Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Clarification needed for Ecodan ASHP settings
It may be useful if I explain a few things about how heat pump systems function and then you can decide how best to operate yours.
The heat pump gathers energy from both the electricity supply and the outside air. The warmer the outside air, the more energy it can provide, and hence less energy is required from the electricity supply.
When the outside air temperature is lower than the inside air temperature your home loses energy, as shown by the heat loss calculations, the colder the outside air temperature then the greater the heat loss.
To maintain a constant indoor temperature the heat pump needs to produce sufficient energy to match the heat loss, so as the outside air temperature gets colder the heat pump needs to work harder to produce more heat energy. The purpose of weather compensation is to try to match the heat energy produced by the heat pump to the heat loss of your home.
To keep your home at the desired temperature, the heat energy produced by the heat pump needs to be transferred to the heat emitters, your radiators and UFH. This is normally done by the water pump located inside your heat pump, but can also involved a further external water pump. Do you have an external water pump?
The amount of heat energy transferred from your heat emitters depends upon their size, and type, along with the temperature of the water being fed from the heat pump and the flow rate of that water. This is why most of the TRV's should be fully open to ensure adequate water flow. Since the size and type of heat emitters is fixed, the amount of heat energy is controlled by varying the water temperature and the water flow rate.
The setting of the weather compensation curve is used to vary the water temperature, and the heat pump controller varies the water flow rate by speeding up or slowing down the water pump.
If you require an upstairs temperature of 19C and a downstairs temperature of 15C, then I would expect your system to operate in the following manner. With your thermostat set at 21C and the TRV's fully open and your UFH set for 15C.
If the outside air temperature is 0C, then the heat pump should be warming the water to approximately 40C, as calculated by the weather compensation. If the downstairs temperature is below 15C then some of this warm water will be fed to the UFH pipework, until the temperature increases to 15C. If the upstairs temperature is below 21C then some of this warm water will be fed to the radiators. If the amount of heat energy coming from the radiators is greater than the heat loss, then the upstairs temperature will start to increase, but as the upstairs temperature rises then so will the heat loss. At some point the heat loss and energy supplied will balance and the upstairs temperature will remain constant.
If the upstairs temperature is above the desired 19C, the weather compensation setting is too high, but if the upstairs temperature is below 19C, then the weather compensation setting is too low.
What I would suggest in your situation is rather than lowering the weather compensation from 40C to 35C at an outside temperature of 0C, you should change the setting to 40C at an outside temperature of -5C. This will have the same effect of lowering the weather compensation curve, but will allow your system response to be maintained should the outside temperature fall to -5C.
By continuing to monitor the system, as you are doing, you should be able to fine tune your weather compensation curve until it closely matches the heat loss of your home. I would not suggest making any large changes and always allow time for the system to stabilise before making any further adjustments.
Thanks Derek - thats one of the best explanations Ive read!!
Funnily enough, changing the slope of the curve (as you suggested) was going to be my next thing to try.
Ill post back on here in a fortnight and give an update.
Cheers!
Hi, just thought Id give an update.
Its been quite a good time to test recently (not that Ive been testing particularly diligently or scientifically!) - we've had a temperatures ranging from -6c to 12c.
I currently have the comp curve set at -40c @ -5c outside, going down to 25c @ 15c outside. So far I feel this is about right for my rooms.
I open the TRVs fully in whatever room Im occupying. (Im either in my office for the most part, or in my bedroom). The stat is sat either in my office or bedroom. Its set to 20c, but it hardly ever gets to 20c so the heating is on all the time.
The Ecodan doesnt let me go below 25c, which got me thinking whether that was a safety feature. Is there any negatives to having the comp curve set as low as I have it? (cycling etc...)
I still cant get a COP better than ~2.1 (I never have, even when it was first installed 4 years ago!), so I dont know if Im reading the Ecodan incorrectly. I dont think I am becuase its a basic case of reading the Consumption and Delivered figure and dividing one by the other.
Cheers
Posted by: @tuftyHi, just thought Id give an update.
Its been quite a good time to test recently (not that Ive been testing particularly diligently or scientifically!) - we've had a temperatures ranging from -6c to 12c.
I currently have the comp curve set at -40c @ -5c outside, going down to 25c @ 15c outside. So far I feel this is about right for my rooms.
I open the TRVs fully in whatever room Im occupying. (Im either in my office for the most part, or in my bedroom). The stat is sat either in my office or bedroom. Its set to 20c, but it hardly ever gets to 20c so the heating is on all the time.
The Ecodan doesnt let me go below 25c, which got me thinking whether that was a safety feature. Is there any negatives to having the comp curve set as low as I have it? (cycling etc...)
I still cant get a COP better than ~2.1 (I never have, even when it was first installed 4 years ago!), so I don't know if Im reading the Ecodan incorrectly. I dont think I am becuase its a basic case of reading the Consumption and Delivered figure and dividing one by the other.
Cheers
Your curve looks fine if it works for you. You can change the flow temp settings; it's in Operation Settings - Heating Operation - Flow Temp Range. I think the minimum is 20.
Your COP still seems a bit low. Do you have a buffer, low loss header or similar? They can sometimes cause lower efficiency. Mine has never been that low and my flow temps are a bit higher than yours now.
How do I find out if I have a buffer, low loss header or similar? If I do have one, is it a case of turning it off?
Ive just taken a photo showing the Consumed/Delivered:
Consumed: 428kwh (22 HW; 405 Heating)
Delivered: 883kwh (64 HW; 818 Heating)
COP 2.06 overall (2.9 HW; 2.01 Heating)
Hot water has always had a COP of ~2.8, whereas Heating has never had a COP of more than ~2.2 .
Posted by: @kev-mYour curve looks fine if it works for you. You can change the flow temp settings; it's in Operation Settings - Heating Operation - Flow Temp Range. I think the minimum is 20.
Your COP still seems a bit low. Do you have a buffer, low loss header or similar? They can sometimes cause lower efficiency. Mine has never been that low and my flow temps are a bit higher than yours now.
Ive just dug out the gubbins the installers gave me and in the Material List they have "Low Loss Header for maximised efficiency, avoiding short cycling of ASHP". So I have got a Low Loss Header. Now I know this, is there something else I can do to try and get a better COP?
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 7,064 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
-
RE: Rate the quality of your heat pump design and installation
I had a Worcester Bosch compress 2000 fitted March 2026...
By Josejo , 5 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 8 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 20 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 22 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 22 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 1 day ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago