Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
Posted by: @abernyteIs there also a danger in the terminology that is being used ie low loss header, buffer and volumiser
Agreed
Posted by: @abernyteNot all LLH's act as buffers, correctly specified and installed they operate perfectly correctly as a hydraulic separator. It very much depends on where on the LLH the ports are positioned.
Surely an LLH suffers from mixing of flow and return to the same extent, probably more because its smaller, than a buffer does, and like a buffer needs to be set up properly to function without degrading efficiency (which seems to be where many installations go wrong).
Can you explain why 'hydraulic separation' is needed in a typical domestic central heating system. I totally understand why extra volume may be needed, but not hydraulic separation. if you are doing something complex with a back up boiler or a rather large system then maybe, but in a typical house what value does it add?
Posted by: @derek-mPosted by: @abernyteIs there also a danger in the terminology that is being used ie low loss header, buffer and volumiser. Not all LLH's act as buffers, correctly specified and installed they operate perfectly correctly as a hydraulic separator. It very much depends on where on the LLH the ports are positioned.
Are we in danger of vilifying an entire class of products?
As far as I am aware there would be no problem with a LLH or buffer tank, if the primary and secondary flowrates can be balanced to ensure that no mixing of the flow and return takes place. Obviously balancing the flowrates becomes problematic if the heat pump controller is able to vary the primary flowrate, without the necessary adjustment also being performed on the secondary, thereby unbalancing the system.
Having an additional water pump that may not be necessary is also a possible waste of electrical energy.
True, but it appears they are frequently not balanced.
My questions to @abernyte (or anyone else) is:
In a domestic installation of a 'normal' scale (say up to 6 bedrooms/300 sq m) with either radiators or UFH but not both
- what value does a LLH add?
- what value does a buffer add that a volumiser doesn't add?
The application of Occams razor is generally a good principle so until we identify the value add then there is no argument for their presence.
The default setup on a Mitisubishi Ecodan solar thermal ported pre plumbed cylinder has a LLH. My installer, who was one of the highly experienced "better" class of installer when queried regarding this said that the LLH in question has the flow injection plume above the return fitting outlet (not opposite as some seem to have) and as such would operate as a thermal separator to allow the primary and secondary pumps to operate efficiently at different variable speeds.
Since installation the system operates with a flow temp rarely above 35C and has been a resounding success as a heating system. Not a scientific recommendation I admit but I see no reason to doubt his explanation ...so far!
Posted by: @abernyteThe default setup on a Mitisubishi Ecodan solar thermal ported pre plumbed cylinder has a LLH. My installer, who was one of the highly experienced "better" class of installer when queried regarding this said that the LLH in question has the flow injection plume above the return fitting outlet (not opposite as some seem to have) and as such would operate as a thermal separator to allow the primary and secondary pumps to operate efficiently at different variable speeds.
Since installation the system operates with a flow temp rarely above 35C and has been a resounding success as a heating system. Not a scientific recommendation I admit but I see no reason to doubt his explanation ...so far!
Which simply begs the question - why do I want primary and secondary pumps in the first place (which incidentally must be balanced for the LLH to work without impeding system efficiency). For the avoidance of doubt I'm talking about a typical fairly simple domestic setup where a heat pump replaces a gas boiler (ie 95% plus of real world scenarios). Why would I have a second pump, a low loss header/buffer etc. None of this appears in your typical CH system. What value do they add.
You may not know I accept, but until someone tells us then the best assumption is no value at all and, since they clearly add trouble and cost, thats a good argument to leave them out.
@abernyte I suspect that arrangement might be similar to the one in our airing cupboard. The flow is the top left pipe and the return is the lower left. The top right is the flow to the secondary pump thence to radiators and the lower right is return from the radiators? Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
Posted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
Posted by: @jamespaPosted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
The only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems.
Posted by: @derek-mPosted by: @jamespaPosted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
The only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems.
Wow that's inventive but I'm sure you agree that it can be discarded as a legitimate reason.
Perhaps we ought to ask why should they be included rather than trying to argue that they should be omitted. No system designer worth their salt includes components without a reason.
Posted by: @jamespaPosted by: @derek-mPosted by: @jamespaPosted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
The only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems.
Wow that's inventive but I'm sure you agree that it can be discarded as a legitimate reason.
Perhaps we ought to ask why should they be included rather than trying to argue that they should be omitted. No system designer worth their salt includes components without a reason.
Which is why I have spent the past three years trying to convince forum members that they should have their poorly designed systems corrected to make them operate more efficiently.
Posted by: @derek-mThe only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems
I think you are both correct, its because systems aren't designed, they are plumbed in by people who don't understand system design but attend a manufacturer's installation course. So the additions of these components are their to mitigate any system design and it will function in any given scenario, not optimally but it will function.
Posted by: @garyPosted by: @derek-mThe only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems
I think you are both correct, its because systems aren't designed, they are plumbed in by people who don't understand system design but attend a manufacturer's installation course. So the additions of these components are their to mitigate any system design and it will function in any given scenario, not optimally but it will function.
I fear you are right. However the reason suggested (which is very plausible) is the equivalent of dressing a dirty wound instead of first cleaning it up because the patient complains about the sting of the antiseptic, except that if you did the latter you would likely get struck off.
-
Ecodan DHW Settings missing
2 months ago
-
Hacking a heat pump to increase heating range over 38C
2 months ago
-
Running my heat pump for half the cost of a gas boiler
3 months ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
4 months ago
-
Capacitors May Replace HFCs in future Heat Pump Systems
6 months ago
Currently viewing this topic 1 guest.
- 25 Forums
- 1,431 Topics
- 30 K Posts
- 28 Online
- 1,216 Members
Join Us!
Latest Posts
-
@transparent Hi thanks for your reply, you are correct ...
By Potatoman , 12 hours ago
-
RE: Bivalent oil boiler system to work alongside ground or water source heat pump
I can provide a lot of detail on LED lighting. But no...
By Transparent , 12 hours ago
-
RE: Octopus (the grid) is my battery
@toodles That's great! Only at 32.5kw but it was pret...
By Andris , 13 hours ago
-
RE: Making best use of Agile with a battery and ASHP
I try to ovoid doing that...
By Majordennisbloodnok , 13 hours ago
-
RE: Have Octopus Energy discovered a way to Narnia?
Thanks for the advice I asked for (and got) their room ...
By Davesoa , 16 hours ago
-
Your graph shows some interesting correlations. Simple ...
By SUNandAIR , 21 hours ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@kenbone no need for what kenbone regarding the 100watt...
By David999 , 3 days ago
-
RE: Insulation of flow and return Heat Pump piping
@mike-h Thanks Mike. Toodles.
By Toodles , 3 days ago
-
RE: Bivalent (or even trivalent!) system design options for a new GSHP installation
For your interest @algienon this is what happens when a...
By Transparent , 3 days ago
-
RE: Rising Damp – Production Recommendation
Yet another topic I'm not an expert in. Nonetheless, th...
By Majordennisbloodnok , 3 days ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor yes, the more I read the forum posts the more I...
By sjn , 3 days ago
-
RE: Observations on my Ecodan's estimates of energy consumed and delivered
As it is possible for the FTC to be powered from a sepa...
By HarriUp , 3 days ago
-
RE: ASHP Cut-off Temperatures: What's Your Setting and is a Your Heating Still On?
My system has been running 24/7 on weather compensation...
By HughF , 3 days ago
-
RE: Heat Pump Truth or Myth#2 - Cycling uses a lot of power and ruins your COP
I cannot state that I have noticed that our A2A heat pu...
By Derek M , 4 days ago
-
RE: Maximising Savings: Navigating My First Year with Octopus Energy and Heat Pump Running Costs
@toodles I can also happily report that the Agile tarif...
By Steve D , 4 days ago
-
@editor As we all know, RHH always strive to educate, e...
By Toodles , 4 days ago
-
@bontwoody I used the website link to contact them for ...
By Toodles , 4 days ago
-
RE: Samsung ASHP power cycling
I have considered that and I would have expected to see...
By Blaine_t , 4 days ago
-
RE: 14kW Midea ASHP in an old leaky building
Hi @batalto. I see you have a Midea ASHP and I am sched...
By Kbedders , 4 days ago
-
RE: Additional ASHP kW for DHW cylinder?
We're in a similar boat to you with a hodgepodge of dif...
By Mars , 4 days ago
Latest Topics
-
By Potatoman 13 hours ago
-
Have Octopus Energy discovered a way to Narnia?
By Davesoa 20 hours ago
-
Making best use of Agile with a battery and ASHP
By jamesw 2 days ago
-
By Toodles 4 days ago
-
By Blaine_t 4 days ago
-
Insulation of flow and return Heat Pump piping
By Toodles 4 days ago
-
Rising Damp – Production Recommendation
By Mars 4 days ago
-
Additional ASHP kW for DHW cylinder?
By Project_Electrify 5 days ago
-
By IRMartini 7 days ago