Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Grant Aerona3 13kW Noisy pipes after balancing
Hi @grantmethestrength, looks like your pump setting is on speed 3 in your Grant ASHP, grab the installation manual, read up on circulator pump dip switch settings and drop it to speed 2, circa 3000rpm. You may have to open up some rad lockshields and recheck, but getting a pump speed appropriate to the required flow with a reasonably open circuit is preferable to the pump running flat out against closed valves. The Grant ASHPs are defaulted to speed 3 when supplied, and few installers bother to change that, because throttling the flow on the Grant supplied flow setter/indicator is the lazy, quicker and easier option.
Thanks guys, I will open up the valves again and check the dipper switches when I get home tomorrow. Quick follow up question, if the flow has been limited at the ahem new to me flow valve 😜 if I change the pump speed to 2 do I just open the flow valve up to get say 28l/min or just open it as wide as it can go (well until it gets noisy again lol)? Is there a sweet spot?
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
25kWh Sigenstor battery
@grantmethestrength The new to you flow valve is summat I know not of at this stage but, my gut feeling is that if it is in the water circuit, is partially closed and you have noise then, it is well worth noting its’ position then openi9ng it up fully to see what happens. If at this point, everything runs happily still but the noise hasn’t disappeared, then try the heat pump’s pump by reducing the speed a little. little by little improvements will come your way! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @grantmethestrengthif I change the pump speed to 2 do I just open the flow valve up to get say 28l/min or just open it as wide as it can go (well until it gets noisy again lol)? Is there a sweet spot?
Pretty much, noise is caused by high fluid velocity and turbulence created by restrictions, which is caused by things like nearly closed balance valves, TRVs, etc. Noise is also wasted energy, as is a pump on max speed against partly closed valves which could be on a lower speed setting. Open all the valves up, including the flow setter/indicator, set the primary circulator to an appropriate speed to get the required system velocity, and go from there 🙂
- 27 Forums
- 2,778 Topics
- 65.5 K Posts
- 2,051 Online
- 7,185 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Say hello and introduce yourself
@olivierm welcome to the forums and finding the right i...
By Mars , 32 minutes ago
-
RE: Estimating true heat loss from twelve months of consumption data
Finally, after what seems like an eternity, we paid a d...
By ian33a , 4 hours ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
@paul1098 — as we are getting down to the nitty gritty,...
By cathodeRay , 16 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
I’ve had two calibration cycles in the last three month...
By Davesoa , 21 hours ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@editor That's a pity, but thank you for checking. I'l...
By ltron2 , 1 day ago
-
My fifth heat pump book, Heat Pumps Explained, is out n...
By Mars , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
Just furkled Into the parameter menu. Found the master ...
By AgentGeorge , 2 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
It's interesting that Norway with a much colder climate...
By Rob of York , 2 days ago
-
RE: Review your electricity provider
Happy to add Scottish Power and the review 'dont touch ...
By JamesPa , 2 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
Yes, and I would suggest likely to get worse with more ...
By Batpred , 4 days ago
-
RE: Electricity price predictions
This topic seems more suitable for this thread... I a...
By Batpred , 4 days ago
-
RE: Why are ASHP installs so expensive?
It is clearly difficult to say, there must be cases whe...
By Batpred , 4 days ago
-
RE: Panasonic Free Multi Z and Etherea Internal units.
@dgclimatecontrol Thank you for that information and re...
By Toodles , 4 days ago
-
RE: My Kronoterm Adapt 0312 ASHP is finally installed!
@editor It was serendipitous really. Both my wife and I...
By tomasmcguinness , 4 days ago