Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan flow rate tweak
Dear all,
I currently have the setup below.
- Zubadan PUHZ-SHW140 YHA (-BS) outdoor
- Ecodan ERST20C-VM2DR1.UK indoor
My dT is 10 around freezing temperatures, and I want to lower that by increasing the flow rate.
I adjusted the pump speed to 5 (maximum), but it doesn't give me a lot of flow. My outdoor unit supports a flow between 18 and 37 liters per minute, according to the specs. The max flow of my indoor unit is 27 liter per minute, but I only reach 21 liters per minute (probably piping, height resistance, etc). There is no button to control pump speed on the pump itself. The water pump is a Grundfos UMP3K 15-75-130.
I see that there are other indoor units (E*PT 20X series for example) that have the exact same water pump, but according to the specs of those units they have a max flow of 35 liters per minute. Besides, when I look up the specs of the water pump on the website of Grundfos, the max flow of my pump is much higher than the 27 liters (or even the 35) per minute.
I think the pump speed is restricted by the indoor unit, even when it is on speed 5. Unplugging the CNPWM doesn’t set the water pump on max performance either.
Does anyone have ideas how to increase the flow by speeding up the pump (which should be possible according to the specs of the water pump)?
1. Are all your radiator valves (both any thermostatic valves and the lockshield valves) fully open?
2. What diameter is your pipework to the radiators?
3. What size house?
Thanks for your reply.
Yes all radiators and floor heating is fully open. Pipes are 28mm or bigger. It is a 15kW heatpump used for both a big farmhouse and an apartment.
I think the 21 liter (out of the max 27) corresponds with the height resistance etc. I don’t think I can improve much on the piping and radiator sitution itself.
Therefore I am looking for alternative solutions to increase the flow.
Thanks for your reply.
Where did you find that table? The information in my installation manual is totally different (different flow rates, doesn’t say dT of 8 etc).
It mentions an additional pump. But what do they mean with that? Putting two pumps in series doesn’t result in extra flow, only in extra kPa.
@jingle86 Thats in the Ecodan ATW Databook Volume 6.0 https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_ATW_Databook_Vol.6_.0_.pdf#page-1.
No idea what they mean that's why I suggested calling the technical help line they are usually very helpful and its free.
- 27 Forums
- 2,792 Topics
- 66 K Posts
- 3,128 Online
- 7,197 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
I think Heat Geek have done an amazing job on their bra...
By Tomtheheatingengineer , 6 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
I have just had 3 heat loss surveys, one by heat geek o...
By David , 7 hours ago
-
RE: Heat Geek Zero Disrupt: Are We Sleepwalking Into Another Race to the Bottom?
I think that's the key question. After all inverter uni...
By Prunus , 8 hours ago
-
RE: battery storage without solar
As of October 1st they need specific qualifications to ...
By EtchedPixels , 9 hours ago
-
RE: How should the Boiler Upgrade Scheme be reformed?
A unit which uses water to transfer the heat/chill from...
By Temperature_Gradient , 10 hours ago
-
RE: Renewables & Heat Pumps in the News
With regards to the BUS grant raid, I gave it more thou...
By ASHP-BOBBA , 10 hours ago
-
RE: Why are ASHP installs so expensive?
The whole system seems to work on the basis of...
By ian33a , 10 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
Good plan. If you can get half hourly meter readings a...
By JamesPa , 15 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@editor Most certainly. The heat pump was an ideal s...
By Abernyte , 15 hours ago
-
Although regulations may well vary from country to coun...
By Majordennisbloodnok , 16 hours ago
-
RE: Does anyone have experience of a smart water meter?
Yep I caught our slow leak from a £100 bill rise 8)
By EtchedPixels , 16 hours ago
-
RE: Do You Need a Buffer Tank or Low Loss Header for Underfloor Heating in a Large Property?
@jamespa in some cases, failing the Turing test might b...
By GrahamF , 19 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@energystoragetech The heat capacity of some...
By JamesPa , 21 hours ago
-
RE: tepeo ZEB UK Support & Info Thread
Sorry you are correct, I was remembering figures from t...
By JamesPa , 1 day ago
Members Online
No online members at the moment