Buffer tank required? Samsung 12kW heat pump
I'm having a Samsung 12kw monobloc heat pump installed today. The fitter gets part way through the install then tells me there isn't space for the buffer tank. He says he's checked with the office and my 7 rad system doesn't actually need one.
This doesn't sound right to me but without the technical knowledge I can't be sure. Does anyone on here know if this is true?
Posted by: @riponowlI'm having a Samsung 12kw monobloc heat pump installed today. The fitter gets part way through the install then tells me there isn't space for the buffer tank. He says he's checked with the office and my 7 rad system doesn't actually need one.
This doesn't sound right to me but without the technical knowledge I can't be sure. Does anyone on here know if this is true?
Hi,
Look through the manual for your particular model of ASHP to find the minimum system water capacity requirement. Look at the specification for each of your 7 radiators and find the water volume of each. Add up the total volume of the 7 radiators and add maybe 10% to 20% for the volume of the pipework.
If the water volume of the radiators and pipework are greater than that specified by the ASHP manufacturer then it should be acceptable to operate without a buffer tank provide you don't have TRV's installed except in the bedrooms.
If you are still in doubt then ask the installer to explain in detail how, a buffer tank was initially specified, but is now no longer required.
@derek-m Thank you for responding. All the rads are specified to have TRVs on them (the install isn't finished yet). In fact I'd like to update them to smart TRVs eventually so I can schedule them for different times of the day.
Posted by: @riponowl@derek-m Thank you for responding. All the rads are specified to have TRVs on them (the install isn't finished yet). In fact I'd like to update them to smart TRVs eventually so I can schedule them for different times of the day.
Hi,
Did you specify TRV's or your installer? Are you also having thermostats?
@riponowl, this may help:
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@derek-m A single Hive controller is being installed. My existing rads just had manual turn valves which never turned. I had to chase up the supplier after they sent the quote to make sure they would all the new ones would have TRVs so that they would be easy to replace with smart TRVs if I wanted to do that at a later date.
The most telling factor is that the installers turned up with a buffer tank, cut out a section of the vinyl flooring on which to fit it only to decide later that there wasn't space. It was only when I queried if they were putting in a buffer that installer came clean on what had happened. It was clearly part of the spec.
I'm going to get an update from them shortly, I'll report back in a bit.
@editor Thank you, that is really interesting. I almost feel bad for giving the installer a hard time now (almost). It seems to be at odds with this though
Now I really am confused.
@riponowl, I have to be honest, the buffer tank is a point of contention. We have one, and the industry seems to be split. Some installers insist on having them, others say that they are there to bail out poorly designed and installed systems. From what I've read, and I'm not an expert, having a well-designed system with no buffer tank and no TRVs on rads leads to much better efficiencies.
We have a buffer tank like I've said, and we have TRVs, and we have a SCOP of 2.7-2.8 which is quite reasonable and which we're not dissatisfied by.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Well, the install went ahead without the buffer, there was absolutely no space near the tank so I will so how it goes. I will have a better idea about how it is performing in a week or so. I have more pressing problems with non performing rads to deal with first 🙁
Thanks again to all contributors.
Posted by: @riponowl@derek-m A single Hive controller is being installed. My existing rads just had manual turn valves which never turned. I had to chase up the supplier after they sent the quote to make sure they would all the new ones would have TRVs so that they would be easy to replace with smart TRVs if I wanted to do that at a later date.
The most telling factor is that the installers turned up with a buffer tank, cut out a section of the vinyl flooring on which to fit it only to decide later that there wasn't space. It was only when I queried if they were putting in a buffer that installer came clean on what had happened. It was clearly part of the spec.
I'm going to get an update from them shortly, I'll report back in a bit.
Hi,
TRV's and thermostats were developed for use with gas and oil boilers, whose water flow temperature was much higher than that required to heat the home. An ASHP can control the water flow temperature down to much lower levels, in fact the lower the temperature, the more efficient the system will operate.
Of course it is your choice if you wish to have TRV's and thermostats installed in preference to the control system specifically designed for the ASHP.
@derek-m Thanks!
I just wanted to be a little more energy efficient by having the upstairs rads turn down during the day and the downstairs rads turn down a little at night. It's no deal breaker though, right now I will be happy if it just works.
It's unlikely to save you much if any money but you might want the option of TRVs in the bedrooms for comfort (if you like a cooler room). That's what I've done but they are fully open most of the time.
-
Surface mount or bury primaries for heat pump installation?
3 weeks ago
-
UFH and ASHPs
2 months ago
-
Installing your own ASHP - DIY
3 months ago
-
ASHP install contract and BUS grant money
5 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
5 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,112 Topics
- 46.4 K Posts
- 38 Online
- 3,408 Members
Latest Posts
-
RE: Buffers, hot water and cooling
@prunus, @jamespa is correct, but removing the buffer ...
By Brendon Uys , 2 hours ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 20 hours ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 1 day ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 1 day ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 1 day ago
-
RE: Wood burner with ASHP - direct air?
@sune is ideal to answer this, but I think he's on vaca...
By Mars , 2 days ago
-
RE: Say hello and introduce yourself
Hi @topher - you might be interested to see this very r...
By Transparent , 2 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
We've got a svenar heat pump controller en route and lo...
By benson , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 3 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 4 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 4 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 4 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 4 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 4 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 6 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 1 week ago