Low COP on Samsung 16kw Gen6

43 Posts
7 Users
7 Reactions
9,060 Views
(@iancalderbank)
Noble Member Contributor
3665 kWhs
Joined: 2 years ago
Posts: 643
 

Posted by: @catapult

@derek-m The good old hand test suggests all 4 pipes are a similar temperature. I'll try and source a proper thermometer. 

The three pumps have three set levels. Currently all running on the highest level. I think they can technically also run on "proportionate", or whatever the P stands for,  but they aren't wired for that. I had a look at the Grundfos manual and it suggested proportionate wasn't suitable for systems with a bypass, which I think I have.

Current flow rate is 32.6lpm. Is that reasonable?

brendon uys has written an extensive article about this based on a lot of very scientific testing. https://renewableheatinghub.co.uk/how-to-correctly-install-heat-pumps-so-that-they-work-properly-and-efficiently

To solve this, its worth you drawing a pipework diagram. Focus on in/out of the buffer, if you have a bypass where is it, where are the pumps and which pump does what, and what flow rates are they running at (may not be the same) if they show that.  then you can write on the diagram what you are seeing at each point.

It looks very much like you have a 4 port buffer setup from your pictures. This buffer is a point at which the hot water coming from the heat pump can get mixed with cooler water in the buffer. This leads to the temperature of the water going to the radiators from the buffer being a bit lower. This means the heat output of the radiators might be below target. So then the system asks the heat pump for more heat , in response to which it to turn up its LWT, which makes it use more energy. you get a warm house, but the COP drops.

some call this effect "distortion". see https://www.youtube.com/watch?v=mNcRx45DQ8M&ab_channel=HeatGeek . The "ideal world approach" as per the article would be to rebuild the system without a buffer, but obviously thats not something you can contemplate right away.

To prove this you need to know water temperatures and ideally flow rates, on the 4 pipes in and out of the buffer. 

If you want to get into datalogging like a lot of the rest of us, then you can learn about the low-cost DIY tech that enables you do datalog the flows and temperatures of each pipe over time - plenty of other posts about that on this (and other) forums, I won't duplicate.

If you don't - go on amazon / ebay and buy some cheap fishtank temperature probes like these with metal ends https://www.amazon.co.uk/Thlevel-Thermometer-Temperature-External-Refrigerator/dp/B07TY6HRL4/

get inside the insulation of the pipes , on a straight bit after any branches, ideally around 30-50cm before it goes into each port of the buffer. align the thermometers metal head so that it is parallel to the pipe, better contact that way. apply a bit of heat conducting paste (like from heatsink assembly on a PC) if you have any (if not, don't worry about it). tape it to the pipe as tight as you can. then replace the insulation. Its fine to have the wire for the thermometer under the insulation until it can find a way out. try to keep the insulation back into its original place.

watch and write down the temperatures over time.

the suspicion / expectation is that the temperature on the  buffer-to-radiators pipe is going to be a few degrees lower than the heat pump-to-buffer pipe. thats distortion loss inside the buffer. in response to that, your heat pump is raising LWT - which is reducing its efficiency.

 

 

My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
👍
1
ReplyQuote
(@catapult)
Eminent Member Member
105 kWhs
Joined: 2 years ago
Posts: 18
Topic starter  

Posted by: @craig1980

@catapult schedule overides the water heating. Mine heats up once for 1.5 hrs (often doesn't take that long) at 3am on our cheaper rate electric. When we get up the hot water is usually at least 48 degrees. We both have showers and there is still enough to wash up later and other small jobs with hot water through the day. You can set several on/off schedules.

 

I stayed up til way past my bedtime to watch what the DHW does. Apparently drops at 0.46 degrees an hour, which seems quite high. So 11 degrees a day. I'm guessing the hot water was heated 3 times a day based on that. It also only took 20 mins to go from 44 to 50 degrees which is a lot faster than I expected. I've now set it up to heat automatically from 6am for 45 mins. I think that'll be the equivalent of using 2/3 of the electric. We'll see how that goes.

dhw

Does the schedule setting include a stop if it reaches set temperature, or does it just blindly heat for the set time?

 


   
ReplyQuote
(@catapult)
Eminent Member Member
105 kWhs
Joined: 2 years ago
Posts: 18
Topic starter  

@iancalderbank thank you. I've purchased the thermometers and will go from there.


   
ReplyQuote



(@iancalderbank)
Noble Member Contributor
3665 kWhs
Joined: 2 years ago
Posts: 643
 

Posted by: @catapult

. Apparently drops at 0.46 degrees an hour, which seems quite high. So 11 degrees a day. I'm guessing the hot water was heated 3 times a day based on that. 

 

seems a bit high. mines 0.275 degrees an hour on a new 300L unvented, running at much hotter temps (I'm charging it on off-peak immersion, thats another story). 

image

 Have a look at the insulation on the pipes in/out of the cylinder. Both the ones carrying the DHW, and the ones from the heat pump. Are any of them acting as radiators? Does the hot water exit of the cylinder go straight up? If so convection currents will carry heat out. insulation mitigates it but doesn't stop it. A short downward-facing loop in the pipe stops it. I insisted my plumbers put this in (they moaned lots) and it made a huge difference.

