Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Low loss header
Does anyone have the latest info from freedom on low loss headers? I asked my fitter to remove the current one and he won't do so because he said it would invalidate the warranty.
I'm sure someone said it's been updated in their documents to not be required anymore.
I've spoken with Freedom and after a really long and useful call (the guy has very helpful in talking over the system) he said the following things at the high level
- There is no reason why you need a low loss header and they will warranty a system without one provided the proper calcs have been done and your system has been designed/confirmed to work without one
- They say a low loss header loses you around 10%-15% efficiency
- They put them in (low loss headers) to ensure customers don't have issues through poor design from the trade
- Weather compensation is set high as they expect the installer to have done the work to set the correct curve
- Midea specify low loss headers in their documents so Freedom is just repeating the statement
- Ideally you should run off the controller and not a thermostat
- They do have an additional sensor to monitor return temps that allows the system to adjust weather compensation on the fly (or that was my understanding)
Now its down to me to see if I can get my fitter to actually make the changes and calculations needed.
Posted by: @bataltoI've spoken with Freedom and after a really long and useful call (the guy has very helpful in talking over the system) he said the following things at the high level
- There is no reason why you need a low loss header and they will warranty a system without one provided the proper calcs have been done and your system has been designed/confirmed to work without one
- They say a low loss header loses you around 10%-15% efficiency
- They put them in (low loss headers) to ensure customers don't have issues through poor design from the trade
- Weather compensation is set high as they expect the installer to have done the work to set the correct curve
- Midea specify low loss headers in their documents so Freedom is just repeating the statement
- Ideally you should run off the controller and not a thermostat
- They do have an additional sensor to monitor return temps that allows the system to adjust weather compensation on the fly (or that was my understanding)
Now its down to me to see if I can get my fitter to actually make the changes and calculations needed.
10-15% is a lot of money at upcoming prices (I appreciate not so much for you personally!). But sounds like good news. Maybe your guy could bypass the LLH but leave in place just in case?
@kev-m speaking frankly I'm not sure my installer is up for it. He's more of a plumber by his own admission. I might need to call freedom and see if they can recommend an engineer Vs a technician.
The low loss header (LLH) is typically used to ensure flow rates and reduce call outs due to restrictive conditions in retro fit setups.
whilst they do work, in practice there is a trade off as the secondary pump, the one which then becomes the heating circulator, has no modulating control from the heat pump. A modern heat pump, such as the Midea, controls flow temp using a combination of fan speed, compressor duty and circulator flow rate. It’s extremely efficient when used this way.
When you separate the ASHP and house circulation this way, the only compensated flow is the primaries from the ASHP.
ideally we wouldn’t use them. In practice there are a number of issues.
1- lack of maintenance leads to flow issues. An LLH Reduces load and gives a low speed area of water in the vessel, this naturally aerates and drops dirt to the internal magnet. Therefore extending the period between faults. It’s a fix rather than a cure.
2- retrofit plumbing can have a number of issues. Unknown pipe routes. Unknown sizing etc. separating the flows means we don’t have to worry too much about that.
3- the manual actually shows it installed. Most installers will not go off piste and the manual is gospel and the word of the warranty gods. Most of it is pure nonsense but it will cause a bun fight in the event of a claim.
there are situations where an LLH is a must. Micro bore setups will not generally allow the high flow rates needed for heat pumps and will constantly fault on flow. LLH fixes that.
In an ideal world, we wouldn’t bother with separation at all. If your plumbing system is good, then theoretically it will work fine. It’s an acceptance of liability. If you were asking me as an installer, I’d be ok with it, I’d just provision to retro fit later, so leave space in the pipework for the LLH and a pump. Four lever valves to allow a section of pipe to be easily removed on the flow and return. Probably install the auto bypass in that section as it can go when an LLH is used.
hope some of this helps.
Internationally recognised award winning installer of heat pumps and stuff
@saenergy I have a feeling you are the person who has been recommended to me by Freedom to modify my system. I sent you an email yesterday (if you're that same SA energy they recommended)
ah that is likely. I’ll be in touch. Been laid up with a broken back.
Internationally recognised award winning installer of heat pumps and stuff
@saenergy that'll be you. The nice lady on the phone said you were at home because of an injury and were just doing emails etc - and clearly checking forums. Hope you make a speedy recovery. In the meantime happy to share any info you might need to understand my system/issues I am trying to fix.
Posted by: @bataltoany idea when you might be able to come to make those system changes?
hi @batalto I’m interested in what you did in the end. Did you manage to remove your low loss header? What was the layout you chose. I’m thinking of leaving the LLH in place and connect the returns through it and then bypass the two flows, connecting them together, with an air vent included.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 470 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 16 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 8 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 9 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 12 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 13 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 14 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 14 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 17 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 17 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 23 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago