Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Creating a second zone on Mitsubishi Ecodan ASHP
Gary -in the installation manual I'm looking at, on p26, 5.3. Functions Settings, under SW2-6. (mixing tank) it states that when SW2-6 is off 2 Zone temp control is not available! And under SW 4-1 multiple units (which I don't have) it states that when SW4-1 is off 2 zone temp control is not available. I'm getting very confused!
Derek - thanks for that. Zone 1 was set to Room RC1 (I assume that's because I have the wireless thermostat ). I've changed it to main RC to see if it makes any difference but I can't leave Zone 2 unselected. It has to be TH1, MainRC or Time/Zone. I've tried all of them.
@bryanb There are known to be mistakes in the manual, so don't treat it as gospel, afaik SW2-6 is if you have a mixing valve to have different temperatures in the 2 zones so hotter rads and cooler UFH, if you dont have that it should be set to off. SW4-1 is definitely if you have more than one outdoor unit this is nothing to do with 2 zone control so again I think is a mistake in the manual and both SW4-1 and SW4-2 should be set to off.
SW1-8 should be set to ON if you have a wireless controller, presumably that is the case and by wireless controller I mean this.
If the above controller is on zone 1 that should be set to RC1 and if zone 2 is using a 3rd party thermostat should be set to main RC.
This is the main RC.
I'm not sure any of these changes will impact the error you are seeing but its worth a shot.
Thanks for your time with this Gary. I have a wireless controller running Zone 1. Sounds like the manual is more of a hindrance than a help! Your comment re SW4 1& 2 make sense.
I think though if I didn’t have SW2-6 on it gave me an LL error which was to do with incorrect DIP switches. I’ll check all that again when I clear out the airing cupboard to get at the control box.
Had another go at this, the morning. With SW2-7 ON it gives me a flashing LL error at the top of the main controller, but it still appears to run normally. However it does not seem to set up a Zone 2. The bottom left button on the controller is still marked "I" and I cannot set up Zone 2 room sensors. If I turn on SW2-6 I don't get the LL error and can set up Zone 2 settings - left button on controller marked as "Z1 or Z2". But then after several minutes the L5 error comes up and everything shuts down.
I guess if I turn on SW2-6, it's looking for a mixing tank(which I don't have) but presumably would have a thermistor which it can't find, hence the L5 error. I have what I think is called a low loss header, but that's hardly a mixing tank, with no temp sensors.
Not sure where to go from here!
- 27 Forums
- 2,778 Topics
- 65.5 K Posts
- 2,305 Online
- 7,185 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Estimating true heat loss from twelve months of consumption data
@ian33a What size unit did you get in the end? My guess...
By scrchngwsl , 50 minutes ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
Whenever I see the word modelled I am reminded of the t...
By cathodeRay , 60 minutes ago
-
RE: Say hello and introduce yourself
@olivierm welcome to the forums and finding the right i...
By Mars , 2 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
I’ve had two calibration cycles in the last three month...
By Davesoa , 22 hours ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@editor That's a pity, but thank you for checking. I'l...
By ltron2 , 1 day ago
-
My fifth heat pump book, Heat Pumps Explained, is out n...
By Mars , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
Just furkled Into the parameter menu. Found the master ...
By AgentGeorge , 2 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
It's interesting that Norway with a much colder climate...
By Rob of York , 2 days ago
-
RE: Review your electricity provider
Happy to add Scottish Power and the review 'dont touch ...
By JamesPa , 2 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
Yes, and I would suggest likely to get worse with more ...
By Batpred , 4 days ago
-
RE: Electricity price predictions
This topic seems more suitable for this thread... I a...
By Batpred , 4 days ago
-
RE: Why are ASHP installs so expensive?
It is clearly difficult to say, there must be cases whe...
By Batpred , 4 days ago
-
RE: Panasonic Free Multi Z and Etherea Internal units.
@dgclimatecontrol Thank you for that information and re...
By Toodles , 4 days ago
-
RE: My Kronoterm Adapt 0312 ASHP is finally installed!
@editor It was serendipitous really. Both my wife and I...
By tomasmcguinness , 4 days ago