Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
Posted by: @abernyteIs there also a danger in the terminology that is being used ie low loss header, buffer and volumiser
Agreed
Posted by: @abernyteNot all LLH's act as buffers, correctly specified and installed they operate perfectly correctly as a hydraulic separator. It very much depends on where on the LLH the ports are positioned.
Surely an LLH suffers from mixing of flow and return to the same extent, probably more because its smaller, than a buffer does, and like a buffer needs to be set up properly to function without degrading efficiency (which seems to be where many installations go wrong).
Can you explain why 'hydraulic separation' is needed in a typical domestic central heating system. I totally understand why extra volume may be needed, but not hydraulic separation. if you are doing something complex with a back up boiler or a rather large system then maybe, but in a typical house what value does it add?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @derek-mPosted by: @abernyteIs there also a danger in the terminology that is being used ie low loss header, buffer and volumiser. Not all LLH's act as buffers, correctly specified and installed they operate perfectly correctly as a hydraulic separator. It very much depends on where on the LLH the ports are positioned.
Are we in danger of vilifying an entire class of products?
As far as I am aware there would be no problem with a LLH or buffer tank, if the primary and secondary flowrates can be balanced to ensure that no mixing of the flow and return takes place. Obviously balancing the flowrates becomes problematic if the heat pump controller is able to vary the primary flowrate, without the necessary adjustment also being performed on the secondary, thereby unbalancing the system.
Having an additional water pump that may not be necessary is also a possible waste of electrical energy.
True, but it appears they are frequently not balanced.
My questions to @abernyte (or anyone else) is:
In a domestic installation of a 'normal' scale (say up to 6 bedrooms/300 sq m) with either radiators or UFH but not both
- what value does a LLH add?
- what value does a buffer add that a volumiser doesn't add?
The application of Occams razor is generally a good principle so until we identify the value add then there is no argument for their presence.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The default setup on a Mitisubishi Ecodan solar thermal ported pre plumbed cylinder has a LLH. My installer, who was one of the highly experienced "better" class of installer when queried regarding this said that the LLH in question has the flow injection plume above the return fitting outlet (not opposite as some seem to have) and as such would operate as a thermal separator to allow the primary and secondary pumps to operate efficiently at different variable speeds.
Since installation the system operates with a flow temp rarely above 35C and has been a resounding success as a heating system. Not a scientific recommendation I admit but I see no reason to doubt his explanation ...so far!
Posted by: @abernyteThe default setup on a Mitisubishi Ecodan solar thermal ported pre plumbed cylinder has a LLH. My installer, who was one of the highly experienced "better" class of installer when queried regarding this said that the LLH in question has the flow injection plume above the return fitting outlet (not opposite as some seem to have) and as such would operate as a thermal separator to allow the primary and secondary pumps to operate efficiently at different variable speeds.
Since installation the system operates with a flow temp rarely above 35C and has been a resounding success as a heating system. Not a scientific recommendation I admit but I see no reason to doubt his explanation ...so far!
Which simply begs the question - why do I want primary and secondary pumps in the first place (which incidentally must be balanced for the LLH to work without impeding system efficiency). For the avoidance of doubt I'm talking about a typical fairly simple domestic setup where a heat pump replaces a gas boiler (ie 95% plus of real world scenarios). Why would I have a second pump, a low loss header/buffer etc. None of this appears in your typical CH system. What value do they add.
You may not know I accept, but until someone tells us then the best assumption is no value at all and, since they clearly add trouble and cost, thats a good argument to leave them out.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@abernyte I suspect that arrangement might be similar to the one in our airing cupboard. The flow is the top left pipe and the return is the lower left. The top right is the flow to the secondary pump thence to radiators and the lower right is return from the radiators? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
The only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems.
Posted by: @derek-mPosted by: @jamespaPosted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
The only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems.
Wow that's inventive but I'm sure you agree that it can be discarded as a legitimate reason.
Perhaps we ought to ask why should they be included rather than trying to argue that they should be omitted. No system designer worth their salt includes components without a reason.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @derek-mPosted by: @jamespaPosted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
The only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems.
Wow that's inventive but I'm sure you agree that it can be discarded as a legitimate reason.
Perhaps we ought to ask why should they be included rather than trying to argue that they should be omitted. No system designer worth their salt includes components without a reason.
Which is why I have spent the past three years trying to convince forum members that they should have their poorly designed systems corrected to make them operate more efficiently.
Posted by: @derek-mThe only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems
I think you are both correct, its because systems aren't designed, they are plumbed in by people who don't understand system design but attend a manufacturer's installation course. So the additions of these components are their to mitigate any system design and it will function in any given scenario, not optimally but it will function.
Posted by: @garyPosted by: @derek-mThe only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems
I think you are both correct, its because systems aren't designed, they are plumbed in by people who don't understand system design but attend a manufacturer's installation course. So the additions of these components are their to mitigate any system design and it will function in any given scenario, not optimally but it will function.
I fear you are right. However the reason suggested (which is very plausible) is the equivalent of dressing a dirty wound instead of first cleaning it up because the patient complains about the sting of the antiseptic, except that if you did the latter you would likely get struck off.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
2 months ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
2 months ago
-
6 Red Flags to Avoid When Considering a Heat Pump Installation
3 months ago
-
L9 error with Mitsubishi ecodan heat pump
4 months ago
-
Ecodan DHW Settings missing
1 year ago
- 22 Forums
- 2,037 Topics
- 44.4 K Posts
- 34 Online
- 3,250 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 4 hours ago
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
@majordennisbloodnok, the same thought occurred to me, ...
By Morgan , 4 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I agree with @mars. My install was not dissimilar. ...
By JamesPa , 5 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 5 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 21 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 1 day ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 2 days ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 2 days ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 2 days ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 2 days ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 3 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 3 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 3 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 4 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 4 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 4 days ago