Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
Posted by: @abernyteIs there also a danger in the terminology that is being used ie low loss header, buffer and volumiser
Agreed
Posted by: @abernyteNot all LLH's act as buffers, correctly specified and installed they operate perfectly correctly as a hydraulic separator. It very much depends on where on the LLH the ports are positioned.
Surely an LLH suffers from mixing of flow and return to the same extent, probably more because its smaller, than a buffer does, and like a buffer needs to be set up properly to function without degrading efficiency (which seems to be where many installations go wrong).
Can you explain why 'hydraulic separation' is needed in a typical domestic central heating system. I totally understand why extra volume may be needed, but not hydraulic separation. if you are doing something complex with a back up boiler or a rather large system then maybe, but in a typical house what value does it add?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @derek-mPosted by: @abernyteIs there also a danger in the terminology that is being used ie low loss header, buffer and volumiser. Not all LLH's act as buffers, correctly specified and installed they operate perfectly correctly as a hydraulic separator. It very much depends on where on the LLH the ports are positioned.
Are we in danger of vilifying an entire class of products?
As far as I am aware there would be no problem with a LLH or buffer tank, if the primary and secondary flowrates can be balanced to ensure that no mixing of the flow and return takes place. Obviously balancing the flowrates becomes problematic if the heat pump controller is able to vary the primary flowrate, without the necessary adjustment also being performed on the secondary, thereby unbalancing the system.
Having an additional water pump that may not be necessary is also a possible waste of electrical energy.
True, but it appears they are frequently not balanced.
My questions to @abernyte (or anyone else) is:
In a domestic installation of a 'normal' scale (say up to 6 bedrooms/300 sq m) with either radiators or UFH but not both
- what value does a LLH add?
- what value does a buffer add that a volumiser doesn't add?
The application of Occams razor is generally a good principle so until we identify the value add then there is no argument for their presence.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The default setup on a Mitisubishi Ecodan solar thermal ported pre plumbed cylinder has a LLH. My installer, who was one of the highly experienced "better" class of installer when queried regarding this said that the LLH in question has the flow injection plume above the return fitting outlet (not opposite as some seem to have) and as such would operate as a thermal separator to allow the primary and secondary pumps to operate efficiently at different variable speeds.
Since installation the system operates with a flow temp rarely above 35C and has been a resounding success as a heating system. Not a scientific recommendation I admit but I see no reason to doubt his explanation ...so far!
Posted by: @abernyteThe default setup on a Mitisubishi Ecodan solar thermal ported pre plumbed cylinder has a LLH. My installer, who was one of the highly experienced "better" class of installer when queried regarding this said that the LLH in question has the flow injection plume above the return fitting outlet (not opposite as some seem to have) and as such would operate as a thermal separator to allow the primary and secondary pumps to operate efficiently at different variable speeds.
Since installation the system operates with a flow temp rarely above 35C and has been a resounding success as a heating system. Not a scientific recommendation I admit but I see no reason to doubt his explanation ...so far!
Which simply begs the question - why do I want primary and secondary pumps in the first place (which incidentally must be balanced for the LLH to work without impeding system efficiency). For the avoidance of doubt I'm talking about a typical fairly simple domestic setup where a heat pump replaces a gas boiler (ie 95% plus of real world scenarios). Why would I have a second pump, a low loss header/buffer etc. None of this appears in your typical CH system. What value do they add.
You may not know I accept, but until someone tells us then the best assumption is no value at all and, since they clearly add trouble and cost, thats a good argument to leave them out.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@abernyte I suspect that arrangement might be similar to the one in our airing cupboard. The flow is the top left pipe and the return is the lower left. The top right is the flow to the secondary pump thence to radiators and the lower right is return from the radiators? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
The only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems.
Posted by: @derek-mPosted by: @jamespaPosted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
The only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems.
Wow that's inventive but I'm sure you agree that it can be discarded as a legitimate reason.
Perhaps we ought to ask why should they be included rather than trying to argue that they should be omitted. No system designer worth their salt includes components without a reason.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @derek-mPosted by: @jamespaPosted by: @abernyteYes other than Mitsubishi use a 35mm LLH
But why (bother with a secondary pump and llh) in a typical domestic install?
Does anyone actually know a reason that stands up to scrutiny? I am not trying to be difficult, I genuinely want to know? @abernyte, @editor, @derek-m any ideas or is this another appendix from heat pump history that needs to be surgically removed?
The only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems.
Wow that's inventive but I'm sure you agree that it can be discarded as a legitimate reason.
Perhaps we ought to ask why should they be included rather than trying to argue that they should be omitted. No system designer worth their salt includes components without a reason.
Which is why I have spent the past three years trying to convince forum members that they should have their poorly designed systems corrected to make them operate more efficiently.
Posted by: @derek-mThe only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems
I think you are both correct, its because systems aren't designed, they are plumbed in by people who don't understand system design but attend a manufacturer's installation course. So the additions of these components are their to mitigate any system design and it will function in any given scenario, not optimally but it will function.
Posted by: @garyPosted by: @derek-mThe only reason of which I can think, is that it would be to allow system designers to accommodate 'smart' thermostats and TRV's into their designs, without suffering 'low flow' problems
I think you are both correct, its because systems aren't designed, they are plumbed in by people who don't understand system design but attend a manufacturer's installation course. So the additions of these components are their to mitigate any system design and it will function in any given scenario, not optimally but it will function.
I fear you are right. However the reason suggested (which is very plausible) is the equivalent of dressing a dirty wound instead of first cleaning it up because the patient complains about the sting of the antiseptic, except that if you did the latter you would likely get struck off.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
4 weeks ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
1 month ago
-
6 Red Flags to Avoid When Considering a Heat Pump Installation
2 months ago
-
L9 error with Mitsubishi ecodan heat pump
3 months ago
-
Ecodan DHW Settings missing
1 year ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 54 Online
- 2,278 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa @bontwoodyHeat loss calculations found and att...
By BAMi , 1 hour ago
-
RE: What is the best strategy for operating a very oversized heat pump?
I think you are right to frame the question as you did,...
By Old_Scientist , 1 hour ago
-
RE: Setback savings - fact or fiction?
Here's the same plot, less the R squared values, done q...
By cathodeRay , 2 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 2 hours ago
-
@jamespa thanks, it's way off of the MCS performance es...
By big_si , 3 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 5 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 5 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 6 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 8 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 1 day ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 2 days ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 12 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 13 hours ago
-
SolarPV tables / online calculator
By MichelleC 20 hours ago
-
By Toodles 2 days ago