Ecodan help with efficiency setup and design - removing manifold mixers, LLH and pumps
thank you that's very good to hear, I will hopefully start the mods at the end of the week all going well.
alongside I plan to rewire so the main FTC display will be the one thermostat its downstairs in the centre of the house and the bedrooms will just act as temperature limiters
@rich I agree with your assessment that your pump is oversized, I have the same unit in a similarly-sized house with a design temp of 50° at -2.5 and I have come to the same conclusion. MCS heat loss assessments are notoriously pessimistic compared to how people find their houses perform, and EPC values are an over-generalised, rushed, stab in the dark. Unfortunately these are the figures that your plumbers supplied to Mitsubishi to get the OK for the system they put in. The SCOP value will assume far more heat is being supplied and probably has no idea of how much baseload all those pumps are drawing.
I slightly disagree with Derek’s statement that running at 33 at 0C is not a matter for concern in that it does show that you don’t need a large heat input at a low OAT but need even less for the vast majority of the time. I certainly find that my 8.5kW unit only runs continuously at 3°C or below, above that it cycles as it can’t modulate down far enough, and it cycled more frequently under WC than it does with AA. Rather than have the lowest flow temp but have pumps running circulating the heat 24 hrs a day, perhaps shorter defined on/off sessions charging the slabs at a higher temperature would work better for you. There are those who only run their HP during low-cost power periods but get enough heat in to last a whole day.
I suppose I should just point out that altering the pipework might well invalidate the Mitsubishi guarantee, if that is important to you. It is probably worth talking to them anyway whatever you do as they do seem to be quite customer friendly.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Thanks for the reply I haven't yet altered the pipework as decided the coldest part of the year is not the best time if anything was to go wrong,
I have to agree with you about the low flow temperatures not working out for efficient running mine suffers terribly and is cycled far to much at anything from about +2c you can see the flow and return temperatures raising as the UFH can not give away any more heat and the heat pump is as low as it can go.
I think moving off weather compensation and having longer off times will work out more cost effective the issue I have at the moment is most of the pumps are not controlled via the FTC removing the pumps and turning the 3 remaining stats for temperature limiters leaving the main FTC as the one main stat goes hand it hand. Trying to rewire the pumps to do that will unfortunately be quite extensive.
In regards to the warranty this is not something I am really bothered about keeping I'm more keen on just having the simplest most efficient design
Time for an update
I had some time the last few days and with the warmer weather decided its now or never.
I'm no plumber but for a first go I am fairly happy, 4 pumps and the low loss header have now been removed.
I have had the system running for a few hours and am please to report monitoring the manifold l/min flow gauges before and after the mods there has been no loss in flow 😀
I did then have to shut the system down as I have a leak that I will have to fix on Friday
moving the dip switches to set up the new one zone I discovered several more errors like the PWM for the pump just being unplugged
going forward I will look at balancing the system (upstairs return is much hotter) and changing my running style to auto adaption.
I've added some pictures
Nice work - my system is almost identical to yours, I look forward to seeing if you get any efficiency benefits.
@rich congratulations. For doing this, and also on having the confidence in yourself to do this in winter. albeit you did check the forecast 😉
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@rich that is admirable. We’ll done. Looking forward to seeing how the system performs once you’ve balanced the rads.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
morning all,
The system has now been running 24/7 since Friday in weather compensation mode and the house is sat at 21c downstairs 20c upstairs.
so far we seem to have big electric savings I would put most of this down to the removal of all the extra pumps and control rather than heat pump as this still needs better control to get the most out of it.
I have slowed the upstairs flows to match the Delta T of downstairs as you can see the temperatures have become a lot better compared to the original. I am going to aliexpress some more cheap thermometer so I can better balance the system.
I briefly tried Auto adaption but this raised the flow temperature a lot, s this due to my heat pump constantly running around its lowest frequency (possibly oversized) I have used 540 code to see that I am getting a flow rate of 15 this seems ok but possibly a bit low for my heat pump?
today with it 5C outside I am still getting cycling so I am considering trying to schedule stops letting the slab cool slightly before adding more energy in what do you think?
please seen the before and after pictures of temps and flows
Looks good so far. The cycling may be the low flow temps rather than the energy (although they are of course related). Ecodans seem to struggle to maintain LWTs in the low 30s. When I'm running on WC I raise the LWT a bit more than is necessary and let the external stats limit the room temp, which does stop the ASHP periodically.
Thanks yeah I am using the FTC controller as the stat so I am just trailing Advanced Auto Adaption however I have noticed this raises the LWT significantly
Posted by: @richThanks yeah I am using the FTC controller as the stat so I am just trailing Advanced Auto Adaption however I have noticed this raises the LWT significantly
I think auto adaption is best suited to fast response emitters, like rads or fan coils. It is essentially load compensation.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
-
Mitsubishi Ecodan 11kw Defrosting Issue.
1 week ago
-
Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
1 month ago
-
Ecodan consuming 100kwh per day in new build!!!
2 months ago
-
Help with understanding my Mitsubishi Ecodan air source heat pump
5 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
5 months ago
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 35 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Powerwall 3 or Myenergi or something else?
Many of those tariffs are simple time of use tariffs, w...
By Temperature_Gradient , 32 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
Yes thats the whole point of the flexis as regards tran...
By JamesPa , 45 minutes ago
-
So far as I can tell designing for DT5, which is 'the n...
By JamesPa , 1 hour ago
-
Mitsu PAR-WT60R Wireless Controller - options
I hope I have satisfactorily installed the above wirele...
By DavidAlgarve , 3 hours ago
-
WC curve best discovered by experiment anyway as any lo...
By JamesPa , 8 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 1 day ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 1 day ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 1 day ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 1 day ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 1 day ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 2 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 2 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 2 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 3 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago