Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Air Changes per Hour - ACH and the MCS requirement
A blower door test typically pressurises the home to +/-50Pa relative to outside, and measures the airflow required to achieve this in m^3/hour. Using the total building surface area and total internal volume you can get the whole house air changes per hour @50Pa, and also the airflow per m^2 of building fabric - the two numbers usually come out quite similar when metres are used - hence often it's not clear which one is used. Normally there isn't 50Pa difference between inside and outside, so the actual airflow through the building is a lot lower - by default I think a factor 20 is applied. This magic factor of 20 is an approximation - in reality it depends on house shape (taller houses should have a lower factor applied) and how exposed the location is (more exposed will give a lower factor) and where the leaks are(encouraging stack ventillation again gives a lower ratio).
Building regs presently ask for 8m^3/hr/m^2 @50Pa or better(lower). I'm not sure why 0.5 is picked for ventillation loss rather than the 8/20=0.4 that my maths gives, my guess is still thats where the value comes from.
Posted by: @roblA blower door test typically pressurises the home to +/-50Pa relative to outside, and measures the airflow required to achieve this in m^3/hour. Using the total building surface area and total internal volume you can get the whole house air changes per hour @50Pa, and also the airflow per m^2 of building fabric - the two numbers usually come out quite similar when metres are used - hence often it's not clear which one is used. Normally there isn't 50Pa difference between inside and outside, so the actual airflow through the building is a lot lower - by default I think a factor 20 is applied. This magic factor of 20 is an approximation - in reality it depends on house shape (taller houses should have a lower factor applied) and how exposed the location is (more exposed will give a lower factor) and where the leaks are(encouraging stack ventillation again gives a lower ratio).
Building regs presently ask for 8m^3/hr/m^2 @50Pa or better(lower). I'm not sure why 0.5 is picked for ventillation loss rather than the 8/20=0.4 that my maths gives, my guess is still thats where the value comes from.
My Air Permeability is : 2.35 m³/(h·m²) @ 50 Pa. So if I use your magic factor: 2.35/20=0.1175. According to my SAP report the overall Infiltration Rate for my building is 0.099. So not far out.
FromAi:
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow, Southern england, 179 m2, 14w/m2
Underfloor heating all fully open
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Mick Wall has a very thorough measurement set of air changes per hour for his house, on his web site https://energy-stats.uk/air-changes-per-hour-heat-loss/
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
The generally accepted ratio from the 50Pa test to natural usage is 20. But I wanted to understand why and can’t now re-find the references I used to verify a factor of ~20 for us.
https://building-performance.org/bpa-journal/ach50-achnat/
This American web site gives a wider range of weather exposure conditions than the UK but that’s useful in itself because of how broad the factor is, from 9 to 30.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
When evaluating SmartHome temperature sensors, I noticed many would also include hygrometers.
So that could provide a simple way to have targeted ventilation. In tropical locations, aircon operation is typically driven by a combination of temperature and dampness. To be clear, the sensors work in our range as well..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 337 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 6 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 6 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 7 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 8 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 8 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 9 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 11 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 12 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 14 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 16 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 20 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago