Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Is Your House Warmer Upstairs Than Downstairs?
We are running our heat pump with weather compensation and a room thermostat set at 20C in the hall. In the last 24 hours, the temperature has mostly been very close to 20C. It dropped to 19.7C after the overnight hot water cycle and had just a few blips as high as 20.5C.
We have a wide staircase and quite a large landing. We leave all the bedroom doors open all the time, including at night. All the bedrooms have wide open TRVs. The bedroom radiators do not have FRVs and the lockshield valves may be fully open.
We are finding that all the upstairs rooms are running at about 21.5C - i.e. 1.5C warmer than the downstairs thermostat. We all know that hot air rises, so maybe this is just a natural result of convection?
I am wondering whether the upstairs radiators may have more water flow than they need. Therefore, I am considering installing FRVs in the bedrooms as a way to gently reduce the upstairs temperature and hopefully energy consumption.
I am interested to find out whether other people's systems have a similar temperature difference between upstairs and downstairs.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
Posted by: @grahamfI am interested to find out whether other people's systems have a similar temperature difference between upstairs and downstairs
Until I turned down the lsvs upstairs, yes. No real need to buy frvs, lsvs, or trvs fitted with decorator caps to replace the heads, will do the same, albeit with slightly more fiddling, but it's a once only job. Having adjusted the bedrooms are slightly cooler than downstairs, which we prefer.
Posted by: @grahamfWe are running our heat pump with weather compensation and a room thermostat set at 20C in the hall
Before fiddling with the upstairs rads I would turn the downstairs thermostat up to 30 and adjust the weather compensation down to get the house temp right. This should maximise both efficiency and comfort.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Our arrangement of open doors etc. is very similar to yours but we have a requirement for a slightly higher temperature (22.5 deg. C) and we heat 24/7. I have employed the LSV’s to set the output from some radiators just to even out the room temperatures. On bedroom has a programmable TRV so that we may sleep in a cooler room. All the LSV’s downstairs are fully open and the Homely Mode (temperature probe) is in the living room. The maximum variation between rooms over perhaps a week or more might be 0.4 - 0.5 degrees C. so we find our comfort level to be very stable. We have one exception as we keep the bathroom LSV fully open and enjoy a slightly higher temperature and this we appreciate no end! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
We have smart TRVs in the bedrooms set at 20 or 21, but can set back further if required. We are operating under the principle that if used relatively sparingly (16 radiators in total with only 4 having TRVs) it should generally be ok, and this seems to work fine for us.
Fwiw I ried smart trvs with my gas heating. I found it too much faff to use the smart features so reverted to dumb trvs and subsequently, when I got my ashp, to no trvs. The most comfortable for me is the last of these, adjusted on the lsvs to be a bit cooler than the rest of the house and then left. Obviously this will differ from person to person and house to house but, before spending money, try the simplest possible solution.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@benson We have 10 radiators fitted with TRV’s only two are ‘active’ and I am contemplating replacing the other eight with decorator’s caps for neatness. (I blame the MCS for asking installers to fit TRV’s even though they are [in my opinion anyway] more of a source of problems if used extensively than they are of any practical use) Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @grahamfWe all know that hot air rises, so maybe this is just a natural result of convection
Hi @grahamf, yes, exactly this. Unless you live in a house with all internal doors closed, high levels on insulation between downstairs and upstairs, and zero infiltration [air movement] between rooms, you'll get a thermal gradient between low and high elevation. CIBSE and ASHRAE guides have methods of calculating the rate of heat movement due to the natural buoyancy and the lower density of heated air, but to my knowledge, the phenomena is not considered in any heat loss and emitter sizing software. Nor have I seen any consideration of this or suitable correction factors that might be used in CIBSE's domestic heating design guide. CIBSE and Building Regulations assume the two levels are controlled as two zones, so heat can be demanded individually, but despite that being a BR requirement it's not efficient control with low & slow renewable heating where 'open loop' stable system flow rate is best.
