Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Air Changes per Hour - ACH and the MCS requirement
A blower door test typically pressurises the home to +/-50Pa relative to outside, and measures the airflow required to achieve this in m^3/hour. Using the total building surface area and total internal volume you can get the whole house air changes per hour @50Pa, and also the airflow per m^2 of building fabric - the two numbers usually come out quite similar when metres are used - hence often it's not clear which one is used. Normally there isn't 50Pa difference between inside and outside, so the actual airflow through the building is a lot lower - by default I think a factor 20 is applied. This magic factor of 20 is an approximation - in reality it depends on house shape (taller houses should have a lower factor applied) and how exposed the location is (more exposed will give a lower factor) and where the leaks are(encouraging stack ventillation again gives a lower ratio).
Building regs presently ask for 8m^3/hr/m^2 @50Pa or better(lower). I'm not sure why 0.5 is picked for ventillation loss rather than the 8/20=0.4 that my maths gives, my guess is still thats where the value comes from.
Posted by: @roblA blower door test typically pressurises the home to +/-50Pa relative to outside, and measures the airflow required to achieve this in m^3/hour. Using the total building surface area and total internal volume you can get the whole house air changes per hour @50Pa, and also the airflow per m^2 of building fabric - the two numbers usually come out quite similar when metres are used - hence often it's not clear which one is used. Normally there isn't 50Pa difference between inside and outside, so the actual airflow through the building is a lot lower - by default I think a factor 20 is applied. This magic factor of 20 is an approximation - in reality it depends on house shape (taller houses should have a lower factor applied) and how exposed the location is (more exposed will give a lower factor) and where the leaks are(encouraging stack ventillation again gives a lower ratio).
Building regs presently ask for 8m^3/hr/m^2 @50Pa or better(lower). I'm not sure why 0.5 is picked for ventillation loss rather than the 8/20=0.4 that my maths gives, my guess is still thats where the value comes from.
My Air Permeability is : 2.35 m³/(h·m²) @ 50 Pa. So if I use your magic factor: 2.35/20=0.1175. According to my SAP report the overall Infiltration Rate for my building is 0.099. So not far out.
FromAi:
2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Mick Wall has a very thorough measurement set of air changes per hour for his house, on his web site https://energy-stats.uk/air-changes-per-hour-heat-loss/
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
The generally accepted ratio from the 50Pa test to natural usage is 20. But I wanted to understand why and can’t now re-find the references I used to verify a factor of ~20 for us.
https://building-performance.org/bpa-journal/ach50-achnat/
This American web site gives a wider range of weather exposure conditions than the UK but that’s useful in itself because of how broad the factor is, from 9 to 30.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
When evaluating SmartHome temperature sensors, I noticed many would also include hygrometers.
So that could provide a simple way to have targeted ventilation. In tropical locations, aircon operation is typically driven by a combination of temperature and dampness. To be clear, the sensors work in our range as well..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,690 Topics
- 63.1 K Posts
- 475 Online
- 7,100 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Say hello and introduce yourself
@watcher Encouraging except that a bungalow is probably...
By Toodles , 4 hours ago
-
RE: How do I set up Tesla Powerwall export for saving sessions since AI Takeover?
@papahuhu We might well have found that a much smaller ...
By Toodles , 5 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
Yesterday i had a single overvoltage event. But that mu...
By Tim441 , 10 hours ago
-
RE: Design Of Cascade System Replacing Undersized ASHP
I don't know the full details of your house or installa...
By Temperature_Gradient , 11 hours ago
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
Some pics of my heat solutions… Bought the shut...
By Watcher , 11 hours ago
-
RE: Moving growatt axe batteries
@etchedpixels just been informed that you can’t have ba...
By David999 , 23 hours ago
-
RE: Anyone have experience with Daikin Multi+ for air to air & hot water?
Maybe, just maybe, if you are prepared to leave the doo...
By JamesPa , 23 hours ago
-
RE: How to heat a bathroom when using an air to air heat pump?
You can air/air a bathroom with a suitable ceiling or o...
By EtchedPixels , 23 hours ago
-
RE: Plug and play solar. Thoughts?
They've been extensively tested by folks like the Germa...
By EtchedPixels , 23 hours ago
-
RE: Electricity price predictions
@majordennisbloodnok Similar, although no heat pump h...
By IanMK13 , 1 day ago
-
RE: vaillant arotherm plus - Failure - DHW
As expected it failed to run late yesterday with the sa...
By trebor12345 , 2 days ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
Personally, I don't always rate the "payback on install...
By HeatNoob , 2 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thanks. Will be sure to keep a record of s...
By bontwoody , 2 days ago
-
@jamespa Well, something along the lines of "three buse...
By ian33a , 2 days ago