Low Flow Rate Error - 8 kW Ideal Logic ASHP - Help!
Hi all,
Heating has been kicking in more frequently this week and I am now getting a reccuring low flow rate error on my system, 370F27. I can clear it for a few minutes by switching it off and on again but it appears to be persistant and coming back each time.
I called up the Ideal Customer Support and they said it may be due to air in the system or a blockage and to contact my installer. We had an ECO4 install, and my installer has been diabolically slow to respond to any issues since they completed the install, so whilst I will get a response there is no guarantee when (current record is 6 weeks between us sending a message and recieving a response from them! And then they'll need to actually get someone out to us which is a whole other nightmare.)
I have cleaned the magnetic filter and checked all the automatic bleed valves, I also bled the radiators and topped up the pressure to just above 1.5bar. All to keep my Primary flow rate sitting at 13l/min which is 1.5l/min below the minimum flow rate for the system. 😩
Does anyone have any idea of what I might be able to do to increase the primary flow rate so I can have some heating as if it continues to not work, by the time I get a response, my 170 year old stone cottage will have settled back to it's happy place at around 8-10 degrees or just below whatever the outside temperature happens to be! 😱
TIA!
@wh0am3ye - do you have so called primary and secondary circuits (ie some form of separation of what goes through the heat pump and what goes through the rads)? If so, I guess the magnetic filter is on the rad circuit, but there is usually also one on the primary circuit. If there is, have you checked that? Mine is in something that looks like a ball valve, but the ball is actually a filter that unscrews from the bottom closing the valve (and reopening after checking/cleaning!).
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay As far as I can tell, there is just the one filter, on the heat pump side of the cylinder (bottom left in the photo), I attempted to clean it out earlier on, but wasn't able to remove the mesh inside. Perhaps I need to have another go at that as watching the only video I can find online with my issue, the flow rate was being limited by a blocked filter.
@wh0am3ye - can't make out all the details from that photo - is it separated (primary and secondary circuit) or just one big open circuit?
Either way, you need to get the mesh filter out of the magnetic filter, blocked mesh filter and low flow rates have a natural affinity!
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Honestly, I'm not sure. The flow and return come from the heat pump, in to the cylinder on the left side and then the flow and return out to the radiators comes out the cylinder on the right side, where the pump is. I don't know if there is a secondary circuit or not.
Sounds like the plan for this evening is walk the dog, have dinner and dismantle the filter again! I'll update when I've cleaned it and see what happens!
@wh0am3ye - it's just possible that is a huge buffer, the mother of all buffers, not sure. What about DHW, is that entirely separate, with a diverter valve? We can explore more tomorrow.
Meanwhile getting that filter out makes sense. Mine does sometimes need a firm pull to get the mesh but out, it gets a bit stuck at the bottom. If you can find a parts diagram (or cross sectional drawing) for yours, you can reassure yourself that you cam make sure you pull in a way that won't do any damage.
Midea 14kW (for now...) ASHP heating both building and DHW
@wh0am3ye Check out by the ASHP on the pipes next to the unit and see if there is a Y strainer this is usually the culprit to look for 1st
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@wh0am3ye, as @ashp-bobba has pointed out, most flow errors on heat pump systems are caused by a blocked Y-strainer. What's remarkable about them is that they don't require a lot of dirt/corrosive bits to cause the issue. This a good starting point.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor we now fit 800 micron Y strainers rather than the very standard 100Mic, Samsung and a couple of other makes are very sensitive to low flow and we found when servicing as we don't fit Samsung units that the 100Mic can sometimes halve the flow in a clean system, the 800 reduces it by about 10%.
We also sometimes go as far as fitting 35mm Y strainers on a 28mm pipe with reducers just to give a system less restriction but the same protection, just another example of a littler further for it to be a little better, also we actually go back to our installs and service them year after year so helps us not have annoying low flow issues.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Thank you for all your responses!
I gave the magnetic filter another clean and got the mesh out this time. Flow rate back up to 24.5l/min! Success!
I will take a look to see if we have any Y-strainers tomorrow and give them a clean as well if so.
@wh0am3ye super, glad your back up and running.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@wh0am3ye - good news about the flow rate being better after cleaning the mesh filter.
Posted by: @wh0am3yeI will take a look to see if we have any Y-strainers tomorrow and give them a clean as well if so.
Bear in mind the filter if fitted may look like a large ball valve with a cap screwed into the base (as mine does) rather than a Y strainer.
I also think it is still worthwhile identifying the basic design/layout of your system, if only for future reference. I am now more inclined to think that what I thought might be the mother of all buffer tanks may in fact a DHW cylinder, but it is by no means clear. For example, the pump visible in the photo appears to gave been labelled CH1 - which suggests central heating, not DHW.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,255 Topics
- 50.3 K Posts
- 514 Online
- 5,918 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: When will fusion be producing energy?
Ai used to be the same. But then it started delivery of...
By Batpred , 1 hour ago
-
RE: Buying large amp bidirectional RCD and RCBO
Ok, but it would be helpful to get a figure. Perhaps as...
By Batpred , 1 hour ago
-
RE: British Gas Heat Pump Installation Complaint
While it's obviously extremely poor form from British G...
By Steelbadger , 3 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
It’s the perfect strategic partnership between governme...
By Mars , 4 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
Difficult to be completely prescriptive without more de...
By JamesPa , 8 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@allyfish It was going so well with month after month s...
By Toodles , 10 hours ago
-
RE: Electricity price predictions
As that's an energy issue, it would need the DESNZ to p...
By Transparent , 11 hours ago
-
RE: UFH downstairs and radiators upstairs balancing question
Have you tried turning up the stat and turning down the...
By JamesPa , 12 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I have the same firmware. I have MyVaillant version HA...
By JamesPa , 12 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - thank you
By cathodeRay , 13 hours ago
-
RE: Mediation with RECC, what's your experience?
Welcome to the forums @treewizard and sorry to hear abo...
By Mars , 14 hours ago
-
RE: New build installation query
That accounts for why you start with an overly-high DHW...
By Transparent , 14 hours ago
-
RE: Daikin Altherma 3 / HomeAssistant
I would have thought that (instantaneous) power is a fa...
By JamesPa , 15 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Alright, I concede that the Toyotas are, as you say a v...
By JamesPa , 18 hours ago
-
RE: Is it mad to think there should be a minimum SCOP for UK heat pump installs?
Sadly I think it is mad. If the BUS is not granted for ...
By Judith , 1 day ago
-
RE: Who has a V2G EV installation
Perfect, @agentgeorge. I’m always up for some edificati...
By Majordennisbloodnok , 1 day ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Yes but... The evidence is that many heat loss survey...
By JamesPa , 1 day ago
-
What Adam Chapman gets up to in his Spare Time.
Ok, so this just appeared on YouTube (don’t blame me th...
By Toodles , 1 day ago
-
RE: Radiator Sizing Dilemma: Vertical vs Type 33 for Low-Temperature Heat Pump Systems
That's my main concern too. On top of that, I ...
By DREI , 1 day ago