The other thing could be mixing of hot water at the top , with cold water at the bottom, leading to "medium" temp water that isn't usable. Again with the aforementioned cheapy thermometers, if you're cylinder has more than one probe location,  track the behaviour at the different heights in the cylinder over time, to see if you are getting good stratification or not. this can be about the design of how the cold enters the cylinder - is it turbulent , or is it calm. what you should see is the hot water "moving up" the tank as hot is drawn off , and replaced by cold at the bottom - but the temperature of the hot "lump" not dropping. 

 

My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
ReplyQuote
(@catapult)
Eminent Member Member
105 kWhs
Joined: 2 years ago
Posts: 18
Topic starter  

@iancalderbank The pipes around the hot water cylinder have no insulation... so that's a job for this weekend. The pipes around the HP in the boiler room are mostly insulated, but I think I can improve it.

The pipe out of the top of the cylinder immediately splits into two, one goes left, the other goes up and then left, but no downward loops. I think one is for the hot taps and one is for the shower.

It looks like there's only one temperature probe in the middle of the cylinder unfortunately. 


   
ReplyQuote
(@iancalderbank)
Noble Member Contributor
3665 kWhs
Joined: 2 years ago
Posts: 643
 

@catapult ok, so glad in a way it wasn't insulated - diy fix for that  is easy! see what gain you get from that first. 

what model cylinder / post a photo. there might be a 2nd probe pocket hidden underneath a boiler stat.

My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
ReplyQuote
(@catapult)
Eminent Member Member
105 kWhs
Joined: 2 years ago
Posts: 18
Topic starter  

@iancalderbank

20230123 180054

 

20230123 180106

McDonald Water Storage Vented 200L cylinder


   
ReplyQuote
(@iancalderbank)
Noble Member Contributor
3665 kWhs
Joined: 2 years ago
Posts: 643
 

ok so nothing obvious in terms of additional temperature pockets. might be one at the top, can't tell.but there's lots of pipework that you can insulate for an easy gain. and putting an anticonvection U into the upper horizontal exit wouldn't be hard either.

I can't see any spec for that exact cylinder so you might want to look up what its insulation level is and rated daily wattage for loss. If its a bit low, you've plenty of room to DIY an external jacket round it.

once thing you'll find once done is , you'll have more hot water, but the temperature in the cupboard will drop..... so the washing hanger (I see you have one too) won't dry the clothes as quickly (not  a joke, mrs grumbles at me about this).

My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
ReplyQuote
(@william1066)
Reputable Member Member
1333 kWhs
Joined: 2 years ago
Posts: 206
 

Posted by: @catapult

Is it just a case of "suck it up buttercup, it's cold outside", and there'll be big improvements when it gets warmer?

While I don't have a lot of experience installing heat pumps - I have only installed one (mine).  There are some basic principles I think you can work with on efficiency.  So in an ideal case with a modern heat pump, with your weather compensation settings as you mentioned I worked out that the following should be achievable with a good install.  (it will be a bit less than this with defrosts and pumps).

 

If you are way off the numbers below, then your specific setup in terms of plumbing and emitters is likely dragging your COP down, I can't really help you fixing that, but many others on this site likely can provide useful direction.  I added a comparison between the numbers using the formula and those published in the Samsung documentation, for comparison.

[I removed the bottom of the table, the numbers started to get quite high from a COP perspective]

image
image

   
ReplyQuote



(@kev-m)
Famed Member Member
5606 kWhs
Joined: 4 years ago
Posts: 1276
 

On one of the other heat pump forums, a chap has taken all the COP data from a 11.2kW Ecodan, and the degree days data from where he lives and modelled  different compensation curves against fixed flows degrees for SCOP.  The headline was that WC makes about 25% difference at 55C, 20 at 50C, 15 at 45C, 10 at 40C and 5 at 35C.  

I've asked the chap in question if I can publish the model here as it could easily be tweaked to different Ecodans and a little less easily to different ASHPs.  

 


   
ReplyQuote
(@catapult)
Eminent Member Member
105 kWhs
Joined: 2 years ago
Posts: 18
Topic starter  

Posted by: @kev-m

On one of the other heat pump forums, a chap has taken all the COP data from a 11.2kW Ecodan, and the degree days data from where he lives and modelled  different compensation curves against fixed flows degrees for SCOP.  The headline was that WC makes about 25% difference at 55C, 20 at 50C, 15 at 45C, 10 at 40C and 5 at 35C.  

I've asked the chap in question if I can publish the model here as it could easily be tweaked to different Ecodans and a little less easily to different ASHPs.  

 

 

 

Oh that's interesting. I was kinda hoping it'd be a lot more of a difference! But those numbers seem to be similar to what I'm seeing.

 


   
ReplyQuote
(@catapult)
Eminent Member Member
105 kWhs
Joined: 2 years ago
Posts: 18
Topic starter  

@iancalderbank @derek-m I got some thermometers onto the pipes to/from the buffer. At flow temp of 37 degrees

from ASHP to buffer 36.7

from buffer to rads 34.8

from rads to buffer 33.4

from buffer to ASHP 33.8


   
ReplyQuote
Page 3 / 4



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security