Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
Are Chinese-manufactured heat pumps falling short of their promised efficiency and performance, leaving consumers and homeowners out in the cold? Our investigation exposes worrying discrepancies in the testing data of some widely-used and available units. Documents provided to us by Pawel, reveal significant inconsistencies in the performance claims of several Chinese heat pump models.
Let's be clear: this is not an indictment of heat pumps. On the contrary, we firmly believe they have a significant role to play in the future of sustainable heating. However, it's crucial for homeowners and consumers to exercise due diligence in their purchasing decisions.
When faced with the option of a less expensive model manufactured in China that has been recommended by an installer to keep initial costs down, it's essential to be fully informed about the potential consequences. Our goal at Renewable Heating Hub is to empower homeowners with the knowledge needed to make informed choices, ensuring they benefit from the true potential of heat pump technology without falling prey to misleading claims.
We look at these models – the PW040-DKZLRS-E/S from Power World, the PASRW020-BP-PS-D from PHNIX and the BLN-012TC1/BLN-018TC1 from SolarEast – to uncover the truth about their efficiency.
While we primarily examined the models above, this is just the tip of the iceberg. Our research extends to a wider range of models, each marred by troubling irregularities in their testing data.
We possess test reports revealing similar issues in other heat pumps, including the Fantastic Energy FEIHCD040S, Gondzik's Zulu 13 R290 and Zulu 23 R290, Guangdong ZenzAir's ZAF-17II/HPSP1, GZ Axen's KS-90W/EN7BP and Jiangsu's MMHP22D1 & MMHP22D2. The list continues with Exinda's XDASH20D3A, XDASH20D3B, XDASH20D3C and their respective S variants.
These findings suggest a systemic issue in the efficiency claims of these Chinese-made heat pumps, casting doubt on their advertised performance and long-term cost-effectiveness, which sheds light on a widespread problem, potentially affecting countless consumers who trusted in these products' efficiency promises.
What does this mean to homeowners?
The heat pumps in question, despite their testing discrepancies, are currently certified by the MCS, making them eligible for government grants. This MCS certification suggests a reliability and efficiency that may not align with what happens in reality, as the test results appear to have been artificially enhanced. Homeowners are thus potentially misled into installing these units, expecting a performance that may not be delivered.
Why should this matter to you? Imagine purchasing a heat pump, banking on its promised performance and Seasonal Coefficient of Performance (SCOP), only to discover it falls short. This shortfall means higher running costs – costs you're likely to attribute to poor design, installation or commissioning. But the real culprit is the product's inability to deliver on its promised efficiency.


Our findings and research
Power World PW040-DKZLRS-E/S
An examination of Technical Report No.: 64.181.23.00422.01, issued by TÜV SÜD Certification and Testing (China), uncovers critical findings that challenge the integrity and efficiency of this heat pump.
Low Temperature Application. Part Load Ratios and Conditions:
- Part Load A (88%): Outdoor temp -7°C, Inlet/Outlet Water temp -7°C/34°C.
- Part Load B (54%): Outdoor temp 2°C, Inlet/Outlet Water temp 2°C/30°C.
- Part Load C (35%): Outdoor temp 7°C, Inlet/Outlet Water temp 7°C/27°C.
- Part Load D (15%): Outdoor temp 12°C, Inlet/Outlet Water temp 12°C/24°C.
Medium Temperature Application. Part Load Ratios and Conditions:
- Part Load A (88%): Outdoor temp -7°C, Inlet/Outlet Water temp -7°C/52°C.
- Part Load B (54%): Outdoor temp 2°C, Inlet/Outlet Water temp 2°C/42°C.
- Part Load C (35%): Outdoor temp 7°C, Inlet/Outlet Water temp 7°C/36°C.
- Part Load D (15%): Outdoor temp 12°C, Inlet/Outlet Water temp 12°C/30°C.


