Low Flow Rate Error - 8 kW Ideal Logic ASHP - Help!

6 Posts
2 Users
0 Reactions
22 Views
(@wh0am3ye)
Eminent Member Member
Joined: 7 months ago
Posts: 8
Topic starter  

Hi all,

Heating has been kicking in more frequently this week and I am now getting a reccuring low flow rate error on my system, 370F27. I can clear it for a few minutes by switching it off and on again but it appears to be persistant and coming back each time. 
I called up the Ideal Customer Support and they said it may be due to air in the system or a blockage and to contact my installer. We had an ECO4 install, and my installer has been diabolically slow to respond to any issues since they completed the install, so whilst I will get a response there is no guarantee when (current record is 6 weeks between us sending a message and recieving a response from them! And then they'll need to actually get someone out to us which is a whole other nightmare.)

I have cleaned the magnetic filter and checked all the automatic bleed valves, I also bled the radiators and topped up the pressure to just above 1.5bar. All to keep my Primary flow rate sitting at 13l/min which is 1.5l/min below the minimum flow rate for the system. 😩 

Does anyone have any idea of what I might be able to do to increase the primary flow rate so I can have some heating as if it continues to not work, by the time I get a response, my 170 year old stone cottage will have settled back to it's happy place at around 8-10 degrees or just below whatever the outside temperature happens to be! 😱 

TIA!



   
Quote
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2234
 

@wh0am3ye - do you have so called primary and secondary circuits (ie some form of separation of what goes through the heat pump and what goes through the rads)? If so, I guess the magnetic filter is on the rad circuit, but there is usually also one on the primary circuit. If there is, have you checked that? Mine is in something that looks like a ball valve, but the ball is actually a filter that unscrews from the bottom closing the valve (and reopening after checking/cleaning!).  


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@wh0am3ye)
Eminent Member Member
Joined: 7 months ago
Posts: 8
Topic starter  

@cathoderay As far as I can tell, there is just the one filter, on the heat pump side of the cylinder (bottom left in the photo), I attempted to clean it out earlier on, but wasn't able to remove the mesh inside. Perhaps I need to have another go at that as watching the only video I can find online with my issue, the flow rate was being limited by a blocked filter.

WhatsApp Image 2025 10 10 at 19.10.11


   
ReplyQuote



cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2234
 

@wh0am3ye - can't make out all the details from that photo - is it separated (primary and secondary circuit) or just one big open circuit?  

Either way, you need to get the mesh filter out of the magnetic filter, blocked mesh filter and low flow rates have a natural affinity!  


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@wh0am3ye)
Eminent Member Member
Joined: 7 months ago
Posts: 8
Topic starter  

@cathoderay Honestly, I'm not sure. The flow and return come from the heat pump, in to the cylinder on the left side and then the flow and return out to the radiators comes out the cylinder on the right side, where the pump is. I don't know if there is a secondary circuit or not. 

Sounds like the plan for this evening is walk the dog, have dinner and dismantle the filter again! I'll update when I've cleaned it and see what happens!



   
ReplyQuote
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2234
 

@wh0am3ye - it's just possible that is a huge buffer, the mother of all buffers, not sure. What about DHW, is that entirely separate, with a diverter valve? We can explore more tomorrow.

Meanwhile getting that filter out makes sense. Mine does sometimes need a firm pull to get the mesh but out, it gets a bit stuck at the bottom. If you can find a parts diagram (or cross sectional drawing) for yours, you can reassure yourself that you cam make sure you pull in a way that won't do any damage.  


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote