SUNandAIR
(@sunandair)
Noble Member Member
Joined: 3 years ago
Posts: 500
 

Posted by: @jaket

Posted by: @sunandair

A loss

Posted by: @jaket

How do I check the emitter value & that the flushing value is fully closed (what does this look like / where is it positioned?)

I had wondered if you have a list of your radiator sizes and how large your underfloor heating area is since a small emitter capacity can cause cycling. The flushing valve refers to your schematic diagram.... I noticed on the drawing there was a flushing bypass valve which isn’t always fitted. And mentioned it as an aside issue. Just to check that the valve is fully closed since this could cause hot water to bypass the heating system. 

Having said all that, your latest hourly graph looks better for all the changes you have made so things appear to have improved. 

-- Attachment is not available --

Unfortunately I think the issue has not been resolved. See below hourly temps from 13h00.

I’m going to run it for a few days in the current setting to see what the overall consumption / COP figures are like - if these are still terrible I may try out auto adaptive. 

-- Attachment is not available --

  

 

Hi @jake. I’ve started getting a bit of cycling since we have had 12c OAT. we get about 2 or 3 cycles an hour. Auto adapt does help a little by reducing the cycle size  but usually adds a few degrees to the flow temp to reduce the cycling but then stops and pauses to reduce the output.

D8779C7E 5D14 4C7D ACC4 86E0453847FA

Regarding your charts... I find it easier to read the charts when I screenshot my phone to landscape. It produces a longer time line for the hourly graph. Also by adding the tank set temperature line and one of the 25c lines I get a Better proportioned graph with 5c horizontal lines. I think this helps in reading the deltaT of the Flow and Return. Here are 2 screen shots of the same chart. Does the different setup help to see the performance of the output when it’s viewed in landscape? I hope you can see how the top and bottom lines help to change the proportions of the vertical temperature scale.

B1468692 6A8E 46C0 AFB6 82538A447096

Here is your chart from yesterday

931F9D78 1A57 4CBC AB0C 2A1A5B70CD4B

This second one below, I’ve tried to copy your scale and orientation- but it’s  the same chart as mine above in landscape format.

6717C897 3352 4EED BB5F C126CC6CF2EC

 

 


   
ReplyQuote
(@harriup)
Reputable Member Member
Joined: 4 years ago
Posts: 108
 

@jaket 

I think the flat bottom to the return temp shows how the slab temperature is preventing anymore heat being dropped from the circulation in to the UFH - so without being able to deliver heat at the rate it is being generated the flow temp rises until it reaches the set point, hence cycles. So I would read from this that the radiator circuit was not active, as otherwise the return temp would vary more.

In an ideal system the compensation curve would match the heat loss of the house at the different OATs – but if zoning is removing chunks of the house-side heat load then that equation becomes unbalanced. If you have two stats high so they are always calling, then the call from the third stat would effectively switch the entire house demand on and off. This should give you more balance, which should be more efficient.

Having UFH and radiators makes it tricky as the speed of heat transfer into the house is different, auto adapt can be too eager to put more heat in if it doesn’t register a change of temperature within a certain time, which is more likely when the heat transfer to the room is moderated and extended by the slab. But if you try auto adapt then it will refer to the temperature of the room the FTC controller is in – which looks like the second floor from the pic (I presuming you don’t have a Mitsubushi remote stat to set as the target location). When the system has the knowledge of current and desired temps it can use those to create longer runs with appropriate pauses to control the total heat delivery.

 

Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV


   
ReplyQuote
(@jaket)
Eminent Member Member
Joined: 2 years ago
Posts: 19
Topic starter  

@sunandair 

Ah okay so you also get some cycling when the OAT low double digits. What is your COP? 

Interestingly I spoke to the installer briefly today, who said it is normal for the unit to cycle about three times an hour. We didn't have the chance to fully discuss my concerns (he was on site looking at another property) but I will try get him out to take a full look at my set up & stats. 


   
ReplyQuote



SUNandAIR
(@sunandair)
Noble Member Member
Joined: 3 years ago
Posts: 500
 

@jaket we have decided a bit of cycling (but not too much) when it’s 10 or 12c is better at achieving a high CoP and minimise KWh consumption.