When you delve into the specifics of this data the following discrepancies emerge:
- Compressor Frequency Constraint: The compressor frequency for both test points C and D is noted as 30 Hz. If the heat pump cannot operate below 30 Hz, then at lower part loads (which usually require a lower operational frequency for the compressor), the heat pump may not decrease its capacity as much as it should theoretically. This results in disproportionately high heating capacities for the given outlet temperatures.
- Potential Implications: If the heat pump cannot modulate its operation below a certain frequency, this limitation could lead to a scenario where the heat pump operates more efficiently at lower part loads than it actually does. This would make the heat pump appear to perform better in terms of heating capacity than might be expected given the temperature conditions. It could therefore be misinterpreted as deliberate manipulation of performance data if the heat pump’s inability to operate below a certain frequency threshold is not transparently disclosed. Such an omission significantly impacts the portrayal of the Coefficient of Performance (COP) and the overall efficiency of the heat pump, potentially misleading consumers about its true capabilities.
- Mismatch in Heating Capacity for Test Points C and D: The heating capacities for test points C and D do not decrease proportionately with the decrease in outlet temperatures when compared to other test points. This mismatch can occur if the heat pump is maintaining a minimum operational level due to the 30 Hz compressor frequency constraint, which prevents the unit from reducing its output as the demand (part load) decreases.
The mismatch in heating capacities at test points C and D, given the constant compressor frequency and the lower outlet temperatures, suggests that the heat pump's performance at these part loads is not as variable as one would expect. This could be indicative of a performance curve that is not linear across all operational ranges, which should be communicated transparently to users and reflected accurately in performance data sheets.
The consistency of the compressor frequency at 30 Hz suggests a lower limit to the modulation capabilities of the heat pump. Such a limitation should be accounted for in the COP calculation and clearly stated in the performance data to ensure that users are not misled about the efficiency and operational flexibility of the heat pump across its entire working range.
PHNIX PASRW020-BP-PS-D
In the case of the PASRW020-BP-PS-D model, Pawel also provided a technical assessment from the Danish Technological Institute (DTI) in addition to the testing data in Technical Report No.: 64.181.22.00329.01 Rev.00, which was also compiled by TÜV SÜD Certification and Testing (China). The assessment from DTI spotlighted several issues in the PHNIX heat pumps' testing, not dissimilar to the previous case.


- Mismatch in Heating Capacities: In test points C and D, the measured heating capacities were significantly higher than expected. This was likely because the heat pumps could not operate below a certain compressor frequency, leading to inflated heating capacities at these part loads.
- Non-Compliance: The tests did not follow the EN 14825:2018 standard correctly. According to this standard, if a heat pump cannot reach the required part load ratio, the indoor heat exchanger temperatures must be adjusted. These adjustments were not made, resulting in inaccurately high COPs and overstated seasonal energy efficiency.
- Implications for Energy Label Ratings: The failure to adjust temperatures according to EN 14825:2018 led to increased COPs in test points C and D, inflating the seasonal energy efficiency and affecting the heat pumps' ratings on energy labels.
According to DTI this assessment highlights critical testing protocol deviations, raising questions about the reliability of the reported energy efficiency of this PHNIX heat pump model.
Tests were also conducted by Fraunhofer Institute and, in summary, the heat pump frequently entered defrost mode during tests, which hindered the ability to measure it in a stationary state. Adjustments were made to extend the time between defrost cycles, yet this didn't allow for stationary operation of the heat pump.
Their tests faced further issues at -7°C, where the heat pump continuously malfunctioned and reported an error. The team decided to measure the points at positive temperatures (12C), but even under these conditions, the heat pump did not perform as expected, showing irregular output increases.
SolarEast BLN-012TC1 & BLN-018TC1
In Technical Report No.: 64.181.22.02858.01 Rev.00 dated 24/10/2022, once again compiled by TÜV SÜD Certification and Testing (China), when you look at the data collection period for the test across samples A-F, the time allocated for the test is 2 hours, 10 minutes.
