Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
Posted by: @toodlesAt the risk of being drummed out for heretical thoughts ( ;-))) ) No, I’m sure I wouldn’t be, … would I?! Suppose this LLH is losing some efficiency - where is the loss taken place and where is the wasted energy going please? If the loss is in the form of heat that doesn’t make it across the interior of the LLH, does it radiate into the surrounding area? In my case, this will be the airing cupboard where such heat will be ‘always useful’, (harking back to the topic of uninsulated pipe runs within the home again!). If the unharnessed energy is being deflected back out into the return pipe-run to the heat pump outside, I can see that this might well be wasted heat though. Regards, Toodles.
The principal reason that LLH reduces efficiency is if there is a temperature drop flow to flow across it (which there almost inevitably is unless it is particularly well set up). This means that the heat pump operates less efficiently, because it must operate at a higher flow temperature to achieve the same temperature at the emitters. Part of the reduction in efficiency will be that the compressor (which is usually outside) has to work harder, and part of the loss will be that not as much energy is extracted from the outside air. So no, the 'lost' efficiency does not result in an increased radiation into the house (nor is it the case that a 'loss' of energy takes place in the LLH, albeit that it is the cause of the reduced efficiency - the reduction in efficiency occurs even if the LLH is lossless)
There will also of course be some actual loss of energy from the system at the LLH, due to convection. Depending on the location of the LLH that might get radiated into the house. This can be ignored if the LLH is within the heated envelope, and generally is ignored in these discussions.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @toodlesAt the risk of being drummed out for heretical thoughts ( ;-))) ) No, I’m sure I wouldn’t be, … would I?! Suppose this LLH is losing some efficiency - where is the loss taken place and where is the wasted energy going please? If the loss is in the form of heat that doesn’t make it across the interior of the LLH, does it radiate into the surrounding area? In my case, this will be the airing cupboard where such heat will be ‘always useful’, (harking back to the topic of uninsulated pipe runs within the home again!). If the unharnessed energy is being deflected back out into the return pipe-run to the heat pump outside, I can see that this might well be wasted heat though. Regards, Toodles.
If you have any more heretical thoughts then please let me know, so that I can send the Inquisitor round. 😋
The loss isn't actual thermal energy as such, the loss is due to reduced efficiency (lower COP). Because of possible temperature reduction from primary circuit to secondary circuit, the LWT may have to be higher to ensure the heat emitters receive the required quantity of thermal energy.
To produce a higher LWT the compressor has to work harder, using more electrical energy, and in turn the heat pump absorbs less free energy from the OAT.
The overall thermal energy supply to the home should be approximately the same, just less free energy and more expensive energy.
@derek-m Just for ‘fun’, I placed strips of matt black insulting tape on the four pipes to and from the LLH and used my IR thermometer to obtain these approximate readings; I measured the four points a number of times to attempt to obtain steady readings and my best attempts tend to suggest the following temperatures.
Input to LLH from heat pump: 29.8 deg. C
Output to emitters: 29.0 deg. C
Return from emitters: 28.0 deg. C
Return to heat pump: 28.8 deg. C
Do these readings look as if they may be true? I’ll take another set of readings another day when time permits (don’t get older if you can help it, you spend more time than you might like draining the NHS facilities!) meanwhile without placing ‘proper’ sensors on the pipes, I’m not sure I can increase the accuracy. I wonder if there is also room to improve the Delta T by adjusting the secondary pump? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I can't remember ever having used an IR thermometer, but then I've always had access to what I would term correct test equipment. I do believe that one of the other forum members found difficulty getting accurate readings using an IR thermometer. What is the specified operating range and tolerance?
The actual readings obtained could be appropriate for a mild day like today, but again without other values to compare it is difficult to know for certain.
The DT does look low, but again without comparing with values measured during colder weather conditions, I cannot say for certain.
Without further data, I would suggest that you just monitor, without making changes, especially if you are warm and it is not costing you an arm and a leg to operate.
I keep advising people not to grow older, but they will insist upon doing so. 🙄
@toodles I've tried IR with black tape, doesn't work very well . Other forum members have had good results for very little spend with a set of these from amazon. tape them tightly to the pipes, pipe insulation over the top to isolate from ambient.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Oh Ian, I couldn’t see a link or any product details - please could you detail the goods again? My current attempts have been with a non-contact IR Thermometer with a spec. Of 0 ~ 550 C. +/- 1.5 %. Probably indicative but the tape covered pipe might be causing all sorts of errors I would imagine. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@derek-m The system seems to be working well, we are warm and at approx. 450-500 W/h in this present warm weather, I feel all is goodness and light. (COP shows as 4.5 plus), when it was - 6 or -7, the COP was approx. 2.6 I think. As Ian has mentioned, an alternative means of measuring the actual LLH adjoining pipe temperatures would be better though. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles I put a link in the word "these" in the previous post. this type of thing. others on here have used them successfully.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thank you Ian, Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@iancalderbank Amazon delivered the four thermometers today; shame that there was not insulating material interposed between the contact and the button cells; flat cells in three of them and a faint glow only from the other! Did extended battle with Amazon help line / suppliers site and now await replacements. Ho-hum more grey hairs (well, actually, they are white already) and time I won’t get back!;-) Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles You were unlucky. I got the same 4 digital sensors over a year ago and all batteries are still going strong. Great devices across the low loss header to check primary and secondary flow and return temperatures. Make sure the sensor is touching the pipe and well insulated. Cable tie sensor to pipe, and then cable tie insulation completely over it. They would probably benefit from heat sink compound, but my memory of that stuff from my apprenticeship days is it ruins clothes instantly!
@allyfish I had a reply from the supplier, requesting a photo or video the the product!!! I sent a phot of the four displays; one was readable, one was feint and the other two were blank. I asked if they didn’t trust me? Anyhow, I orderedmsome LR44’s that should arrive today so that I can put the ‘kit’ together. Perhaps the supplier will send me another 4 units, I doubt they sell the cells anyway! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
-
Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
7 months ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
7 months ago
-
6 Red Flags to Avoid When Considering a Heat Pump Installation
8 months ago
-
L9 error with Mitsubishi ecodan heat pump
9 months ago
-
Ecodan DHW Settings missing
2 years ago
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 32 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 2 minutes ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 5 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
Hello, unfortunately i did not take any photos, but you...
By ThunderMink , 5 hours ago
-
RE: Solar Thermal DHW and ASHP
Since you already have the ashp it makes little financi...
By Judith , 14 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
I think you’ll find it depends on the room heat loss. A...
By Judith , 14 hours ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 15 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil Fwiw I have the 7kW model with which I'm, ver...
By JamesPa , 16 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@grahamf you appear to value your recirculating loop de...
By Judith , 16 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 16 hours ago
-
RE: Midea ASHP – how to set weather compensation
@cathoderay OK let's wait and see, it sounds an interes...
By Tasos , 19 hours ago
-
RE: What is the Heat Geek Guarantee?
@judith, I’m with you on Heat Geek, but there really do...
By Mars , 20 hours ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 2 days ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 3 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 3 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 3 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 3 days ago