Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Daikin Altherma 3 11 kW Heat Pump – More Efficient But Not Necessarily Cheaper To Run?
I have a Daikin Altherma 3 11kw heat pump which was installed by Octopus about 15 months ago. Octopus set it up to follow the weather curve but also referencing the Madoka thermostat. Over time I have refined the weather curve to try to improve the efficiency (COP c. 3.3 based on the cumulative information from the Madoka MMI) with some success. Last year the heating and hot water consumption was about 4000 kwh. I am trying to convince myself that I should change from the current setup to pure weather compensation, but the thing that is stopping me is I understand (please tell me if this is wrong) that the 11kw Daikin consumes a minimum of about 900w when the compressor is working and I understand that the aim is to keep the compressor working (heating low and slow). If you were the middle of winter I can understand that this might be fine, but 900w multiplied by 24 hours is 21.6kwh per day as a minimum. My consumption for a day earlier this week when the weather was between about 6 degrees and 8 degrees for the whole day was 16kwh. These numbers suggest to me that pure weather compensation used all through the year would be more expensive but quite possibly give me a higher COP/SCOP.
What is it that I am missing?
Posted by: @optimistic-optimiserWhat is it that I am missing?
The fact that when the demand (ie house loss) is less than the minimum that the heat pump can turn down to' the heat pump will cycle on and off so that on average the demand and output are matched
Like this (from my heat pump) between about 11am and 1800 on the first day and after 11am on the second day.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,741 Topics
- 64.3 K Posts
- 517 Online
- 7,144 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
We have large radiators as our emitters. Room temp is 2...
By Old_Scientist , 13 minutes ago
-
RE: Electricity price predictions
2. As EV ownershp increases it'll certainly increase de...
By EtchedPixels , 46 minutes ago
-
I meant to say I cannot register my kit at Energyplus… ...
By Batpred , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
@indevolt-tech When you say 'dedicated switched fused ...
By JamesPa , 6 hours ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
Unfortunately the answer is Yes you will need a new FTC...
By F1p , 1 day ago
-
RE: PV and battery long payback - sense check query
So if it helps I was recently quoted about 8 grand for ...
By EtchedPixels , 1 day ago
-
RE: HomeTherma Is Live: A New Home-Energy Platform Built Around the Homeowner
Signed up!
By bobflux , 1 day ago
-
RE: Has anyone seen this problem before? Huge anticycling times
Oh dear. Glad it was replaced. I have been mighty imp...
By JamesPa , 3 days ago
-
RE: Can I start an argument about buffer tanks please? 🙂
Dont, just adjust the LSVs to get different temperature...
By JamesPa , 3 days ago
-
RE: Heat pump running costs – what has actually worked for you?
I installed the air source heat pump in January 2026, i...
By bobflux , 3 days ago
-
RE: Grant Aerona Air to Water R290 6.5 kW - Quiet Mark and Silent Running
Thats all interesting. DHW on my Vailant seems to respe...
By JamesPa , 3 days ago