In tests for BLN-018TC1, dated 24/04/2023 (Technical Report No.: 64.181.22.04448.02 Rev.00), the data collection period has been reduced to 1 hour, 10 minutes. Corresponding with this reduced collection period, we have seen test reports from other brands and models that have also reduced data collection times.


Correspondence from testing labs that was shared with us contends that, given the frequent initiation of defrost cycles that adversely affect a heat pump's performance, shortening the data collection period can prevent the evaporator from icing up during tests, thereby helping to improve the test results, and giving the products a better efficiency rating.
Heat Pump Misrepresentations: A Call for Greater Consumer Awareness
It is concerning that despite the emerging issues, these heat pumps are still listed on the MCS and remain eligible for government grants. This situation is further complicated by the existence of OEM units, essentially the same models marketed under different brand names, which are also included on the MCS list. Adding to the complexity, you won't find their certificates on the Keymark database in Europe because they have been removed.
The lack of action from MCS to revoke these potentially misleading certifications raises significant concerns. This situation is particularly troubling for homeowners who installed these heat pumps under government grants, relying on what appears to be flawed data. The real impact on these households, who placed their trust in the system's integrity and the MCS's accreditation, is a critical and potentially distressing issue that needs addressing.
It also raises serious questions about the capabilities of these heat pumps and the consequences of inflated test results. Consider this: a product marketed as a 22kW unit, such as the NORDIC R290 Propane 22KW, might actually be a 10kW heat pump with an overstated nominal heating capacity. This is not just misleading; it represents a significant deviation from the expected performance, resulting in a unit that is potentially incapable of delivering the performance advertised on its badge.
For a cautious consumer, it's advisable to consider choosing products from established European, Japanese and Korean brands. These brands are often supported by testing from credible, professional labs, offering an additional layer of assurance regarding their quality and reliability. It's always beneficial to research and select products that have a strong track record of safety and efficacy.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
No great surprise there. You get what you pay for...
There were suspicions last summer: https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/en14825-chinese-ashp-manufacturers-cooking-the-books
A well-known UK stockist of Japanese made ASHPs by Chofu, across their UK range state COPs to EN14511 @ A7W35 in their web site, marketing and installation literature that are significantly higher than the OEM's product data sheet and web site figures. My real world experience is that the OEM SCOPs are more realistic and achievable. Japanese technical data and quality control is usually very robust & reliable. Branding the product up for the UK market is the performance equivalent of a 'go faster' badge on a boy racer's car it seems...
UK branded product literature:
Chofu OEM literature:
6 kW unit +17%, 10kW unit +20%, 13kW unit +22%, 17kW unit +11%. But they are physically identical units....
@allyfish I completely missed your post from last summer – this coincides with the timelines when our contact that "leaked" the test reports to various authorities around Europe and the UK. How did you hear about this at the time?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Answer: yes, probably lied to. Reality: probably doesn’t matter much unless you were borderline on capacity.
my made in china unit seems spot on. Not a whole lot of Chinese in it mind you, all the important stuff is from Carel, Italian …. Don’t know what’s worse 🤣
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
I think whats more important than this, is to have the devices that do have perfectly reasonable databook performance figures , installed in such a way that they achieve those figures, monitored after the fact to make sure. rather than the constant flow that we see of badly designed/implemented setups that don't.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
-
Ecodan consuming 100kwh per day in new build!!!
2 weeks ago
-
Running my new Nibe ASHP efficiently
1 month ago
-
Ecodan help with efficiency setup and design - removing manifold mixers, LLH and pumps
1 year ago
-
Ecodan wont heat with mild outside temps
1 year ago
-
Auxiliary Heating
2 years ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 62 Online
- 2,276 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
All agreed. if you want to delete our exchange for cla...
By JamesPa , 5 minutes ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 50 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 1 hour ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 2 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 2 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 4 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 6 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 8 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 20 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 23 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 8 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 9 hours ago
-
SolarPV tables / online calculator
By MichelleC 16 hours ago
-
By Toodles 2 days ago