It has become a much more prevalent phenomena in recent years due to better thermal insulation performance levels in houses & lower levels of air change in new build or well retrofitted housing stock. If I were to size emitters then for a typical 2 storey domestic dwelling with living space on the ground floor and bedrooms above, I would oversize downstairs by 10% and undersize upstairs by 10%, save for any WCs and bathrooms. Purely empirical 'wetted finger' numbers here, but there's a PHD research paper for some academic heat geek building services engineer on the subject. (They might already be on it...)
@allyfish thanks for your observations. At the moment, I suspect that my upstairs radiators are receiving too much water flow even without the +/-10% adjustments you suggest. I have decided to install FRVs upstairs, so that I have a more scientific flow control mechanism. However, I am not expecting them to make much difference.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
Posted by: @grahamf@allyfish thanks for your observations. At the moment, I suspect that my upstairs radiators are receiving too much water flow even without the +/-10% adjustments you suggest. I have decided to install FRVs upstairs, so that I have a more scientific flow control mechanism. However, I am not expecting them to make much difference.
Why arent you expecting them to make much difference. If the water flow is shut off completely they wont heat at all, and in principle the flow could be adjusted to be anywhere between that (ie zero) and your current flow rate.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaBefore fiddling with the upstairs rads I would turn the downstairs thermostat up to 30 and adjust the weather compensation down to get the house temp right. This should maximise both efficiency and comfort.
I followed your advice and the room temperature drifted up slightly to around 20.5C, even hitting 20.7C at one point. I am not sure that this was due to the thermostat temperature increase to 30C, as the very gentle upward trend had been continuing for several days - since we had our roof put back on!
Anyway, I adjusted the weather compensation Shift down from +2 to +1, the smallest adjustment possible. The temperature is now tracking 20C closely, without any intervention from the thermostat. The heat pump turns off, when the outlet water temperature gets too hot. The attached graph shows that it has been cold enough outside for the heat pump to cycle only a couple of times during the last 24 hours.
I am not expecting FRVs on the upstairs radiators to have much effect, because we leave all the doors open. I think convention will trump the FRVs. One option would be to close all the doors and then balance the temperatures, before opening the doors again. Our installer set the downstairs FRVs to match the radiator capacities, which seems like a good place to start.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
Posted by: @grahamfI followed your advice and the room temperature drifted up slightly to around 20.5C, even hitting 20.7C at one point. I am not sure that this was due to the thermostat temperature increase to 30C, as the very gentle upward trend had been continuing for several days - since we had our roof put back on!
Anyway, I adjusted the weather compensation Shift down from +2 to +1, the smallest adjustment possible. The temperature is now tracking 20C closely, without any intervention from the thermostat. The heat pump turns off, when the outlet water temperature gets too hot. The attached graph shows that it has been cold enough outside for the heat pump to cycle only a couple of times during the last 24 hours.
Good, what Id expect, you may need to tweak the WC as the temperature cools down, but hopefully thats it
Posted by: @grahamfI am not expecting FRVs on the upstairs radiators to have much effect, because we leave all the doors open. I think convention will trump the FRVs. One option would be to close all the doors and then balance the temperatures, before opening the doors again.
As you obviously realise there is nothing the heating system can do to counter heat rising into open bedrooms if you want to maintain them at a lower temperature. You could balance the rooms with the doors closed, but if you always leave them open, whats the point, you are creating artificial conditions for the balancing which dont represent how you are going to operate. If the convection up the stairwell is too much your only options are
1. To have separate cooling upstairs (or open windows)
2. To keep the doors shut
3. Somehow to pipe warm air from upstairs back downstairs (MVHR can sometimes be used to do this)
Alternatively you could forcibly keep the upstairs at the same temperature as downstairs (by turning up the rads), but that might be uncomfortable.
Thats just life, more specifically physics, which sometimes doesn't work in the way we would ideally like it to!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa (Thinks) I wonder if this is a reason for people living in ‘upside down’ houses? The sleeping areas are downstairs and living spaces upstairs. Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 298 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Our Cosy 9 has been in hush mode for three days. So far...
By KevH , 7 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 4 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 16 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 18 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 18 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 21 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago