Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Daikin Altherma 3 11 kW Heat Pump – More Efficient But Not Necessarily Cheaper To Run?
I have a Daikin Altherma 3 11kw heat pump which was installed by Octopus about 15 months ago. Octopus set it up to follow the weather curve but also referencing the Madoka thermostat. Over time I have refined the weather curve to try to improve the efficiency (COP c. 3.3 based on the cumulative information from the Madoka MMI) with some success. Last year the heating and hot water consumption was about 4000 kwh. I am trying to convince myself that I should change from the current setup to pure weather compensation, but the thing that is stopping me is I understand (please tell me if this is wrong) that the 11kw Daikin consumes a minimum of about 900w when the compressor is working and I understand that the aim is to keep the compressor working (heating low and slow). If you were the middle of winter I can understand that this might be fine, but 900w multiplied by 24 hours is 21.6kwh per day as a minimum. My consumption for a day earlier this week when the weather was between about 6 degrees and 8 degrees for the whole day was 16kwh. These numbers suggest to me that pure weather compensation used all through the year would be more expensive but quite possibly give me a higher COP/SCOP.
What is it that I am missing?
Posted by: @optimistic-optimiserWhat is it that I am missing?
The fact that when the demand (ie house loss) is less than the minimum that the heat pump can turn down to' the heat pump will cycle on and off so that on average the demand and output are matched
Like this (from my heat pump) between about 11am and 1800 on the first day and after 11am on the second day.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,639 Topics
- 61.5 K Posts
- 944 Online
- 7,035 Members
Join Us!
Latest Posts
-
RE: Daikin Altherma 3 with Fan Coils in Puglia (Italy)… Sanity Check on System Operation
Hi Mars,Thank you so much for your response,I really ap...
By Simon_JM , 3 hours ago
-
RE: ASHP Capacity loss with aging
This is a good question. The short answer IMO is yes, c...
By Mars , 9 hours ago
-
RE: Loud noises in the night - and one for the toolbox?
Brilliant bit of lateral thinking, and a useful one to ...
By Mars , 12 hours ago
-
RE: Setback savings - fact or fiction?
Yes, also the higher OAT end is possibly a smidge high ...
By RobS , 12 hours ago
-
RE: UK warm homes plan - how can it be delivered?
@bobflux My view is that regulation for consumer pro...
By Batpred , 14 hours ago
-
Hi Mars, I've sent you a request to connect me with a...
By sttpd1917 , 15 hours ago
-
RE: Sizing an ASHP; Heat loss and kW
Annual consumption is almost certainly better than an E...
By JamesPa , 19 hours ago
-
Grant Aerona R290 (15.5kW) - How is DHW Target Temp calculated?
Hello all, We have just had a Grant Aerona R290 insta...
By TaffontheTaff , 20 hours ago
-
RE: Advice on Vaillant Sensocomfort
The latest Vaillant announcement I saw said that they w...
By JamesPa , 1 day ago
-
RE: Debugging my legionella immersion heater
I notice this (66 is rather hot) with my legionella cyc...
By JamesPa , 2 days ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
@transparent I thought you would spot that wind turbine...
By Batpred , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils there is no logic to oversizing a heat pump. It...
By AgentGeorge , 2 days ago
-
RE: Vaillant Sensocomfort Time
Thank youy for the pointer. I think I have managed to ...
By ispookie666 , 3 days ago
-
RE: Forum updates, announcements & issues
I have been doing a lot of work on the site lately and ...
By Mars , 3 days ago