Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
In light of the recent buffer tank/warranty comments in this topic, I’ve written this piece below. It’s a 10 minute read, but I think it warrants a dedicated video/podcast, because there’s a lot of ambiguity and grey areas here that need clarification.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@potatoman As no one seems to be obliging, I attach a diagram. The idea is that only bypass flow goes through the tank when necessary so it is undisturbed by main flow. Connection to tank must be closely coupled.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
@heatgeek is it that this design satisfies the manufacturers? its still (although balance by bypass) a double hydronic volumiser/buffer with 2 pumps
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba I am afraid that you are talking to the wrong person about manufacturers preferences. However, as far as I can see, it functions the same as a 4 port buffer except that flow doesn't go through the top of the tank causing mixing, therefore I would have thought that it is a perfectly acceptable alternative to a 4-port.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
@heatgeek Oh agreed, its a slightly better and slightly less resistive solution, perhaps even the middle ground of no buffer V buffer.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@potatoman hi, the scheme detailed is 2 pumps, one for the ASHP (primary) and 1 for the secondary circuits.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@potatoman No, the installation is exactly the same as a 4 port buffer with primary and secondary pumps except that the output flow bypasses the top of tank so as not to disturb the stratification of the tank. This removes some of the inefficiency problems associated with 4 port buffer tanks, like output temperature being reduced by mixing.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Note a key point here though. The primary pump is connected in the return pipe while the secondary pump is connected in the flow pipe after the buffer tank to provide good hydronic separation between the primary and secondary pumps.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Only the difference in flow between the heat pump and the emitters passes through the tank. This lower flow helps to preserve the stratification of the tank so that dilution of temperature to the emitters is minimised.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Apologies. Poor choice of words. Delete "dilution of temperature to emitters is minimised".
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Posted by: @heatgeekNote a key point here though. The primary pump is connected in the return pipe while the secondary pump is connected in the flow pipe after the buffer tank to provide good hydronic separation between the primary and secondary pumps.
That all sounds very believable. Presumably mixing of return water with flow water to the emitters (and thus a reduction of ft to emitters) will however still occur if the primary pump throughput is less than the secondary, so the requirement to set up properly remains albeit that it is less sensitive than a 4 port.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
8 months ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
8 months ago
-
6 Red Flags to Avoid When Considering a Heat Pump Installation
8 months ago
-
L9 error with Mitsubishi ecodan heat pump
9 months ago
-
Ecodan DHW Settings missing
2 years ago
- 26 Forums
- 2,183 Topics
- 48.1 K Posts
- 58 Online
- 5,756 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
We have a lot of work ahead to get this done properly. ...
By Mars , 13 minutes ago
-
RE: Say hello and introduce yourself
@wully Yes, by all means, start a topic as it will be o...
By Toodles , 20 minutes ago
-
RE: Do I just go with the lowest quote for my heat pump?
You are right It will depend on how its b...
By JamesPa , 1 hour ago
-
RE: Which thermostat should I get (or do I need one?)
You need a plan first I think, it's really about wiring...
By JamesPa , 2 hours ago
-
Samsung Gen 6 - Schedules not working
I think I may have done something silly, but havent bee...
By bontwoody , 4 hours ago
-
RE: DNO export limit problems.
Ask DNO if its a load balancing on your phase of the su...
By AgentGeorge , 4 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
In the latter case is it all the time or at certain eve...
By JamesPa , 4 hours ago
-
@papahuhu Sounds as though you need to speak to your in...
By Toodles , 6 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Signed.
By Morgan , 7 hours ago
-
I ‘did the math’ for Nov. to the end of April to be on ...
By Toodles , 7 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos automations on Home Assistant so if there is a p...
By benson , 9 hours ago
-
RE: Sizing - Save me from my headache
Mitsi 8kW has a 6kW variable and 2kW fixed compressor s...
By JamesPa , 1 day ago
-
@drei your proposed radiator design looks inadequate to...
By GrahamF , 1 day ago
-
RE: Why does an ASHP provide a more comfortable environment than a gas boiler?
Actually, I think the issue is the different rate of he...
By AndrewJ , 1 day ago
-
RE: 5 Star Service from Havenwise
That's why homes are spread across the three phases. ...
By Dan_Grey , 1 day ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
@editor like @jamespa, I had a list of test questions: ...
By GrahamF , 2 days ago
-
RE: Do primaries need anti vibration clips?
@adamk @ashp-bobba The vast majority of the time my 7...
By JamesPa , 2 days ago
-
RE: Which temperature sensor for a Steibel buffer and Ecodan?
@davidalgarve As advised above, its worth speaking to M...
By ASHP-BOBBA , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@seatonian all comments on YT are moderated. I’ll appro...
By Mars , 2 days ago