Air source heat pump problems - NIBE F 2040 ASHP
Hello all ... would really appreciate some thoughts and advice. We had our home renovated last year (early Edwardian, about 2000 sq ft, 3 floors, only top floor has insulation) and the gas boiler was replaced with a NIBE F 2040 ASHP. The installer, who fell out with the builders, has been hard to contact/rely on, but we got him round before Christmas because we were freezing - the system couldn't adequately heat the house and everybody was getting sick. The installer added an additional pump and mixer to increase the temperature in the radiators and the house has been warmer, although the ASHP can't meet the temperature set on the thermostat when the outside temperature is below freezing.
Our electricity usage seems extraordinarily high - more than 80 kWh / day when the outside temp is below freezing and our energy supplier wants to put us on a *massive* monthly direct debit. I called in another technician (original installer doesn't respond to messages), he's changed some settings on the 'curve panel', but has not made a huge difference to electricity usage.
Main questions are, how much electricity should a ASHP be using in a house like this? Should we be doing something different with the ASHP? Is comprehensive house insulation the solution to our problems? How difficult is it to find a reputable insulation firm? (An industry person told me that they have far more work than they can take on).
sincere thanks in advance for any thoughts, John.
Hi - it is hard to be definitive. The house type is key and how much insulation too. We have a Samsung Joule 16 kWh ASHP in a large eco house. During these freezing temps we are using up to 80 kWh/day to keep the house warm and heat the water. We heat the house to 22c in the main rooms and 20c in the bedrooms, which is on the high side. We also heat the water to 52c. So we are pushing it. I know the efficiency of ASHPs can fall off a cliff the more load it is under.
I would say that your consumption isn’t off the scale but any insulation/draught proofing you can do the better.
Posted by: @johnsHello all ... would really appreciate some thoughts and advice. We had our home renovated last year (early Edwardian, about 2000 sq ft, 3 floors, only top floor has insulation) and the gas boiler was replaced with a NIBE F 2040 ASHP. The installer, who fell out with the builders, has been hard to contact/rely on, but we got him round before Christmas because we were freezing - the system couldn't adequately heat the house and everybody was getting sick. The installer added an additional pump and mixer to increase the temperature in the radiators and the house has been warmer, although the ASHP can't meet the temperature set on the thermostat when the outside temperature is below freezing.
Our electricity usage seems extraordinarily high - more than 80 kWh / day when the outside temp is below freezing and our energy supplier wants to put us on a *massive* monthly direct debit. I called in another technician (original installer doesn't respond to messages), he's changed some settings on the 'curve panel', but has not made a huge difference to electricity usage.
Main questions are, how much electricity should a ASHP be using in a house like this? Should we be doing something different with the ASHP? Is comprehensive house insulation the solution to our problems? How difficult is it to find a reputable insulation firm? (An industry person told me that they have far more work than they can take on).
sincere thanks in advance for any thoughts, John.
Hi John, welcome and sorry to hear of your problems. Some more information will help you get the best advice:
- Was a heat calculation done as part of the system design? You should have heat losses for each room and an assessment of the radiator size and type needed to heat it
- What rating ASHP is your Nibe?
-what flow temperatures are you running the system at currently? Is it using a fixed flow or weather compensation?
If your ASHP can't heat the house when it's cold then the ASHP itself, or the radiators, could be too small. But that's not possible to confirm without the above information. It could be something else you can fix by changing settings.
ASHP running costs can go up massively when the average daily temperature drops near freezing, defrost cycles start kicking in, and the house heating load is high. We get maybe 4-6 weeks a year like that typically. ASHPs can't throw huge amounts of heat quickly inside the heated space, but if operated properly they don't need to do that. Insulate the house to the greatest extent possible. Whatever energy source your heating system runs off, a poorly insulated house is heating the street. Have you had a recent EPC survey or an energy assessor in to look at the property? EPCs can be a bit wide of the mark, with some strange recommendations, but that would be a good place to start. Edwardian is probably solid wall (?) - internal insulated dry lining? They may be internal architectural features you don't want to compromise or lose, so it can be challenging.
Posted by: @rickk54I know the efficiency of ASHPs can fall off a cliff the more load it is under.
