Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Fun with Samsung Gen 6 Yearly Schedules
Note: The following procedures will only work if you have the samsung controller configured as the thermostat, it does not apply to third party thermostat control.
I have recently been modifying my controller configuration for my bivalent heat pump / oil boiler system due to clashes between how the oil boiler and heat pump need to be controlled. It became apparent to me that having a single thermostat (Honeywell Home Smart Thermostat) to control both systems was not going to work long term and as I have now found a suitable cabling route (not realised during installation in 2023) in the house, I moved the Samsung controller from my external boiler room into the house.
Once I had completed the electrical work, I reconfigured the Samsung controller to become a room thermostat and enabled it to use its internal abilities to decide its own weather curve (flow temperatures) required to achieve the room target temperature versus outside temperature.
The other advantage of configuring the controller to be a room thermostat was it enabled me to take advantage of the additional Weekly and Yearly schedules alongside the Daily schedules. As there is little in the way of information on this topic (a couple of short YouTube videos) I thought I would share my setup experience in case it is useful for anyone else.
The yearly schedules I was aiming to configure are as follows:
Summer:
Active: June, July and August
CH state:
Off
Autumn:
Active: September and October
CH state:
05:00hrs to 19:00hrs room temperature +20C
19:00hrs to 05:00hrs room temperature +18C (setback)
Winter:
Active: November, December, January, February and March
CH state:
03:00hrs to 21:00hrs room temperature +21C
21:00hrs to 03:00hrs room temperature +19C
Spring:
Active: April and May
CH state:
05:00hrs to 19:00hrs room temperature +20C
19:00hrs to 05:00hrs room temperature +18C (setback)
Creating Groups:
The above season groups need to be created first by
1. Selecting the cog button
2. Select schedules and press "Ok"
3. Select "Add Schedule" press "Ok"
4. Select "Yearly Schedule" press "Ok"
5. Select "Add Group" press "Ok"
At this point you can select one of the following groups (Group 1, Group 2, Rainy, Dry, Spring, Summer, Autumn or Winter.
6. Select the appropriate group and press "Ok"
7. Switch on the months of the year this group will be active by using the navigation arrows to select the month and toggle the selected month "On" or "Off"
8. Press "Ok" when all months have been set for the group.
Creating Schedules:
At this stage you can now add individual schedules to the season groups. These steps are for configuring the above Winter group as an example but are the same steps for all other groups.
1. Press the cog button on the controller
2. Select schedules and press "Ok"
3. Select "Add Schedule" press "Ok".
4. At this step, highlight the "Winter" season group and press the on screen "Select" button by highlighting it and pressing "Ok" on the controller interface.
5. Set individual days of the week the schedule will run by toggling each day "On" or "Off" using the conroller navigation buttons, then press "Ok" when finished
6. Set the time of day to "03:00" for the schedule to become active and press "Ok"
7. Select "On" and "Zone" (if more than one zone available select the required zone) press "Ok"
8. Set "Heat" and set the room temperature to "21C" (or flow temperature if system is configured to use flow temp) press "Ok"
To add the set back simply repeat the above steps but set the time in step 6 to "19:00" and set the room temperature (or flow temp) in step 8 to "19C"
All the schedules associated with the Spring, Autumn and Winter groups should be in the "On" state so the heat pump will be active throughout the heating season. In the case of the Summer season, we want the heating to be off so step 7 in "Creating Schedules" in this case would be "Off" for the zone selected at the time set in step 6.
The "Off" will then become active and re-trigger every 24 hours to ensure the heating system remains off.
Hope the above is useful and if anyone finds errors in the above procedural steps please let me know
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
- 27 Forums
- 2,790 Topics
- 65.9 K Posts
- 3,823 Online
- 7,194 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
The video in the link mentions a direction arrow, which...
By Singlespeed , 10 hours ago
-
RE: Cooling/heating with one unit
@rob-of-york thank you. Hadn't occurred to me that some...
By mrkfm , 13 hours ago
-
RE: Renewables & Heat Pumps in the News
Posted by: @editor I think we should make that approa...
By Rob of York , 18 hours ago
-
RE: Does anyone have experience of a smart water meter?
My neighbour received an email from Anglian Water sayin...
By AndrewJ , 19 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Well the military is well known for going green, isn't ...
By Majordennisbloodnok , 21 hours ago
-
RE: Why are ASHP installs so expensive?
I've ripped out over 11kw of storage and panel heaters ...
By Singlespeed , 21 hours ago
-
RE: Safety study for plug in batteries out to tender - looks like Q3 2027 at best before legal
I think it may depend how much of the world is on fire ...
By EtchedPixels , 1 day ago
-
RE: Air-to-Air Heat Pumps & Air Conditioning: UK Heating and Cooling Q&A
I hope it's not the same people who make the awful TV s...
By EtchedPixels , 1 day ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
I found some interesting data about the price of heat p...
By Rob of York , 2 days ago
-
RE: PV and battery long payback - sense check query
Thanks for all the comments. I finally got to the bott...
By DavidB , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
People following this thread who are hoping that plug i...
By JamesPa , 2 days ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
By Singlespeed , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
just had Vaillant over to service the HP and asked abou...
By AdamK , 2 days ago
-
RE: tepeo ZEB UK Support & Info Thread
OK so ZEB is basically a variant on a storage heater, b...
By JamesPa , 4 days ago
Members Online
No online members at the moment