Kev-M's ASHP Performance
I've started this new thread after starting this process off hereÂ
I've had the ASHP since April 2021. Some details of the process of choosing, installing, etc. are here
I'm doing this to see if I can make my ASHP run more efficiently. By that I mean more cheaply, while still keeping the house warm. I'm not unhappy with the system now; it does a really good job of heating the house and hot water but being cheaper and using less energy is always better. Â
My system is a 14kW Mitsubishi Ecodan running 15 radiators. It was all new at installation, specified via MCS heat loss calculations. The house is a 150m2 1990s bungalow. Heating requirement on EPC is about 20,000 kWh/year although I suspect that is an overestimate. I have two zones, controlled by ESI wireless thermostats. As recommended and set up by the supplier, I've been running the system on the weather compensation setting. I've also been using the thermostat to control the zone temps like you would with a gas boiler; turning them down at night and during the day and up in the morning and evening. In terms of comfort, the ASHP does this very well; it heats up the house remarkably quickly.Â
I have MMSP so I can see minute by minute energy consumed, radiator flow temps and outside temp. It's not quite working properly so I can't see energy delivered or COP. Â
The first step in my plan is to control the system using weather compensation and bypass the thermostats. But before I do that, this is how energy consumption looks using the thermostats and the weather compensation curve I was left with. Â
Â
 Â
The two graphs are for 24 hrs 5/11/21. You can see the frost protection overnight, the thermostats kicking in morning and evening and the HW in the middle of the day. Definitely not the slow, steady output ASHPs are said to be suited to. Both power and flow temps are up and down a lot; on the other hand, it's using no power at all a lot of the time.  Total ASHP energy consumed was 30.6kWh. The weather compensation curve is 50C flow at 0C and 20C flow at 20C. Â
Â
First adjustment 7/11/21:
Thermostats set to manual and 30C (i.e. calling for heat all the time)
Weather compensation changed to this
This is 45C flow at -3C and 20C flow at 18C. Â
TRVs in bedroom turned down
My plan is to use the main controller to move this curve up or down until I find the right setting to keep the house at 20-21C. I'll then change the curve so that it works when set to zero. I'll leave settings for at leat 24 hours to let things settle down after changes.Â
Update 08/11/21.
Phew, it's hot!! House is about 23.5C. It's 4C outside and flow temp is about 36C. On the previous settings, flow temp would have been about 42C. Obviously still too high so will shift the curve down later on. Â
Â
@kev-m That is good news, I would shift it to -2 and try that. Because of the steady temperature, most of our customers run their systems with an internal temperature of 19.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @kev-mUpdate 08/11/21.
Phew, it's hot!! House is about 23.5C. It's 4C outside and flow temp is about 36C. On the previous settings, flow temp would have been about 42C. Obviously still too high so will shift the curve down later on. Â
Â
Do you know how the energy consumption looked vs your previous post of 30.6kWh before any changes?
Appreciate no two days are the same so comparisons need to be taken with a pinch of salt.Â
Update; I moved the compensation curve down -2 at 6pm. The house is still 22C or so. I'm aiming for 20-21 but I'll leave it like this for 24 hours. The ASHP is now firing up for about 10 minutes every 20 minutes or so, on low power. From what I have read, that's OK. The radiators are barely warm to the touch but are still convecting; flow temp is about 30. I'll post some graphs and numbers tomorrow.    Â
@kev-m getting there, but will be better when you change the valves. Flow temp dropped from 43 to 30 and the house is still too hot. COP at 30 - round about 7at this ambient temperature. You obviously have a well-designed system, just not run properly.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Thanks Brendan. Â
Update - House is now 21.5C, feels just about right. Before, it would have been 18C and the heating would just have started after the night turned off. Apart from anything else, the house is much more pleasant like this. Flow temps are now only 27C at about 12C ambient.Â
I'm off to the gym now; I'll do some graphs/figures later. Â
@kev-m 😀Â
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
- 22 Forums
- 2,086 Topics
- 46 K Posts
- 20 Online
- 3,377 Members
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Vaillant AroTherm Plus 7kW
@scalextrix if your under unit heater is like our Myson...
By Judith , 1 hour ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@cathoderay how did you get a script to run for that- d...
By benson , 2 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness bold choice on the Kronoterm. Nice! Wi...
By Mars , 8 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 1 day ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 2 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 3 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 3 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 3 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 4 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 5 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 6 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 6 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 6 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 6 days ago