Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Air Changes per Hour - ACH and the MCS requirement

41 Posts
11 Users
24 Reactions
4,119 Views
 robl
(@robl)
Reputable Member Member
Joined: 4 years ago
Posts: 214
 

A blower door test typically pressurises the home to +/-50Pa relative to outside, and measures the airflow required to achieve this in m^3/hour.  Using the total building surface area and total internal volume you can get the whole house air changes per hour @50Pa, and also the airflow per m^2 of building fabric - the two numbers usually come out quite similar when metres are used - hence often it's not clear which one is used.  Normally there isn't 50Pa difference between inside and outside, so the actual airflow through the building is a lot lower - by default I think a factor 20 is applied.  This magic factor of 20 is an approximation - in reality it depends on house shape (taller houses should have a lower factor applied) and how exposed the location is (more exposed will give a lower factor) and where the leaks are(encouraging stack ventillation again gives a lower ratio).

Building regs presently ask for 8m^3/hr/m^2 @50Pa or better(lower).  I'm not sure why 0.5 is picked for ventillation loss rather than the 8/20=0.4 that my maths gives, my guess is still thats where the value comes from.



   
👍
2
ReplyQuote
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 147
 

Posted by: @robl

A blower door test typically pressurises the home to +/-50Pa relative to outside, and measures the airflow required to achieve this in m^3/hour.  Using the total building surface area and total internal volume you can get the whole house air changes per hour @50Pa, and also the airflow per m^2 of building fabric - the two numbers usually come out quite similar when metres are used - hence often it's not clear which one is used.  Normally there isn't 50Pa difference between inside and outside, so the actual airflow through the building is a lot lower - by default I think a factor 20 is applied.  This magic factor of 20 is an approximation - in reality it depends on house shape (taller houses should have a lower factor applied) and how exposed the location is (more exposed will give a lower factor) and where the leaks are(encouraging stack ventillation again gives a lower ratio).

Building regs presently ask for 8m^3/hr/m^2 @50Pa or better(lower).  I'm not sure why 0.5 is picked for ventillation loss rather than the 8/20=0.4 that my maths gives, my guess is still thats where the value comes from.

My Air Permeability is : 2.35 m³/(h·m²) @ 50 Pa.  So if I use your magic factor: 2.35/20=0.1175.  According to my SAP report the overall Infiltration Rate for my building is 0.099.  So not far out.

FromAi:

Screenshot 2026 01 29 at 16.50.19

This post was modified 3 months ago by trebor12345

Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1

2024 build bungalow, Southern england, 179 m2, 14w/m2
Underfloor heating all fully open
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels


   
ReplyQuote
(@judith)
Prominent Member Member
Joined: 2 years ago
Posts: 519
 

Mick Wall has a very thorough measurement set of air changes per hour for his house, on his web site https://energy-stats.uk/air-changes-per-hour-heat-loss/

 


2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC


   
ReplyQuote



(@judith)
Prominent Member Member
Joined: 2 years ago
Posts: 519
 

The generally accepted ratio from the 50Pa test to natural usage is 20. But I wanted to understand why and can’t now re-find the references I used to verify a factor of ~20 for us.

https://building-performance.org/bpa-journal/ach50-achnat/

This American web site gives a wider range of weather exposure conditions than the UK but that’s useful in itself because of how broad the factor is, from 9 to 30.


2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC


   
🙏
1
ReplyQuote
Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 801
 

When evaluating SmartHome temperature sensors, I noticed many would also include hygrometers.

So that could provide a simple way to have targeted ventilation. In tropical locations, aircon operation is typically driven by a combination of temperature and dampness. To be clear, the sensors work in our range as well..