While I am new to heat pumps (just installed 16kW Samsung Gen6) - what I have learnt is that the carnot equation only has 2 parameters (Temp outside ambient, and Temp flow). Efficiency cannot directly be about anything else. (of course it is more complicated than this .... but bear with me)
So efficiency is about flow temp (which you may be able to control depending on your situation) and ambient temperature (the bit you likely can't control with an ASHP). There is a lot of experience and knowledge needed to design/tweak a system to operate with as low a flow temperature as possible and that is the journey I am on, learning from others on this site and elsewhere. This journey made more difficult by the fact the plumbing components you need to have an optimal system are not easy to source, it seems.
Below is the expected COP for flow and ambient of a good modern heat pump, taken from site below.
@william1066 thanks for your feedback. I don't have enough knowledge about ASHPs to fully take this in - at this stage - but I can see that incorrect settings may be part of our problem. thanks again, John
-
Is this ASHP install OK?
7 months ago
-
Help needed in Essex
10 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
12 months ago
-
Installations in Flats
1 year ago
-
Viessmann Vitocal 250-A in the UK
2 years ago
- 27 Forums
- 2,483 Topics
- 57.2 K Posts
- 522 Online
- 6,179 Members
Join Us!
Worth Watching
Latest Posts
-
RE: A Smarter Smart Controller from Homely?
@benson yes, I keep forgetting those tools do these ...
By Papahuhu , 5 hours ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
PS to above Can you please confirm the model of hyd...
By JamesPa , 5 hours ago
-
RE: Say hello and introduce yourself
Underfloor hydronic, powered by both the heat pump and ...
By upnorthandpersonal , 6 hours ago
-
RE: Brine pump error message on Thermia 8kW ground source heat pump system
@schanna no problem at all… I’ll see what my installer ...
By Mars , 7 hours ago
-
@majordennisbloodnok has a clear explanation above, W...
By F1p , 7 hours ago
-
RE: PV export revenue and HMRC
That makes sense. They are companies that are on market...
By Batpred , 9 hours ago
-
RE: R290 Heat Pump and Foundation Air Bricks
I have been having fun and games whilst getting surveys...
By petch , 9 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
@ashp-bobba brill thanks again!
By cmartinbwmba , 15 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay OK, thanks all. Much as I thought. I am usi...
By Tasos , 17 hours ago
-
RE: Setback savings - fact or fiction?
My Midea unit reports the OAT or rather AIT (air intake...
By cathodeRay , 17 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
House was finished several years ago, complicated a bit...
By errmm , 1 day ago
-
RE: Extending Puredrive Modular Batteries
@scmilne If the manufacturer says they are ...
By Batpred , 1 day ago
-
RE: Configuration issues with 10kW Midea R32 heat pump
@cathoderay thanks so much for your helpful and expert ...
By Richard T eco home , 1 day ago
-
RE: Optimising LG Therma V R32 using AI
@bontwoody Yes, remove schedules for now anyway. H...
By Tim441 , 1 day ago
-
RE: Mitsubishi Ecodan Stats Reporting - Accuracy Worsens In Auto-Adaptation Mode
Emoncms uses the instant power consumption and delivery...
By Sheriff Fatman , 1 day ago
-
RE: Global Energy Systems Thurso ASHP
Thanks for the update Alexander, and I'm glad that you'...
By Mars , 2 days ago
-
RE: Help…my NIBE heat pump has faulted again!
@Fiona, thanks for coming back with the update, and I’m...
By Mars , 2 days ago
-
@martinrobinson, must just be the way that they've set ...
By Mars , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa the installer did fit primary pro flexis which...
By AdamK , 2 days ago
-
@papahuhu Ah good point. Perhaps I will need to make...
By Batpred , 2 days ago
-
RE: Plant Room Panel in Garage for ASHP, PV & Battery
@colinc Ours have their own LEDs, with plenty of col...
By Batpred , 2 days ago
-
RE: Gaslighting in the heat pump industry – has anyone else experienced this?
Yes, anyone trying to get a sense of what a heatpump wi...
By Batpred , 2 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Eventually I had confirmation that, when setting an exp...
By Batpred , 2 days ago
-
RE: Five Years of Renewable Heating Hub
By Majordennisbloodnok , 2 days ago