Buffer tank required? Samsung 12kW heat pump
I'm having a Samsung 12kw monobloc heat pump installed today. The fitter gets part way through the install then tells me there isn't space for the buffer tank. He says he's checked with the office and my 7 rad system doesn't actually need one.
This doesn't sound right to me but without the technical knowledge I can't be sure. Does anyone on here know if this is true?
Posted by: @riponowlI'm having a Samsung 12kw monobloc heat pump installed today. The fitter gets part way through the install then tells me there isn't space for the buffer tank. He says he's checked with the office and my 7 rad system doesn't actually need one.
This doesn't sound right to me but without the technical knowledge I can't be sure. Does anyone on here know if this is true?
Hi,
Look through the manual for your particular model of ASHP to find the minimum system water capacity requirement. Look at the specification for each of your 7 radiators and find the water volume of each. Add up the total volume of the 7 radiators and add maybe 10% to 20% for the volume of the pipework.
If the water volume of the radiators and pipework are greater than that specified by the ASHP manufacturer then it should be acceptable to operate without a buffer tank provide you don't have TRV's installed except in the bedrooms.
If you are still in doubt then ask the installer to explain in detail how, a buffer tank was initially specified, but is now no longer required.
@derek-m Thank you for responding. All the rads are specified to have TRVs on them (the install isn't finished yet). In fact I'd like to update them to smart TRVs eventually so I can schedule them for different times of the day.
Posted by: @riponowl@derek-m Thank you for responding. All the rads are specified to have TRVs on them (the install isn't finished yet). In fact I'd like to update them to smart TRVs eventually so I can schedule them for different times of the day.
Hi,
Did you specify TRV's or your installer? Are you also having thermostats?
@riponowl, this may help: https://renewableheatinghub.co.uk/why-do-you-have-a-buffer-vessel-with-a-heat-pump
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@derek-m A single Hive controller is being installed. My existing rads just had manual turn valves which never turned. I had to chase up the supplier after they sent the quote to make sure they would all the new ones would have TRVs so that they would be easy to replace with smart TRVs if I wanted to do that at a later date.
The most telling factor is that the installers turned up with a buffer tank, cut out a section of the vinyl flooring on which to fit it only to decide later that there wasn't space. It was only when I queried if they were putting in a buffer that installer came clean on what had happened. It was clearly part of the spec.
I'm going to get an update from them shortly, I'll report back in a bit.
@editor Thank you, that is really interesting. I almost feel bad for giving the installer a hard time now (almost). It seems to be at odds with this though
https://www.kensaheatpumps.com/buff-up-your-knowledge-of-buffer-tanks/
Now I really am confused.
@riponowl, I have to be honest, the buffer tank is a point of contention. We have one, and the industry seems to be split. Some installers insist on having them, others say that they are there to bail out poorly designed and installed systems. From what I've read, and I'm not an expert, having a well-designed system with no buffer tank and no TRVs on rads leads to much better efficiencies.
We have a buffer tank like I've said, and we have TRVs, and we have a SCOP of 2.7-2.8 which is quite reasonable and which we're not dissatisfied by.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Well, the install went ahead without the buffer, there was absolutely no space near the tank so I will so how it goes. I will have a better idea about how it is performing in a week or so. I have more pressing problems with non performing rads to deal with first 🙁
Thanks again to all contributors.
Posted by: @riponowl@derek-m A single Hive controller is being installed. My existing rads just had manual turn valves which never turned. I had to chase up the supplier after they sent the quote to make sure they would all the new ones would have TRVs so that they would be easy to replace with smart TRVs if I wanted to do that at a later date.
The most telling factor is that the installers turned up with a buffer tank, cut out a section of the vinyl flooring on which to fit it only to decide later that there wasn't space. It was only when I queried if they were putting in a buffer that installer came clean on what had happened. It was clearly part of the spec.
I'm going to get an update from them shortly, I'll report back in a bit.
Hi,
TRV's and thermostats were developed for use with gas and oil boilers, whose water flow temperature was much higher than that required to heat the home. An ASHP can control the water flow temperature down to much lower levels, in fact the lower the temperature, the more efficient the system will operate.
Of course it is your choice if you wish to have TRV's and thermostats installed in preference to the control system specifically designed for the ASHP.
@derek-m Thanks!
I just wanted to be a little more energy efficient by having the upstairs rads turn down during the day and the downstairs rads turn down a little at night. It's no deal breaker though, right now I will be happy if it just works.
It's unlikely to save you much if any money but you might want the option of TRVs in the bedrooms for comfort (if you like a cooler room). That's what I've done but they are fully open most of the time.
-
Where has Watson gone?
3 weeks ago
-
First time wall mounting an ASHP
1 month ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 months ago
-
Rodents! A word of warning for heat pump owners
2 months ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
3 months ago
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 262 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
RE: LiFePO4 lithium battery fires and explosions
I too had spotted the Na-ion battery and matching inver...
By Transparent , 55 minutes ago
-
RE: Help with heat pump sizing
Unfortunately you will almost certainly need to go a la...
By JamesPa , 1 hour ago
-
@majordennisbloodnok thank you. A great explanation. Bu...
By Carpenterstation , 2 hours ago
-
RE: Poll for Time of Use, tariffs, technology
You are absolutely right. I think another common fac...
By JamesPa , 4 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Let' start with first thing first, HG is a startup, the...
By ksim , 4 hours ago
-
RE: Configuring third party dongle for Ecodan local control
@sheriff-fatman might be interested in this, f...
By F1p , 5 hours ago
-
RE: Commencing on an ASHP Installation Process
Fair play for giving this a go, and please do report ba...
By benson , 7 hours ago
-
RE: Different dT on each radiator?
I cant sorry. Its based on some calculations I did fro...
By JamesPa , 18 hours ago
-
RE: Setback savings - fact or fiction?
Maybe this: or maybe that the effect you are seein...
By JamesPa , 18 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@simonf thats interesting as I’ve noticed my flow and r...
By AdamK , 1 day ago
-
RE: MELcloud scheduling misbehaviour
No, it gets to set temperature easily even during perio...
By Abernyte , 1 day ago
-
RE: Free Ecoheat Heat Pump Install
Sorry hit 'add reply' too early, this forum layout will...
By Deltona , 1 day ago
-
And arguably even more important, sodium will be hopefu...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
I've been thinking of emailing Homely to ask for a few ...
By JohnnyB , 2 days ago
-
Max output of Heat pump (Daikin 4Kw EDLA04)
Hello, I am a bit puzzled that according to pcdb tes...
By GeorgeA , 2 days ago
-
In that case, @technogeek, I’d sign up for the free sol...
By Majordennisbloodnok , 2 days ago
-
RE: Has Anyone Else Noticed a Decline in Tradesmanship?
@cathoderay Hence my rider about ‘all else being equal’...
By Toodles , 2 days ago
-
RE: Heat Pump Performance Analysis Web App using Modbus Data
@redzer_irl — all my heat pump data is in csv files, me...
By cathodeRay , 2 days ago