of hot water was used that it wasn't heated on-demand. I also didn't want it heating at peak times due to cost.
I ended up with two time windows where it will be On and forced to heat, two peak times it is Off and won't heat. The rest of the time is in economy mode which is 5c cooler, which has the effect of not heating unless the tank cools a lot. This worked an absolute treat in the summer. I might get rid of the 2am charge in the winter, although the COP hasn't been too bad overnight right now.
Regarding the heating, I do wonder how effective set points are, given they require setting the flow temperature/water law higher to be able to recover. I have been dropping my water law down to a point where around 8c is modulated right down and running continously. It was cycling before. I am gauging this by looking at the operating time measurement in the energy consumption on the control panel. Mine is a slighly different case though as I have a third party controller and no solar panels/battery. I hope to get some panels soon though!
Good luck with your adventures with the Samsung unit. I am enjoying mine overall, but the data exposed thought the controller is minimal. e.g. I can't work out COP of hotwater and heating individually.
@olly That makes sense for the water tank. When our smart meter gets sorted out so it actually works (no signal) it would definitely be worth using an agile tariff.
I am also irritated that it isn't really possible to work out the COP without adding more measuring gubbins.
I am looking at the MCS handover checklist and thinking hang on, we don't have all of that.
We have the invoice, MCS certificate, not necessarily insurance backed warranty details but at least the paperwork for the equipment which contains the usual warranty stuff. Also manuals.
But I do't seeheat loss calculations for each room, internal and design temps, and the duty of the heat emitters in each room. I suppose the design max heat emitter flow temp is in the quote, but I don't see any details of maintenance requirements beyond what the manuals say.
Also no sign of comissioning control values...
I take it this is quite normal.
My installer left me the entire package from soup to nuts but from what I read here that does not seem to be the norm. May I enquire what part of central Scotland you are in? I ask because in my corner of eastern Perthshire we are a group of 16 house none of whom get any mobile signal whatsoever and the few brave souls who have attempted smart meters have very dumb meters. I very much doubt that the Arqiva signal from Durris, near Banchory, can get us.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 304 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Our Cosy 9 has been in hush mode for three days. So far...
By KevH , 6 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 4 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 16 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 18 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 18 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 21 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago