Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan thoughts please: QUHZ-W40VA takes longer than I would like to revert back to heat mode following a DHW cycle
Welcome to the forums @barry-the-bear
Your experience does seem a bit unusual, but I noticed that the unit in question is a 4kW Ecodan QUHZ. What makes this model stand out is that it uses CO2 (R744) as its refrigerant, which is quite different from other Ecodan models that use traditional refrigerants like R32. While I’m not a refrigerant specialist, CO2-based systems tend to operate differently, especially with regard to temperature management.
One key aspect is that CO2 systems generally prefer lower return temperatures, and this can impact the delta T. With a CO2 system like the QUHZ, a delta T of around 30°C isn’t uncommon, which can explain why you’re noticing specific temperature behaviours. It’s possible that the system is designed to prioritise certain flow temperatures during mode changes (for example, between heating and defrost) to optimise refrigerant performance.
It might be that when the unit switches modes, it needs to hit a specific flow temperature - like the 32°C you’ve observed - before resuming normal operation. This is likely tied to the system’s internal logic for efficiently managing CO2 refrigerant, which behaves differently compared to more common refrigerants.
It could be helpful to have a chat with a Mitsubishi support to get some insight into how the QUHZ manages these transitions. They should be able to explain the logic behind the temperature regulation more clearly.
Let us know.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Thank you for your welcome and reply.
You are right that the QUHZ use CO2 (R744) refrigerant. CO2 does have special properties and may operate more efficiently closer to its critical point (31°C), but I have no idea if that plays a role in the delay transitioning from DHW mode to heating mode - and I'm not sure Mitsubishi do either or at least it's not something they've bothered to explain to me. I have talked to them several times, but not once was the refrigerant mentioned.
About the specific (transitional) UFH flow temperature, there seems nothing special about 32C. That's just what it was on the day. What seems to matter is that the post DHW flow temperature matches the required UFH flow temperature. If I fixed the UFH flow at 40C for example the UFH would start fairly promptly, at 38C it take a little longer and so on. The UFH delta T is typically around 7C.
Cheers!
So I suppose the real question is you house cooling down to much or are temps ok?
How is the circulation pump operated on all the time?
The house isn't cooling while for heat mode - the fabric of the house and the MVHR and so on ensures that doesn't happen, but that doesn't mean it isn't desirable to have a shorter delay. The pump doesn't run all of the time.
Posted by: @barry-the-bearThe pump doesn't run all of the time.
That may be your issue. You have hot water sitting in, I assume is an insulated pipe, so it will not cool quickly. If your pump runs when ever there is a demand for heat, the hot water in the pipe is flushed away when the diverter valve moves to heating system and cools really quickly.
The other issue could be if you have mixer valve on the UFH, it will just recycle 90% of its return water and only let a small amount of hot water through. So you see an issue, but in reality you UFH is getting hot water.
Today even without having to do DHW heating, my ASHP compressor went off 8 hrs ago, water is just circulating, sensing the return temp, if it needs the compressor to start it will.
I don't know if you are right or not!. I am sure though that the UFH doesn't receive any hot water until QUHZ sends it and UFH pump, housed in the packaged thermal store won't run until the flow temperature reduces to the required level. My thought was that the rapid cooling from minute 11 to 15 ideally should continue a little longer.
- 26 Forums
- 2,677 Topics
- 62.6 K Posts
- 140 Online
- 7,090 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Heat pump installation quotations
That will be absolutely murdering your energy efficienc...
By EtchedPixels , 1 hour ago
-
RE: Harvest Thermal - ASHP with a smart thermal battery
The cooling side works much better if you can figure ou...
By EtchedPixels , 2 hours ago
-
Floor standing brackets for K3 rads
My neighbour is a plumber and said I would need to fit ...
By Singlespeed , 2 hours ago
-
After an intense recode, I’m pleased to announce that w...
By Mars , 2 hours ago
-
Why do you want to maintain a specific deltaT? The out...
By JamesPa , 4 hours ago
-
Hopefully this will answer your question. To...
By ASHP-BOBBA , 4 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I would be interested to find out if others do this and...
By ASHP-BOBBA , 5 hours ago
-
Don't you dare. You just carry on as you are; as @batpr...
By Majordennisbloodnok , 6 hours ago
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
@ragtime27 some rooms in our house only have one place ...
By Judith , 6 hours ago
-
RE: Several AC coupled batteries
That is a good point, a manufacturers can stop trading,...
By Batpred , 10 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Hi @hanno - good question. The range of hybrid invert...
By Transparent , 11 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
@transparent the inverter was installed in 2021 and afa...
By Tim441 , 11 hours ago
-
RE: Say hello and introduce yourself
I hope so, @toodles. It's not often that we see a situa...
By Majordennisbloodnok , 15 hours ago
-
RE: Electricity price predictions
Good point, I do expect the bonus of putting my energy ...
By Batpred , 2 days ago