The question we faced is - what is acceptable cycling? We have decided 2 cycles per hour is stable enough and at 10 or 12c that gives us a CoP of about 4.0 sometimes 3.8. At that kind of cycling we are able to run the system at about 32c with 2 cycles per hour and 37c flow temperature without cycling. However we have about 21kw output capacity from our radiators and its a 8.5 Ecodan. 


   
👍
1
ReplyQuote
(@jaket)
Eminent Member Member
Joined: 2 years ago
Posts: 19
Topic starter  

@sunandair your logic makes sense.

My concern is that my COP is 2.5 at best. So I’m trying to find the best set up to maximise the COP, and then understand how to minimise the kWh demand (while being at a comfortable temp inside). 


   
ReplyQuote
 Rich
(@rich)
Trusted Member Member
Joined: 3 years ago
Posts: 18
 

Hi @jaket  

we have similar systems 

100% eclectic house, Ecodan 8.5kW - PUZ-WM85VAA, 210l pre plumbed cylinder, full house UFH total floor about 120spm, part is 1920s solid wall however its been fully internally insulated, part is 1950s foam cavity insulated and part is newbuild, with new double and triple glazing and MVHR. 

I have recently modified to removing zoning and unnecessary complexity in my system and like you are now looking more at optimising running conditions. 

do you have a heat and electric meter or are you taking reading to calculate COP from the unit / app ? this is the way I have to and find the data as only a guide 

this is the cycling I am getting today at 11-12 with OAT of 6c as you can see pretty bad but my floors just cant give up the heat pumps minimum output to my understanding

my next steps are to possibly try auto adaption or schedule in shutdowns 3h on 1h off 

how are you getting on it seems you are in a similar position?


   
ReplyQuote
 Rich
(@rich)
Trusted Member Member
Joined: 3 years ago
Posts: 18
 
cycling

for some reason my screenshot wasn't included 

this is the cycling OAT 6c at 11-12 today weather comp trying to keep to 31c


   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 4 years ago
Posts: 4427
 

Posted by: @rich
cycling

for some reason my screenshot wasn't included 

this is the cycling OAT 6c at 11-12 today weather comp trying to keep to 31c

What are your WC settings?

 


   
ReplyQuote
 Rich
(@rich)
Trusted Member Member
Joined: 3 years ago
Posts: 18
 

My settings are 37c @ -5c to 26 @ 15c I would like this lower as the house is 21c feeling a bit to warm sometimes 

however I am already getting a lot of cycling.


   
ReplyQuote



(@derek-m)
Illustrious Member Member
Joined: 4 years ago
Posts: 4427
 

Posted by: @rich

My settings are 37c @ -5c to 26 @ 15c I would like this lower as the house is 21c feeling a bit to warm sometimes 

however I am already getting a lot of cycling.

Cycling isn't necessarily a bad thing, since it may mean that you are using less electrical energy to keep your home warm.

What is the heat loss calculation for your home?

 


   
ReplyQuote
 Gary
(@gary)
Prominent Member Member
Joined: 2 years ago
Posts: 350
 

@rich I have an 8.5kw ecodan to keep cycling to 1 per hour at any temp below 10C I need to run at 32C, anything less leads to a lot of cycling.

That is with upstairs rads on and UFH downstairs all open, even then the house will heat up and thermostats will cut off the heat pump after a few hours.

You will have to run it more on and off at a higher flow temp if you want to reduce/eliminate the cycling.

 

 

 


   
👍
1
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 4 years ago
Posts: 4427
 

Posted by: @gary

@rich I have an 8.5kw ecodan to keep cycling to 1 per hour at any temp below 10C I need to run at 32C, anything less leads to a lot of cycling.

That is with upstairs rads on and UFH downstairs all open, even then the house will heat up and thermostats will cut off the heat pump after a few hours.

You will have to run it more on and off at a higher flow temp if you want to reduce/eliminate the cycling.

 

 

 

What range of indoor temperatures do you get when operating your system in that manner?

 


   
ReplyQuote