Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan flow rate tweak
Dear all,
I currently have the setup below.
- Zubadan PUHZ-SHW140 YHA (-BS) outdoor
- Ecodan ERST20C-VM2DR1.UK indoor
My dT is 10 around freezing temperatures, and I want to lower that by increasing the flow rate.
I adjusted the pump speed to 5 (maximum), but it doesn't give me a lot of flow. My outdoor unit supports a flow between 18 and 37 liters per minute, according to the specs. The max flow of my indoor unit is 27 liter per minute, but I only reach 21 liters per minute (probably piping, height resistance, etc). There is no button to control pump speed on the pump itself. The water pump is a Grundfos UMP3K 15-75-130.
I see that there are other indoor units (E*PT 20X series for example) that have the exact same water pump, but according to the specs of those units they have a max flow of 35 liters per minute. Besides, when I look up the specs of the water pump on the website of Grundfos, the max flow of my pump is much higher than the 27 liters (or even the 35) per minute.
I think the pump speed is restricted by the indoor unit, even when it is on speed 5. Unplugging the CNPWM doesn’t set the water pump on max performance either.
Does anyone have ideas how to increase the flow by speeding up the pump (which should be possible according to the specs of the water pump)?
1. Are all your radiator valves (both any thermostatic valves and the lockshield valves) fully open?
2. What diameter is your pipework to the radiators?
3. What size house?
Thanks for your reply.
Yes all radiators and floor heating is fully open. Pipes are 28mm or bigger. It is a 15kW heatpump used for both a big farmhouse and an apartment.
I think the 21 liter (out of the max 27) corresponds with the height resistance etc. I don’t think I can improve much on the piping and radiator sitution itself.
Therefore I am looking for alternative solutions to increase the flow.
Thanks for your reply.
Where did you find that table? The information in my installation manual is totally different (different flow rates, doesn’t say dT of 8 etc).
It mentions an additional pump. But what do they mean with that? Putting two pumps in series doesn’t result in extra flow, only in extra kPa.
@jingle86 Thats in the Ecodan ATW Databook Volume 6.0 https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_ATW_Databook_Vol.6_.0_.pdf#page-1.
No idea what they mean that's why I suggested calling the technical help line they are usually very helpful and its free.
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 403 Online
- 7,028 Members
Join Us!
Latest Posts
-
RE: Estimating true heat loss from twelve months of consumption data
@ian33a — a measured heat loss always trumps a calculat...
By cathodeRay , 4 minutes ago
-
RE: Setback savings - fact or fiction?
@cathoderay Thanks for your detailed response.Just two ...
By PeterWurmsdobler , 12 minutes ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
The hot water heating looks normal. The heat transfer ...
By GrahamF , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
Good questions @temperature_gradient. My understanding ...
By springswood , 4 hours ago
-
RE: Anyone concerned about GivEnergy?
@sunnyskies I agree with Downfield trying to ask the GE...
By Judith , 13 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 15 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 20 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 22 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 1 day ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 1 day ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 1 day ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 2 days ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 2 days ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 2 days ago