Ecodan help with efficiency setup and design - removing manifold mixers, LLH and pumps
thank you that's very good to hear, I will hopefully start the mods at the end of the week all going well.
alongside I plan to rewire so the main FTC display will be the one thermostat its downstairs in the centre of the house and the bedrooms will just act as temperature limiters
@rich I agree with your assessment that your pump is oversized, I have the same unit in a similarly-sized house with a design temp of 50° at -2.5 and I have come to the same conclusion. MCS heat loss assessments are notoriously pessimistic compared to how people find their houses perform, and EPC values are an over-generalised, rushed, stab in the dark. Unfortunately these are the figures that your plumbers supplied to Mitsubishi to get the OK for the system they put in. The SCOP value will assume far more heat is being supplied and probably has no idea of how much baseload all those pumps are drawing.
I slightly disagree with Derek’s statement that running at 33 at 0C is not a matter for concern in that it does show that you don’t need a large heat input at a low OAT but need even less for the vast majority of the time. I certainly find that my 8.5kW unit only runs continuously at 3°C or below, above that it cycles as it can’t modulate down far enough, and it cycled more frequently under WC than it does with AA. Rather than have the lowest flow temp but have pumps running circulating the heat 24 hrs a day, perhaps shorter defined on/off sessions charging the slabs at a higher temperature would work better for you. There are those who only run their HP during low-cost power periods but get enough heat in to last a whole day.
I suppose I should just point out that altering the pipework might well invalidate the Mitsubishi guarantee, if that is important to you. It is probably worth talking to them anyway whatever you do as they do seem to be quite customer friendly.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Thanks for the reply I haven't yet altered the pipework as decided the coldest part of the year is not the best time if anything was to go wrong,
I have to agree with you about the low flow temperatures not working out for efficient running mine suffers terribly and is cycled far to much at anything from about +2c you can see the flow and return temperatures raising as the UFH can not give away any more heat and the heat pump is as low as it can go.
I think moving off weather compensation and having longer off times will work out more cost effective the issue I have at the moment is most of the pumps are not controlled via the FTC removing the pumps and turning the 3 remaining stats for temperature limiters leaving the main FTC as the one main stat goes hand it hand. Trying to rewire the pumps to do that will unfortunately be quite extensive.
In regards to the warranty this is not something I am really bothered about keeping I'm more keen on just having the simplest most efficient design
Time for an update
I had some time the last few days and with the warmer weather decided its now or never.
I'm no plumber but for a first go I am fairly happy, 4 pumps and the low loss header have now been removed.
I have had the system running for a few hours and am please to report monitoring the manifold l/min flow gauges before and after the mods there has been no loss in flow 😀
I did then have to shut the system down as I have a leak that I will have to fix on Friday
moving the dip switches to set up the new one zone I discovered several more errors like the PWM for the pump just being unplugged
going forward I will look at balancing the system (upstairs return is much hotter) and changing my running style to auto adaption.
I've added some pictures
Nice work - my system is almost identical to yours, I look forward to seeing if you get any efficiency benefits.
@rich congratulations. For doing this, and also on having the confidence in yourself to do this in winter. albeit you did check the forecast 😉
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@rich that is admirable. We’ll done. Looking forward to seeing how the system performs once you’ve balanced the rads.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
morning all,
The system has now been running 24/7 since Friday in weather compensation mode and the house is sat at 21c downstairs 20c upstairs.
so far we seem to have big electric savings I would put most of this down to the removal of all the extra pumps and control rather than heat pump as this still needs better control to get the most out of it.
I have slowed the upstairs flows to match the Delta T of downstairs as you can see the temperatures have become a lot better compared to the original. I am going to aliexpress some more cheap thermometer so I can better balance the system.
I briefly tried Auto adaption but this raised the flow temperature a lot, s this due to my heat pump constantly running around its lowest frequency (possibly oversized) I have used 540 code to see that I am getting a flow rate of 15 this seems ok but possibly a bit low for my heat pump?
today with it 5C outside I am still getting cycling so I am considering trying to schedule stops letting the slab cool slightly before adding more energy in what do you think?
please seen the before and after pictures of temps and flows
Looks good so far. The cycling may be the low flow temps rather than the energy (although they are of course related). Ecodans seem to struggle to maintain LWTs in the low 30s. When I'm running on WC I raise the LWT a bit more than is necessary and let the external stats limit the room temp, which does stop the ASHP periodically.
Thanks yeah I am using the FTC controller as the stat so I am just trailing Advanced Auto Adaption however I have noticed this raises the LWT significantly
Posted by: @richThanks yeah I am using the FTC controller as the stat so I am just trailing Advanced Auto Adaption however I have noticed this raises the LWT significantly
I think auto adaption is best suited to fast response emitters, like rads or fan coils. It is essentially load compensation.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
3 hours ago
-
Ecodan 11.2kw Wireless thermostat drop outs
1 week ago
-
Ecodan consuming 100kwh per day in new build!!!
1 week ago
-
Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
2 weeks ago
-
Transforming a Derbyshire Property into an Energy-Efficient Haven
1 month ago
- 22 Forums
- 2,032 Topics
- 44.3 K Posts
- 25 Online
- 3,237 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 2 hours ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
Welcome to the forums. It’s clear that you’ve taken t...
By Mars , 3 hours ago
-
RE: help sizing rads based on room by room heat loss
By JamesPa , 4 hours ago
-
Hi Thanks for the reply, the walls are being constru...
By Fingers , 5 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 6 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 10 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 10 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 10 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 10 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
From the Full SAP Report: Space heating requirements:...
By trebor12345 , 10 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 14 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 17 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 17 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 20 hours ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 1 day ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 2 days ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 2 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 3 days ago