Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
buffer/volumizer cupboard space eater, do i need one?
Posted by: @sunandair@heacol I’ve also herd that a volumiser can help with short cycling.
I wondered if short cycling would be reduced if it was caused by mild outdoor ambient circa 10c and a corresponding low flow temperatures and possibly insufficient radiator capacity at low flow temperatures…. Can you use a volumiser as a replacement for increased radiator capacity to reduce cycling? Eg. Flow temps down to 30c and rad capacity sized for 50c at -3c might not be large enough… as an example.
or is this just a red herring?
As you say, short cycling can occur during milder ambient conditions where the flow temps are reduced and the radiators/emitters then cannot dissipate the heat that is being produced. This causes the return temperature to rise (as the heat cannot be effectively dissipated into the property) thus narrowing the dT between flow and return. When this happens, the heat pump can cycle off to allow the water to cool and maintain a more optimal dT (somewhere in the controller logic the heat pump decides when dT drop below a certain value, the heat pump should cycle off).
Having a volumiser is not going to change the above fundamentals, as unlike a radiator it cannot dissipate heat (it's well insulated so it is reasonable to assume near zero heat loss relative to a radiator or other emitter). Consider it as simply a well lagged fat pipe, so there is more volume of water in the system. It may take longer to reach the initial point of cycling as there is initially more water to heat, so at best it may extent the periods between cycling (so short cycling now becomes longer cycling). Extending this premise, if the system volume were infinitely large, the return temperature would never rise to the point where the dT narrows to cause cycling, so there is a point of diminishing returns and as long as the system volume is large enough, then short cycling shouldn't be an issue. I do not know what this point is, but I have heard recommendations of having a system volume that is 3-4 times the recommended minimum system volume.
Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero
Posted by: @old_scientistWhen this happens, the heat pump can cycle off to allow the water to cool and maintain a more optimal dT (somewhere in the controller logic the heat pump decides when dT drop below a certain value, the heat pump should cycle off).
Not sure this is precisely what happens or how the control loop works. What I observe on plots I have seen (including mine) is that the flow temperature rises above the set point (because the heat pump is putting in more heat than the radiators are emitting). Eventually the flow temperature exceeds the target + allowable hysteresis, at which point the heat pump will shut down. You could in fact restore deltaT by simply slowing down the water pump, but the flow temperature will still rise above the target value because the heat pump is putting in more heat than the radiators are emitting.
Posted by: @old_scientistHaving a volumiser is not going to change the above fundamentals, as unlike a radiator it cannot dissipate heat (it's well insulated so it is reasonable to assume near zero heat loss relative to a radiator or other emitter). Consider it as simply a well lagged fat pipe, so there is more volume of water in the system. It may take longer to reach the initial point of cycling as there is initially more water to heat, so at best it may extent the periods between cycling (so short cycling now becomes longer cycling)
Agreed, particularly with the sentence in brackets. A volumiser changes the period of the cycling but not the on/off ratio.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaNot sure this is precisely what happens or how the control loop works. What I observe on plots I have seen (including mine) is that the flow temperature rises above the set point (because the heat pump is putting in more heat than the radiators are emitting).
Here might be a case in point James.
Here are 2 hourly charts showing flow and return. These are supposed to be operating at fixed flow 34C and 35C respectively. They both have a little burst of temperature before closing down for around 4 minutes. I’ve always assumed this was a deliberate duty cycle function to bridge the shutdown temp drop… but it’s just a guess. There is no thermostat controlling, it’s just fixed flow. The room temp is close to 21 with an ambient of around4C last night and 9C for this afternoons chart
This 24 hour indoor/outdoor temp chart covers both hourly graphs above.
- 27 Forums
- 2,808 Topics
- 66.3 K Posts
- 3,562 Online
- 7,212 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 3 hours ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@susannasaunders That's a serious amount of solar PV ...
By Rob of York , 8 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
So far there is nothing on the value of the BUS grants ...
By Rob of York , 12 hours ago
-
Coming back on subject... A shortened version of the ...
By Transparent , 14 hours ago
-
RE: Say hello and introduce yourself
Perhaps it is time for an update on ‘our’ project. We h...
By Toodles , 16 hours ago
-
RE: Marvel Heating liquidation
The interesting thing about the IBG: when I called them...
By davidnolan22 , 1 day ago
-
RE: Free app: run the immersion / heat pump from Growatt battery & solar surplus – no Home Assistant
Please bear in mind, everyone, that in order to use thi...
By Majordennisbloodnok , 3 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
@burtis Thanks for posting this and Im so pleased you ...
By JamesPa , 3 days ago
-
RE: I need help with Ecodan ASHP
@f1p It turns out there have been a solar panel install...
By Andris , 3 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews your installer would be right to say that the...
By GrahamF , 3 days ago
-
RE: Tradespeople on Their Phones: What’s Acceptable When They’re Working in Your Home?
Actually, that's a very important point. I've only ev...
By Majordennisbloodnok , 4 days ago
-
RE: Aerotherm and weather compensation
These are likely inked. The basic explanation is tha...
By JamesPa , 4 days ago
-
RE: Electrical works for air to air heat pump
agree with above. I have not had extra costs added wh...
By Batpred , 4 days ago
-
Good to hear that you found a solution. Absolutely a...
By Batpred , 4 days ago
Members Online
No online members at the moment