Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Daikin Altherma 3 11 kW Heat Pump – More Efficient But Not Necessarily Cheaper To Run?
I have a Daikin Altherma 3 11kw heat pump which was installed by Octopus about 15 months ago. Octopus set it up to follow the weather curve but also referencing the Madoka thermostat. Over time I have refined the weather curve to try to improve the efficiency (COP c. 3.3 based on the cumulative information from the Madoka MMI) with some success. Last year the heating and hot water consumption was about 4000 kwh. I am trying to convince myself that I should change from the current setup to pure weather compensation, but the thing that is stopping me is I understand (please tell me if this is wrong) that the 11kw Daikin consumes a minimum of about 900w when the compressor is working and I understand that the aim is to keep the compressor working (heating low and slow). If you were the middle of winter I can understand that this might be fine, but 900w multiplied by 24 hours is 21.6kwh per day as a minimum. My consumption for a day earlier this week when the weather was between about 6 degrees and 8 degrees for the whole day was 16kwh. These numbers suggest to me that pure weather compensation used all through the year would be more expensive but quite possibly give me a higher COP/SCOP.
What is it that I am missing?
Posted by: @optimistic-optimiserWhat is it that I am missing?
The fact that when the demand (ie house loss) is less than the minimum that the heat pump can turn down to' the heat pump will cycle on and off so that on average the demand and output are matched
Like this (from my heat pump) between about 11am and 1800 on the first day and after 11am on the second day.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 1,249 Online
- 7,027 Members
Join Us!
Latest Posts
-
RE: Estimating true heat loss from twelve months of consumption data
Hi @ian33a you could do your own heat loss calculation ...
By Judith , 6 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@djh ah, I have never seen this before, interesting ide...
By ASHP-BOBBA , 6 hours ago
-
RE: Anyone concerned about GivEnergy?
@sunnyskies I agree with Downfield trying to ask the GE...
By Judith , 6 hours ago
-
RE: Setback savings - fact or fiction?
@jamespa — this version may be marginally better: &nb...
By cathodeRay , 8 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 9 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 14 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 16 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 18 hours ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 21 hours ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 21 hours ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
That would be abnormal but I cant see from your charts ...
By JamesPa , 21 hours ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 1 day ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 1 day ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 1 day ago