Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@editor No, but any plumber can do it. do not complain about poor running costs when you are not prepaired to do anything about it.
@derek-m I totally agree, just because physics says its possible, doesn't mean it is in practice. However I am inclined to believe the claim for the moment - I can even see his logo behind the controller. I just want to understand exactly the conditions this result comes from. Whats the house heat loss for example?Â
Posted by: @batalto@derek-m I totally agree, just because physics says its possible, doesn't mean it is in practice. However I am inclined to believe the claim for the moment - I can even see his logo behind the controller. I just want to understand exactly the conditions this result comes from. Whats the house heat loss for example?Â
Batalto,
The point where I start having difficulty with Brendon's claims is when he states that insulation and heat loss are of no importance. It just does not equate with the laws of Thermodynamics. I fully appreciate that the efficiency of an ASHP can be drastically improved by changing their operating conditions, reducing heat demand being one of them.
@derek-m you clearly need to replace the heat being lost with at least that amount to maintain a stable temperature.
I get the claim that building performance has no impact on the efficiency of the HP - the HP doesn't care where it is, it will simply perform under the conditions its been told to e.g. flow temperature of X. The occupant however cares greatly as 7.4 COP might be fantastic in terms of efficiency, but if you are putting less heat in than you need it does not matter. I could run my ASHP at a flow temperature of 15 degrees and get a great COP - but my house will be cold.Â
This is why I would like to know what the parameters are for that HP which mean it delivers and keeps a house at 21 degrees when its 3 degrees outside. if the flow temperature is only 27 degrees that means the house is losing 6 degrees across all of its fabric to maintain that temperature. Given the fact radiators aren't ideal for low temperatures as well there are a bunch of questions.
I dreamt I had 10 ASHPs installed last night. Just saying! 🤪Â
I'm assuming @heacol is the only installer we have on the forum at the moment. It does seems that he might be onto something. Perhaps the reason most installations have buffer tanks is that the industry as a whole still has a 'boiler' mentality when it comes to designing installations.
It's easy to see why they think their installations are fit for purpose, if customers are not complaining about COP.
I imagine 'run of the mill' installers have no particular interest in having a system run as efficiently as possible, they aren't paying the electricity bill. They would rather have a system that delivers heat reliably that they don't have to come back to. This is where we are I think.
I agree with @editor that Brendons comments are not being ignored, they just aren't simple to implement for those of us that have systems already installed and may be under warranty.
Mars, perhaps you could raise the question of full flow, buffer less systems if you manage to get an interview with someone suitable?
Â
Posted by: @markcI dreamt I had 10 ASHPs installed last night. Just saying! 🤪Â
I'm assuming @heacol is the only installer we have on the forum at the moment. It does seems that he might be onto something. Perhaps the reason most installations have buffer tanks is that the industry as a whole still has a 'boiler' mentality when it comes to designing installations.
It's easy to see why they think their installations are fit for purpose, if customers are not complaining about COP.
I imagine 'run of the mill' installers have no particular interest in having a system run as efficiently as possible, they aren't paying the electricity bill. They would rather have a system that delivers heat reliably that they don't have to come back to. This is where we are I think.
I agree with @editor that Brendons comments are not being ignored, they just aren't simple to implement for those of us that have systems already installed and may be under warranty.
Mars, perhaps you could raise the question of full flow, buffer less systems if you manage to get an interview with someone suitable?
Â
Mark, Spot on.
Mars can get Heat Geeks on to explain it.
I have found the heat pump industry as a whole to be very divisive, and approaches to thinking and installations are binary. It's either 1 or 0. Buffer tank or no buffer tank. Open loop systems versus controllers (thermostats, TRVs, etc.). There appears to be  no middle ground. I'm not saying that what Brendan does is not better – he is just in the minority because every quote we received (six in total) had a buffer. Most users on the forums that have had heat pumps installed in the last 2-3 years will have buffer tanks. Quick show of hands – who has a buffer tank as part of their heat pump system?
If buffer tanks are installed because installers are "lazy" and don't want phones ringing because flow is insufficient leading to heat pump errors, that's inexcusable. These systems cost a lot of money and they should be installed to the highest, most efficient standard.Â
I will invite installers to have a look through this forum, and hopefully some will respond, and we'll see where this conversation goes.
Â
Â
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Well I’m completely baffled.......I shouldn’t have to faff about with a system like this it’s ridiculous! I didn’t have to do this with a gas boiler!
As someone with a post grad education in a science I find all the do this, try this, maybe this - very unscientific and can see 10 years down the line ASHP will be the elephant in the room.....I should add, I’m normally pretty good at following instructions and working things out and certainly not averse to giving it a go....
Apparently I can’t change the compensation curve settings it has to be the installer.......
@caroline2000 just find the access code for the model you have. A quick google should do it, it'll be in the manual
Â
@caroline2000, this is a worrying trend. Homeowners are asked make the switch, at heavy expense, and there appear to be no concrete guidelines in place that installers should abide by, and as a result consumers are being asked to grapple with, and understand, systems that should just work.Â
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @editor@caroline2000, this is a worrying trend. Homeowners are asked make the switch, at heavy expense, and there appear to be no concrete guidelines in place that installers should abide by, and as a result consumers are being asked to grapple with, and understand, systems that should just work .Â
Mars, I have said this before, it is your friend, Ian Rippin's fault. This is exactly what MCS is supposed to do, it is the installation standard for renewable energy products and installations. Unfortunately, it is a tick box exercise that adds £2500.00 to your bill and produces the result that you all see. Installations that are not for purpose. I despair, and have had many heated arguments with him and other leaders of our industry, I am not very well liked because I do not keep quiet, and believe me, I have paid the price. They are all in if for themselves and not for you, and that is what they are protecting.
Maybe you need to get him back on and hold him to account.
Your statement "as a result consumers are being asked to grapple with, and understand, systems that should just work", is exactly why I have spent the last 10 years designing a unit that "just works", I am now in the process of trying to get funding to take it to the next stage but have now been refused twice by OFGEM and BIAS, they seam to deem a direct electric boiler to be a more environmentally efficient product. But I will persevere.
-
High air source heat pump running costs – Vaillant AroTherm Plus
2 weeks ago
-
What is the lowest temperature you set your heat pump to?
4 weeks ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
1 month ago
-
Rodents! A word of warning for heat pump owners
3 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
4 months ago
Currently viewing this topic 9 guests.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 929 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 10 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 10 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 14 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 14 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 15 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 16 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 18 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 18 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago